  • 11-01-2012, 12:14 AM
    captn-b
    Could not tell you
    Other than the bypass was ran with the line set it has been disconnected for ever since I have done work at this facility which is eleven years
  • 11-01-2012, 12:00 AM
    heatingman
    How was the hot gas originally piped?
  • 10-31-2012, 06:52 PM
    jayguy
    Quote Originally Posted by captn-b View Post
    ...Drained some oil, still 15 deg super heat top of compressor no more than 130 deg...
    what is your condensing temperature at 130F? i would start to be worried if the condensing temperature was above 80F with a 130F discharge temperature.
  • 10-31-2012, 01:33 AM
    captn-b
    Ok. I'll start by saying i've never done anything over 5 tons before this project.
    I bid it for 4 installers and 2 helpers to have 2 40 ton condesers changed out in one week turn key.
    After my boss got involed I ended up with 1 helper 1 startup guy and me. That being sayed the existing condensers and airhandlers are on the roof with no more than 5' of rise in the lineset so no traps needed. Existing line sets were roughly 75' 2-1/8 O.D. & 7/8 O.D well within the Trane specs. Existing evap coil met Trane specs for handling 410. Filter dryer and suction filter installed per Tranes Piping diagram. A piss load of RX-11 was used to flush lineset and coil but next day oil would still migrate and start dripping out. ( not a confidence builder )
    When I started the first unit on Thursday all was good. got a 15 deg super heat as recommened per install manual. Oil at sight glass clear with few bubbles. No slugging.
    Next morning it looked like the mineral oil migrated back to compressors finally and sight glass was white with bubbles, compressors sounded labored. Drained some oil, still 15 deg super heat top of compressor no more than 130 deg. Plan on completely changeing out comp oil this Friday when new oil shows up ( apparently not a stock item in San Diego) Pray condensers hold out.
    Same on both units, less on one than the other. Will use Fracto meter to test percentage.
    As far as the hot gas bypas, according to install manual it is not recommened per install guide on constant volume system and it refers to using frost stat instead.
    I'm currently not slugging, and from what I can see the original installers of the R-22 system did not adjust the TXV's properly, and in the winter with the extreme heat load of the ovens in the space that this unit serves, it would drop below optium levels of super heat and slug the compressors.
    I'm learning as I go and hope I at least break even on this one. Thank God this is a good cotomer and even if I loose a little bit a money they hand me enough work to make u for it in the long run.
  • 10-30-2012, 09:57 PM
    alcomech
    It sound like you have it under control, but what will frost stats do for the design of the system? Safety controls are necessary for a complete and properly designed system, just as hi and low pressure safety cut out's are, but they do absolutely nothing for equipment performance.

    I am one who would like to learn from your great endeavor of trying to successfully retrofit an old problematic R-22 system with a new blend such as 410A. You are not the first and definitely will not be the last to attempt a retrofit of this type. Heck to even try to keep the existing coils is just not the best option either. It’s clear that the odds are against you. But I will pray for you.

    Unless you have done a retrofit of this size before and successfully completed an installation where the system has been trouble free with years of service, you are just simply asking for trouble. A job like this takes trial and error as you are paving a new path for yourself. You cannot just simply change out equipment like this and expect it to work.

    How much is a new compressor replacement for a 40 ton system? Let me think- uh. Oh, 2- 10 ton tandem scrolls a pop, along with the additional cleanup and if not caught in time, possibly a severe burn out which will just increase the cost.

    But I know you don’t want to hear any of that. So…what have you done to improve the performance of the existing system? Have you thought of what caused the old system to fail? I know that you said that oil was slugging the compressors but everyone knows that is just a symptom of your problem. What have you done to prevent migration of oil and what improvement have you made to prevent this from happening again?

    If you are slugging oil to the compressor at start up and possibly liquid refrigerant, you will need to identify what is causing this. You may want to consider a suction accumulator, but this will need to be properly design for your system.
    There is much more to consider. Such as total developed length of refrigerant piping along with total vertical lift or drop.
    How about capacity control under a part loaded condition as well as operation of the condenser under a low ambient temperature.

    You say that you removed the traps but why. Are they not needed?

