Well, I take it all back then
That what is there - 1/2HP compressors. Maybe I'm now losing the Rest of my mind.
Because it sure seems to me that in the last gang of stores we did - the 8' cases all got 3/4HP units. <g>
I'm not doing the cases on this job - just the warehouse and some other odds and ends. But I saw the boxes and condensing units sitting there so I looked. 1/2 HP just seemed light to me.
Guess I'm wrong though. <g>
Thanks.
No runs yet - the floor is a honeycomb of 8" tubes
The plumber was still digging up the old floor tunnels when I was there. I can only see the tubes from the cellar end. They run out on various angles to all over the store. But the stores ends have all been filled and abandoned. I told them to sawcut the floor to about 3-4" deep under where the cases will be. This cut would have to intersect every buried tube and we all can work with all of them.
But who knows what they will do? When I left they were "projecting" where the ends of the tubes "had to be" and looking for them with a sledge hammer. Like four monkeys and the perverbial football.
Just guesstimating where I think the deli will go as versus where the cellar is - I would guess somewhere between twenty and forty feet of total line run. Call it it fifty feet max - because of the way things go. <g>
Three cases - so IF the floor tunnel is only centered - each of the end cases will have an additional 15-17 feet of run. If they open enough tunnels so that the runs can be on the diagonal - the runs will be shorter.
If things end up like plumbers set them up - the runs will be longer. <g>
PHM
---------
Quote:
Originally Posted by
Mishap64
1/2 HP will do it. You mentioned the condenser was in a rack. How far a run?