Reply to Thread

Post a reply to the thread: 30 Ton Voyager

Your Message

 
 

You may choose an icon for your message from this list

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Additional Options

  • Will turn www.example.com into [URL]http://www.example.com[/URL].

Topic Review (Newest First)

  • 08-10-2012, 02:25 PM
    jdblack
    Sorry for the delay on part number. Trane board 6400-0882-01 rev e. Assy 6400-0883-03 rev n.

    Sent from my ERIS using Tapatalk 2
  • 08-04-2012, 02:56 PM
    hands
    Quote Originally Posted by jdblack View Post
    you need to upgrade the main control board. the problem gets solved by shutting down the first stage for ten seconds then bring both stages on together. this fires all three fans at the same time. its the only repair because once you get a fan pinwheeling it cant overcome when it starts.

    Sent from my MID7012 using Tapatalk 2
    As I posted earlier, the first stage does shut down for about five to ten seconds then brings on both stages. Condenser fan three would run backwards. After replacing the motor and letting the unit run on its own, the fan was running the correct direction.

    I have another unit doing the same thing at times. I hate to replace the motor since it's still running. It seems that I have read about a device that installs on motors to prevent the blades from spinning backwards. I need to look into more.
  • 08-03-2012, 11:35 PM
    alcomech
    Quote Originally Posted by jdblack View Post
    you need to upgrade the main control board. the problem gets solved by shutting down the first stage for ten seconds then bring both stages on together. this fires all three fans at the same time. its the only repair because once you get a fan pinwheeling it cant overcome when it starts.

    Sent from my MID7012 using Tapatalk 2
    That is a two fold repair in that in a two stage circuit with a tandem compressor as the second stage, it is very common in a high ambient condition that the short cycling can not over come the head pressure on such a short delay. This will create a high LRA and trip the circuit breaker depending on which circuit short cycled.

    It sounds like Trane has changed the starting strategy with this new board.

    _______________
    Understand the symptoms and you will find the solution.
  • 08-03-2012, 11:25 PM
    alcomech
    Quote Originally Posted by jdblack View Post
    you need to upgrade the main control board. the problem gets solved by shutting down the first stage for ten seconds then bring both stages on together. this fires all three fans at the same time. its the only repair because once you get a fan pinwheeling it cant overcome when it starts.

    Sent from my MID7012 using Tapatalk 2
    Is there a new bulletin on this? And is this for the Microtel UCM or Reliatel.
    I wonder if you know what the new revision number is for the updated UCM board.

    Thats definitely a solution.
  • 08-03-2012, 11:18 PM
    jdblack
    you need to upgrade the main control board. the problem gets solved by shutting down the first stage for ten seconds then bring both stages on together. this fires all three fans at the same time. its the only repair because once you get a fan pinwheeling it cant overcome when it starts.

    Sent from my MID7012 using Tapatalk 2
  • 08-03-2012, 11:18 PM
    alcomech
    That run cap is usually rated at 25 MFD and any thing less would cause the symptoms which you are having. Recheck actual microfarad reading and verify that this is a quality run cap, GE or OEM.
  • 08-03-2012, 11:12 PM
    alcomech
    Just some info on low ambient control and condenser fan motor operation which is controlled by the outside air sensor.

    Outdoor Motor (ODM2) will be turned “OFF” since the UCP is sensing a low ambient
    condition.

    I have had Voyagers with the same symptoms and going off on high head pressure. Found that the OSA sensor had a degraded performance and was out of calibration by 10 degrees. It ohm'd out just fine but had a voltage drop which was inconsistent with actual temperature. Changed out the sensor ($9.00) and haven't been back since.

    Per Trane: During low ambient operation compressor run time is counted and
    accumulated by the UCP. Low ambient operation is defined as 55° F for single condenser fan units, and 40° F for dual condenser fan units.

    Hope this helps

    _______________________
    Understand the symptoms and you will find a solution.
  • 07-24-2012, 05:44 PM
    Workin4TheMan
    Quote Originally Posted by hands View Post
    I replaced the capacitor for fan three first, but it didn't make a difference. I then tested the other two capacitors and they were good. The thing that got me was I could switch the plug connectors and the motor would run fine. I switched around fan one and fan three so three was the first fan and it ran good, but then the other fan one would run backwards and so on. I was thinking the motors were getting weak. But the new motor did the same thing when I ran them in test mode.
    Looks like a wiring issue at the capacitor since a new motor did the same, check the diagram and wire #'s that land on the cap for the motor that is going backwards and verify that the common and capacitor lead are reversed at the capacitor. Then reverse the two leads at the capacitor (leaving the common feed to the caps in place) and it should now spin correct. They are all the same color so it's easy to get them mixed up.

