Originally Posted by
Poodle Head Mikey
One of the best kept secrets in the HVAC/R business must be that all refrigerant gets charged as a liquid. <g>
Who the hell has the time to warm the cylinder repeatedly and then wait for pounds and pounds of refrigerant to boil off? Don't your service managers scream over all the time you are taking?
There are little vaporizing widgets you can charge through but why not just crack the suction side gauge handle and let it boil/vaporize in through the crack? If you are very curious (as I was <g>) use two 1/4" flare MxF sight glasses. Put one before the suction hose - screw it onto the left bottom side of your gauge set - and put the other one onto the suction access flare on the unit. Then crack the suction gauge manifold handle a little and see what the refrigerant looks like in the sight glasses.
With the manifold gauge cracked - tell me what you see.
And also note the suction pressure increase on your gauge (valve open versus valve cracked) initially 'set' it for 5-10 lbs over running suction pressure. Use an analog gauge and watch the needle flutter. If the needle is steady the gauge valve is either open too far or closed too much. <g>
PHM
-------