Your new furnace most likely has significantly more heating capacity than your old one, and has much higher airflow requirements.
I hope they increased your ductwork too.
Did they do a load calculation, or just replace input capacity for input capacity?
How to stop a Trane: Buy Westinghouse equipment; they make train brakes too.
See? Not so hard. Just a matter of switching suppliers.
I agree, sounds like a LOT of furnace for that house! Was a Manual-J Calc done on the home when you got a bid?
A static test should be done, and also temp rise.
The exhaust vent and cold air intake are 3"x 6' w 3 elbows
returns are 2-14"x8" and a 6" round
send vents 10"x8" , 10"x24", 18"x8"
Rheem was 80 vented to chimney .
If I am over sized what are my options . None of the 4 contractors did static tests etc. Looks like I have a bigger problem than a switch eh.
Since it was just installed, I would be demanding to see the load calculation. And if it is in fact oversized, I would be wanting the proper sized unit.
If the unit is sized properly and the ductwork is the problem, then you need new ductwork. But if the contractor never mentioned the need for ductwork, I would be asking for pretty good price.