    As far as the hot gas by-pass I strongly suggest that you incorporate one for each circuit. It is needed for capacity control and without some sort of refrigerant evaporator control it is just not a good idea, especially with the cold weather that is here.
  • 10-30-2012, 08:53 PM
    allstar08
    Tell me why you are not using the hot gas. You have peeked my interest.
  • 10-30-2012, 08:52 PM
    allstar08
    The problem is my compressors might be getting hit with liquid. The failures have been mechanical. The oil had no acid in it when I tested it. It is almost like the bearings are getting washed out. They sounded hideous.
  • 10-29-2012, 09:53 PM
    captn-b
    Thanks for the info
  • 10-29-2012, 09:51 PM
    captn-b
    Yes I changed out all the goodies and rerouted the line set to get rid of the traps and low spots
    Trane confirmed that the existing coil could handle 410
    The existing unit killed quite a few compressors and it looks like it was because the way it was set up it kept lugging the compressors with oil
    I'm not using the hot gas bypas but frost stats instead and so far were not slugging
  • 10-29-2012, 09:44 PM
    jayguy
    i know that you are just asking about oil changes, but you did change out the compressors too...right? txv's? you might consider running for the border when this is done. change your phone number. change the company name. mother nature doesn't care if your budget can't handle it. r22 and r410a are 2 very different refrigerants and they require the proper engineering and design to make them work. you will probably be changing out the evaporators before too long.

    not that it has to do with your original question, but why did the old compressors not last long? if it wasn't corrected, then, you should know that the new compressors are more expensive to replace than the old compressors were.
  • 10-29-2012, 09:31 PM
    mikeacman
    I started with 100% wrong oil ,,,my case was extreme ,,,being burned by that I just won't guess anymore ....sounds like you have a handle on it ...
  • 10-29-2012, 09:11 PM
    captn-b
    Thanks for the info
    I flushed the holy crap out of the system but there is no way to get all the mineral oil out
    I hope the compressor collects most of it and it doesn't take to many changes
    I get the two oils don't mix but I wouldn't think it would damage the compressors to bad scrolls are fairly forgiving ( I pray )
  • 10-29-2012, 08:47 PM
    mikeacman
    Quote Originally Posted by captn-b View Post
    Allstar08,
    What were the problems you that you were having and how many times did you change the oil
    I noticed after the first day we had to drain some of the oil because the compressors were getting to full
    im not the OP ....but I had a run in with mixed oil....



    I had a factory ordered water cooled (condensor ,air over evap) split that was built to run on R134A and carrier filled the comps with mineral oil .... I spent a couple days and if I remember went thru 20 gallons (for two 06E's) of oil before I was under 5% mineral to poe ....
    im thinking around 5 changes per compressor ....
    134 because it was a refrigerator factory and they wanted a cooling system for their offices that ran on 134A,just like their product

    my experience was the mineral tended to lay out in the system and as you got more poe in it all started coming back at a rate that I had to babysit it .... at first the oil just left and did not come back . I had a gut feeling before I started it that it was wrong but was shown it was ordered for 134A service . My gut was right.
    .

    Without an oil refrac I would have been guessing ....that unit has been running close to ten years now with no compressor failures....
  • 10-29-2012, 08:32 PM
    captn-b
    Allstar08,
    What were the problems you that you were having and how many times did you change the oil
    I noticed after the first day we had to drain some of the oil because the compressors were getting to full
  • 10-29-2012, 08:25 PM
    captn-b
    It is a Trane and new oil is 4 days out. I hope the compressors last that long there not acting up or over heating I just don't like the look of the oil thru the sight glass
  • 10-29-2012, 08:23 PM
    captn-b
    I will be picking one up as you suggested
    I definetly see a diferance in the oil and have ordered poly oil in to replace . I just can't believe how expensive it is
    Thanks
  • 10-29-2012, 06:39 PM
    mikeacman
    Quote Originally Posted by captn-b View Post
    Yes and I plan on changeling out compressor oil a couple of times just to make sure it's more poly than mineral
    as I mentioned you could use an oil refractometer and know for sure ...

    I will shut up now...
  • 10-29-2012, 12:17 AM
    captn-b
    Yes and I plan on changeling out compressor oil a couple of times just to make sure it's more poly than mineral
  • 10-28-2012, 11:01 PM
    allstar08
    I have been down this road and I am still on it. I am in the process of replacing both compressors. Is it a Trane?
  • 10-26-2012, 09:32 PM
    captn-b
    Thanks for all the advise. I did cut out all the low spots and blew a rag- plug thru the line set. Started one side of one unit today and low and behold no problems. Will be hopefully start other circuits tommorow. I pulled a deep vac 4 times and introduced 410 each time to grab any moisture. Oil at compressers looks good and I am getting 40 degrees at evap coil.