Originally Posted by
CraziFuzzy
Did you ever get this sorted? I'm not sure it was every really explained what you need the extra volume for. The idea is, the cycling is due to a difference in chiller capacity, and system load. This results in total heat being either removed, or added to the system. This heat results in a temperature change in the system, which leads to the cycling, where the temp starts swinging the other way. There is no 'fix' to remove the cycling - and a variable flow system is going to have the same problem. All you can hope to do is slow down the cycling. This is where loop volume comes in (A chilled water buffer tank). By increasing the overall system volume, the rate of temp change for a given imbalance is greatly reduced. Slowing the rate of temperature change will slow down the staging up and down rate.
That said, there are other advantages (on the energy saving front) from using a primary/secondary system, and getting rid of the 3-way valves. Currently, you are using extra electricity most the year just to move water in a circle, for no real reason, other than the system was easier to design. You can fix two problems in one by using a chilled water buffer as the decoupler between a primary and secondary system. Put a fixed speed primary pump (they don't have to be very big) for each of the chiller modules, that only turns on when that chiller is needed. Get rid of the 3-way valves, and use a VFD on the system pumps (which would now be secondary pumps).