It's important to note that the electric meter is on the buildiing, not the air handlers, VAVs, or compressors. Depending on what sort of system you have and what kind of shape your air-side controls are in, it may be better to reset static pressure instead of discharge air temp. Maybe even more so in a system with parallel or series fans, because you can already get a lot of turndown on the main fans already. You can reset based on critical zone(s), average space temperature, outside ambient, and many other things. Ya gotta look at the entire system.
Let's say you have large tonnage rooftops with recip compressors for example. When you reset discharge air, what are all of the starts and stops costing you on those compressors? In both mechanical wear & tear and kw usage. Now is the time of year here when recips are cycled to death. Let's say you have a central plant with 2 centrifugal chillers with older controls. from an energy standpoint, is it better to unload the chillers or back down the speed of the secondary pumps? Depending on if you reset static or discharge air, it could do either.
It sounds like you're already approaching the energy usage as a system problem, and this is how it needs to be approached.