    Good Luck...
  • 07-24-2012, 01:20 AM
    pillclinton209
    Did you check voltage to motors when they run backwards and amp draw ?
  • 07-21-2012, 11:09 PM
    hands
    Quote Originally Posted by Workin4TheMan View Post
    The only problem I have had with fans spinning backwards on this unit (and it was twice in one summer) was a 2 yr old unit that the caps failed on at different times. First was fan 3, then one of the 2 for the first stage. Replaced both caps only, motors were fine. Haven't had that problem since. Are you sure you changed the right cap? And did you check the other 2?

    Had a ton of cap failures in the last 2 yrs...........
    I replaced the capacitor for fan three first, but it didn't make a difference. I then tested the other two capacitors and they were good. The thing that got me was I could switch the plug connectors and the motor would run fine. I switched around fan one and fan three so three was the first fan and it ran good, but then the other fan one would run backwards and so on. I was thinking the motors were getting weak. But the new motor did the same thing when I ran them in test mode.
  • 07-21-2012, 03:51 PM
    Workin4TheMan
    The only problem I have had with fans spinning backwards on this unit (and it was twice in one summer) was a 2 yr old unit that the caps failed on at different times. First was fan 3, then one of the 2 for the first stage. Replaced both caps only, motors were fine. Haven't had that problem since. Are you sure you changed the right cap? And did you check the other 2?

    Had a ton of cap failures in the last 2 yrs...........
  • 07-21-2012, 11:22 AM
    Dallas Duster
    Quote Originally Posted by hands View Post
    Yes, I have split Trane and Carrier coils many times. But on the 20 ton Trane RTU's I have worked on, the coils can't be split. I havn't checked the 30 ton unit I have been talking about because you have to lift the top to see how the coil is made.

    Have you been able to split coils on 30 ton Trane Voyager's. The Model number is #YCD360A4HK1A2DH1ABC00F0H00000.
    I've done 301's and have heard about the 360's and 420's. Me thinks super fitter tech must know something about it.
  • 07-21-2012, 11:04 AM
    hands
    Quote Originally Posted by Dallas Duster View Post
    Have you ever split a Trane coil Hands?
    Yes, I have split Trane and Carrier coils many times. But on the 20 ton Trane RTU's I have worked on, the coils can't be split. I havn't checked the 30 ton unit I have been talking about because you have to lift the top to see how the coil is made.

    Have you been able to split coils on 30 ton Trane Voyager's. The Model number is #YCD360A4HK1A2DH1ABC00F0H00000.
  • 07-21-2012, 10:39 AM
    Dallas Duster
    Quote Originally Posted by hands View Post
    Sorry for the delay, I just got back from vacation.

    Six- The fans are pinwheeling, if one fans is on, the other two pinwheel, but not real fast so the 2nd fan can overcome it when it starts. When two fans are running, the 3rd is pinwheeling fast and then runs back wards. The schematic shows four fans but has a small insert for three fans, but not all of the wire numbers match. Trane likes to do this for some reason.

    gwoner-The k4 relay is not welded shut, I had to jump it at times to get the fan to run.

    superfittertech- It is a two coil condenser, not sure if they can be split. You would four guys or a crane to get the top off. But if it is like the 20 ton units, the coil can't be split.

    Have you ever split a Trane coil Hands?
  • 07-21-2012, 10:26 AM
    hands
    Sorry for the delay, I just got back from vacation.

    Six- The fans are pinwheeling, if one fans is on, the other two pinwheel, but not real fast so the 2nd fan can overcome it when it starts. When two fans are running, the 3rd is pinwheeling fast and then runs back wards. The schematic shows four fans but has a small insert for three fans, but not all of the wire numbers match. Trane likes to do this for some reason.

    gwoner-The k4 relay is not welded shut, I had to jump it at times to get the fan to run.

    superfittertech- It is a two coil condenser, not sure if they can be split. You would four guys or a crane to get the top off. But if it is like the 20 ton units, the coil can't be split.
  • 07-17-2012, 04:10 PM
    beenthere
    Real fun to clean.
  • 07-15-2012, 09:07 PM
    superfittertech
    those are triple split coils
  • 07-14-2012, 08:44 PM
    gwoner

    fans

    check the k4 relay . I bet your contacts are welded closed.
  • 07-14-2012, 02:17 PM
    Dallas Duster
    Don't you have to split those coils also?
  • 07-14-2012, 01:14 PM
    Six
    If two fans are spinning backwards its most likely because they're pinwheeling.

    Air running through the blades spinning them backwards.

    If they're getting power to a leg on the motor when they shouldnt then someone monkeyed with the wiring and it needs to be repaired.

    Should be a schematic you can refer to.
This thread has more than 20 replies. Click here to review the whole thread.