No condensate from HVAC drain
I am a first time homeowner of a 45 year old ranch with a 22 year old HVAC, and the condensate line drain for the AC is dry, although the 22 year old system is working. The outside condenser is clean, but does seem to run a lot, inside filter is replaced at regular frequency. I do have a dehumidifier running in the basement, collecting over 1.5 gallons/day, but the independent humidistat in the basement averages about 70%. At first I thought it was a clogged line, but it is not. How do I without knowledge of HVAC systems or local contractors/service personnel depend on their assessment, as the system is functional--but AC without condensate??? Doesn't make sense to me. Any ideas, how does one approach the problem if there is one? Central Illinois humidity without condensate...? Thanks. John.
Required Trouble Shooting Data
Quote:
Originally Posted by
rascally
There is only one drain line to the stand pipe adjacent to the HVAC system. It's a clear flexible tubing that starts from the pan at the bottom of the evaporator coil and runs to the stand pipe, a distance of maybe 4'.
As far as pressures go, I do not have the equipment to check them. But if I'm understanding correctly, you are thinking that I'm getting minimal cooling from the system running a lot, and the stand alone dehumidifier is acting like a slave unit because the system may be low on refrigerant? FYI The stand alone dehumidifier is set to run constantly on high.
My advice: get a low cost humidity gage at a local hardware store & see what the percentage-RH is in your home, I can cross-reference that to the wet bulb depression.
TROUBLE SHOOTING DATA
Age a unit & EER or SEER Rating ________
SF of home & major city near you __________
Outdoor temperature: _____________
Outdoor condenser’s DB discharge-air-temperature ___
In-Door temp DB and WB: ___________
Air Handler's Total-ESP: _____________
Suction-Vapor line temperature: ____________
Liquid line temperature: ______________
Superheat & Subcooling: _____________
Return air temp DB and WB, or %RH: ____________
Supply air temp DB and WB, or %RH: ____________
If you want meaningful help, provide us with most, if not all, of the above EASY TO TAKE data.
Then perhaps, we can ballpark an opinion on what the unit is doing.:)