A reasonable {Not short though} ROI might be to specify SEER 15 instead of SEER 13 in Houston TX.
10 year savings might be ~ $2,000
______ SEER ……. kW/Ton
_____ 13 ……. 1.14
______ 15 ……. 1.04
______ SEER 13 vs 15
___________ ……. 1.0962
______ 2,800 ……. Operating Hours per Year
______ 7 ……. Tons approx. for 3,600 Sq. Feet
______ 7.28 ……. kW for SEER 15
______ 20,384 ……. kW-Hours per year
______ $0.080 ……. $/ kw 2012
______ $1,630.72 ……. $/kW Annual SEER 15
______ 1.0962 ……. SEER 13 vs 15
______ $1,787.52 ……. $/kW Annual SEER 15
______ $156.80 ……. Annual Savings
______ $1,568.00 ……. 10 year Savings
______ $1,957.86 ……. 4% Year Escalation in Electric Rate
________________________________ 2012 _________ $0.080
2013 $163.07 1.04 ______________ 1 1.040 __ $0.083
2014 $169.59 …….. ______________ 2 1.082 __ $0.087
2015 $176.38 …….. ______________ 3 1.125 __ $0.090
2016 $183.43 …….. ______________ 4 1.170 __ $0.094
2017 $190.77 …….. ______________ 5 1.217 __ $0.097
2018 $198.40 …….. ______________ 6 1.265 __ $0.101
2019 $206.34 …….. ______________ 7 1.316 __ $0.105
2020 $214.59 …….. ______________ 8 1.369 __ $0.109
2021 $223.18 …….. ______________ 9 1.423 __ $0.114
2022 $232.10 …….. ______________ 10 1.480 __ $0.118
If any mechanical contractor can not EASILY provide theses specifics or quite similar,
they are not adequately schooled in Energy Savings versus SEER rating and Life Cycle Cost$.
If one tells you your savings will be 30% for SEER 15 versus 13,
they're "using Smoke & Mirrors."
Whether the energy savings are actually achieved depends on the contractors competence
on the initial installation
and whether you select an annual maintenance agreement.
Of course, the annual maintenance agreement will be about equal to the savings.