Originally Posted by
jpsmith1cm
You said that you measured a 38 pound suction line with 414b, then disagreed with me when I pointed out that it was impossible for ice to form at that condition. (47 degrees Saturation Temp)
Didn't disagree, was just trying to explain myself better. I swear to you that with my 38lb suction I had a 32degree suction line, and before I added the extra refrigerant my suction temp was 25degrees. I even checked my guage with another gauge.
You said that you thought that you should use the bubble point (liquid side) for the suction line (32 Saturation temp). This is incorrect, you would use DEW point for the suction side of the system.
I agree you use dew point for suction side. But with the readings I was getting that didnt add up. so I thought to myself maybe because I'm flooding and there is liquid in the suction line that I should look at bubble point. Because the readings made sense the, but maybe I'm way off with that.
So, I'm using what you've given me of your readings and some simple math to point out why I think that your readings are erroneous.
You can call me an arrogant prick if you like, I've been called worse and I'm still standing.
What I do know is refrigeration, and something here isn't adding up.