Here is the replacement style module.Attachment 323681
Printable View
Here is the replacement style module.Attachment 323681
I've seen one before, just didn't remember it.
Here is the one that York is supplying here. Attachment 323881Attachment 323891
Sent from my iPhone 4s
using Tapatalk
So whats it not doing now.
Replace the roll-out switch. This is a common problem with these units. You will read continuity, and 24V through the switch to the R.O. terminal, but it will not pass the proper current to operate the board.
I was that kid once. Now I replace it with every failed module.
I've always used the Honeywell with the continuous retry to prevent nuisance lockouts. Just needs a little rewiring.
I had a similar call with no ignition, and was told it was running motor due to venting failure. I am still waiting for final answer from my boss this week as they replaced venting on friday.