What is the lowest suction superheat allowed when using screw compressors on a med temp rack?
I read 4 to 10 is normal due to efficiency.
Thanks
Printable View
What is the lowest suction superheat allowed when using screw compressors on a med temp rack?
I read 4 to 10 is normal due to efficiency.
Thanks
A specific Make & Model number would give you a direct answer.
Other than that, I've seen & read 10* to 20* suction superheat on screw compressors.
hsk7461-80 bitzer compressors on a medium temp rack using 404A