i ordered a t-state for a old true 2 door freezer
i came with a relay and some new wiring, and no instructions..
true is closed
anyone got these instal instructions?
Printable View
i ordered a t-state for a old true 2 door freezer
i came with a relay and some new wiring, and no instructions..
true is closed
anyone got these instal instructions?
If there is a Grasslin clock in the unit you need the relay. If it's a Paragon you don't. The relay was added because the inrush of current was causing the contacts on the Grasslin timers to weld. Someone here might have a wiring diagram. Wish I could be more help The relay would be located in the chase the compressor pugs into
it has a regular 8141-00 timer..so i can just replace the t-stat then??
Yes.
Here's a link in the Educational Forums for the 2007 True Service Manual which has a section on temperature controls which covers those relays:
http://hvac-talk.com/vbb/showthread....-Manufacturing
If the new thermostat is a Danfoss and the compressor is larger than a 1/3 hp, you will need the relay.
wow, thanks icemeister..