Originally Posted by
softail124
I think this could be an issue other than the loop, I would not be afraid of 29 degree EWT at this time of year. I had a four ton Envision doing exactly what yours is doing. The EWT was 30 and LWT was 24. You have to remember the Envison water flow light is controlled by a thermistor on a refrigerant line, if you have a bad txv it will trigger a water flow light. The first thing you have to verify is how many gpm are flowing through the unit. With these temperatures if you have 15 gpm I would say it is either a bad txv or a restriction in the txv, especially if the system has functioned properly prior to this.