Intelipak Remote pot.
Does anybody know what the ohms value Trane likes for the remote economizer minimum position. I think it is TB-14 terminal 8 and 9, but the 135ohm kele control that is hooked up has no effect on the position. Is is programming or the wrong ohm value? Any advice?
-
i don't believe that there is a TB14...i guessed at one of the 78,474 different model numbers that make up Intellipaks but then I gave up.
-
I believe it's 270ohm. Also, you need to set the default OA min position setpoint source to remote pot. It's under setpoints>setpoint source.
-
I will give it a try. I am tempted to purchase the remote pot from Trane just to see what the ohm value is.