System is undercharged. Have the service company return to balance charge. Gurgling noise is refrigerant vapor as it enters metering device. The smooth, hissing noise you heard before was a full liquid head being presented to device - no vapor. When a system is underchaged, there is not enough volume to maintain head and the gurgling noise results. If there were a sight glass present in the liquid line, you would see the result of an undercharge as bubbles. There is a possibility that the system may have non-condensibles but need more info. Just curious - why did the system need an evac and recharge?
Original poster: The site-glass is on the liquid line as it exits the compressor (outside). True, it has bubbles in it that never go away [Others her have told me to paint over it, as it has no diagnostic value..] This connection has gurgled ever since it was installed in 1988. I had it evacuated & recharged just as "PM", since it'd never been evacuated in 16 years. Outside unit is 1988 Carrier 3ton, and Carrier AH inside, also 3-ton (A/C-only). I didn't see the guages when the guy re-charged last year, so I didn't see what the charge was. Is there any way that the charge can still be improper, even tho the guages indicate and OK-charge? Any quick way I can tell if there's a metering device installed? I can post a pic of the lineset connection to the evap. Lastly, the gurgling is always present, no matter what the outdoor temp is, and no matter what the indoor temp is.