  • 02-17-2013, 04:54 PM
    timebuilder
    Quote Originally Posted by Liamd8 View Post
    Try removing that wire feeding the main valve portion of the gas valve, and see what happens. Maybe the valve is going bad and when power is fed to the main valve solenoid in the gas valve it's causing a strain on the board causing it to restart the ignition sequence.
    That would be one that I haven't seen.
  • 02-17-2013, 03:41 PM
    RDorr92788
    Quote Originally Posted by Liamd8 View Post
    Try removing that wire feeding the main valve portion of the gas valve, and see what happens. Maybe the valve is going bad and when power is fed to the main valve solenoid in the gas valve it's causing a strain on the board causing it to restart the ignition sequence.
    ok
  • 02-17-2013, 03:26 PM
    Liamd8
    Try removing that wire feeding the main valve portion of the gas valve, and see what happens. Maybe the valve is going bad and when power is fed to the main valve solenoid in the gas valve it's causing a strain on the board causing it to restart the ignition sequence.
  • 02-17-2013, 02:15 PM
    timebuilder
    This reminds me of the 50's TV show "what's my line?"

    Look at how good this famous star looked in those days....

    http://www.youtube.com/watch?v=1gR-vU44gd4
  • 02-17-2013, 02:07 PM
    RDorr92788
    no. it has a flame sensor.
  • 02-17-2013, 02:06 PM
    timebuilder
    Mercury switch for the pilot with three terminals?
  • 02-17-2013, 01:01 PM
    RDorr92788
    facing the burner compartment , the flue and gas line come in at the right hand side near the corner. the inducer is at he bottom and the burners are on top. Tan
  • 02-17-2013, 12:57 PM
    timebuilder
    Quote Originally Posted by RDorr92788 View Post
    no serial available

    If you are facing the unit, is the flue over on the right hand end, where the gas line comes in, OR

    is it in the middle, with the gas line, right in front of you as you face the unit?

    Is the unit a light green color?
  • 02-17-2013, 12:51 PM
    RDorr92788
    no serial available
  • 02-17-2013, 12:50 PM
    RDorr92788
    thats what i was thinking also, no i assumed pressures were ok. i will check it tue. assumtion is the mother of all ****ups.
  • 02-17-2013, 12:45 PM
    timebuilder
    Did you get a serial number?
  • 02-17-2013, 12:43 PM
    RDorr92788
    yes this a gaspack rtu. no I did not get any pics. most likely i will be back there on Tue. I can snap a few then.
  • 02-17-2013, 12:40 PM
    hvac wiz 79
    pilot should remain energized in the sequence. You attempt checking/setting pressures?

    Sent from my SGH-T999 using Tapatalk 2
  • 02-17-2013, 12:32 PM
    timebuilder
    Quote Originally Posted by RDorr92788 View Post
    it is being used on a commercial building
    When you say "on" a commercial building, do you mean this is a rooftop unit? Did you take a picture?
  • 02-17-2013, 12:27 PM
    RDorr92788
    the more i look, I am not finding this model # on line. the tag is bleached out and this # was written on unit above tag. could this be a 584apo?
    it is 3 phase
  • 02-17-2013, 12:16 PM
    RDorr92788
    it is being used on a commercial building
  • 02-17-2013, 12:11 PM
    timebuilder
    This is a commercial unit??
  • 02-17-2013, 11:42 AM
    RDorr92788

    White Rogers Ignition module

    I am working on a Payne m/n 584apw048080aa?g. I had an ignition problem with the orignal ignition module g770ngc-7. I installed a white rodgers module 50d50-843. followed the wiring diagram,added a burner ground, installed the green C chip. the ignitor sparks, lites pilot, main gas starts and shuts off pilot, no flame, main shuts off and restarts cycle. i have had this same problem with a Carrier furnace, tried a Robertshaw mod then a White Rodgers and both acted the same. is there something i am missing? is there a trick that is not in the paperwork?