Originally Posted by
tipsrfine
What I was meaning is that without low ambient conditions the additional refrigerant would not be needed. Sporlan's charging procedures first show you the proper charge of refrigerant needed without low ambient conditions. Under those conditions a receiver would not really be needed, so that charge should be able to be stored in the condenser in a pump-down. Next sporlan directs you to weigh in the additional refrigerant needed for low ambient conditions into the "high side";which is really why the receiver tank is there-to store the extra refrigerant needed for low ambient conditions. Therefore the normal charge should be able to be "stored" in the condenser at pump-down, alllowing you to weigh in the additional low ambient charge in the receiver that has been isolated from the condenser in a pump-down.