liquid line small line frozen start near furnece ( exv) dont blow heat in heat mode ac works ok but only around 12-15 f diffrent beetwen in and out
Printable View
liquid line small line frozen start near furnece ( exv) dont blow heat in heat mode ac works ok but only around 12-15 f diffrent beetwen in and out
restriction at indoor check valve if freezing in heat mode, and TXV if in cooling.
Can you shoot a pic of it frozen?So we see what it is exactly doing.