  • 04-12-2013, 06:51 PM
    gasser65
    No, upflow. Wierd I know, but it fixed it in this case.
  • 04-12-2013, 06:19 PM
    hvacvegas
    Quote Originally Posted by gasser65 View Post
    Tstat isn't wired wrong so strip heat runs at the same time as the heat pump, right? I just fixed one that had been there for ten years with that problem. Customer had been told the HP switch was a safety feature and just reset it if it tripped - it tripped in heat mode almost everyday since it was installed.
    Thats gotta be a downflow right?
  • 04-12-2013, 05:34 PM
    gasser65
    Tstat isn't wired wrong so strip heat runs at the same time as the heat pump, right? I just fixed one that had been there for ten years with that problem. Customer had been told the HP switch was a safety feature and just reset it if it tripped - it tripped in heat mode almost everyday since it was installed.
  • 04-12-2013, 11:36 AM
    Heatpump1$
    After sharing the operating data with the Frigidaire tech he advised to pull charge. The install is two years old and an approved combination. Pressures still are a little high but unit has 28 degree td and has been running since. Temp across drier is good. The strange part is that the unit was under charged by 5 # and the high pressure occurred sooner.
  • 04-11-2013, 11:10 PM
    hvacvegas
    Nameplate isn't for approved coil, it's for the "most commonly used coil".

    Just like DOE ratings on equiptment.
  • 04-11-2013, 09:08 PM
    brian.cornell
    Is this a newer heat pump installed on an existing coil if so charging by weight on nameplate would probably be slightly overcharged. If you have checked temp across drier and indoor coil for cleanliness already than I would say outdoor TXV
  • 04-10-2013, 11:35 AM
    Heatpump1$
    This installation is using an approved coil and I did not ad extra for the 35 foot lineset.
  • 04-10-2013, 10:59 AM
    second opinion
    Quote Originally Posted by Heatpump1$ View Post
    I pulled 1.5# of charge out and this seems to have everything working good. First time I have overcharged by weighing at name plate. Every brand has their own quirks. Thank you everyone on your responses.
    Nameplate charge means nothing unless you have the tested coil and line set, unless it is a package unit
  • 04-10-2013, 10:29 AM
    Heatpump1$
    I pulled 1.5# of charge out and this seems to have everything working good. First time I have overcharged by weighing at name plate. Every brand has their own quirks. Thank you everyone on your responses.
  • 04-09-2013, 01:36 AM
    Heatpump1$
    to daniel87829,
    what is ymmv? Thanks
  • 04-09-2013, 01:08 AM
    Heatpump1$
    The unit was under charged upon first visit and it would trip sooner than with full charge. Suction pressure with correct charge stayed fairly constant but head pressure steadly climbed. Opening up tx only seemed to delay the high pressure trip. There was no pressure difference across the filter drier.
  • 04-09-2013, 12:56 AM
    Barrettservices
    Quote Originally Posted by Heatpump1$ View Post
    Hello All,
    Having an issue with a heat pump running at high discharge temp and pressure and tripping on high pressure. I pulled charge and weighed it back in. Was low on charge which was caused by a poor service port gasket. Unit runs a little longer and trips on high pressure. Filters good, coil clean, charge good. Suspect outdoor unit txv. Any input would be greatly appreciated.
    Whats you suction pressures at before it trips? Is there a charge chart on the panel of this unit that shows the pressures? Have seen many heat pumps that were weighed in be overcharged in heat mode.
  • 04-09-2013, 12:28 AM
    daniel87829
    Is there a filter drier? could the installer have allowed gunk/solder to block a line? During install over heated line overheating valve?
    Possible metering device clog/ malf.
    Maybe do temp check at discharge before port, after port, or maybe on line setup to metering device
    Top of head thought ymmv
    Sent from my LGL35G using Tapatalk 2
  • 04-09-2013, 12:25 AM
    Heatpump1$
    Had a look and it is clean.
  • 04-09-2013, 12:21 AM
    PVCOOLING
    Make sure the indoor coil is clean.
  • 04-09-2013, 12:20 AM
    Heatpump1$
    Frigidaire FT4BF-060k
  • 04-09-2013, 12:10 AM
    hvacvegas
    model numbers.
  • 04-08-2013, 11:49 PM
    Heatpump1$

    Cause of high pressure in heat pump heating.

    Hello All,
    Having an issue with a heat pump running at high discharge temp and pressure and tripping on high pressure. I pulled charge and weighed it back in. Was low on charge which was caused by a poor service port gasket. Unit runs a little longer and trips on high pressure. Filters good, coil clean, charge good. Suspect outdoor unit txv. Any input would be greatly appreciated.

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •