I like my Megger MIT 410EN. I had an Intellipack doing the same thing and found the bearings in the blower motor had become magnetized and were drawing in particulates causing an intermittent ground fault. Had to replace the motor on that one.
I use the fluke 1587(i believe that's the correct model number) it's a meggar/meter combo. Love it. Found plenty of nuisance problems, and i use it when my reg meter takes a plunge.
Fluke 87 V is a great meter and has a meg ohm function however it is not a true Megger or equal to Biddle/Megger
Originally Posted by anthonyac1 ...m#tr16016gt4cn1strodlf00aooco S#033032h117 date of manufacture code is after the 'H'...11th week, 2007. the affected ribbon cable date codes were 46th week, 2006 (467) to 20th week, 2007 (207) you will need Danfoss part number: 175Z1821, 2 per drive. you should be able to go through trane to get them. reference TR1-SVA01-EN obviously, please check for a grounded motor or motor wires first as new ribbon cables will not fix that.
Originally Posted by anthonyac1 the vfd had a fault that said earth fault. to me it would mean it sensed a ground fault ohmed the blower motor and traced all the power cables leaving the drive going to the motor. I did not meg the motor maybe the insulation is breaking down. I didn't find anything bad so I restart unit and it operated fine. I restarted unit 2 times just to see if it will reoccur. I called one of the top dogs in the company and told them he said this unit has a history with that same fault so now im curious to know what causes it and what are some things to check for?? im sure I wont be going back another tech would but for future reference I would like to know..... it was the tr1 series trane vfd I was told its the same as a danfoss. Possibly Could Be Excessive Moisture Getting In PeCkerhead Of Your Motor,Verify Your Airflow,And Temperatures Maybe seal The Peckerhead Cover, Have Seen Moisture Cause This Problem Many times
Scratch that...AMB45 is the model and it is 650 bucks at Graingers.
I am not a fan of the 'megger in a meter' idea, but I also admit that I have never used one before either. The amprobe one I got at Graingers was about 500 if I remember correctly. If you want to really get into megging, then you want one that at least has a timer feature and not all of the flukes have that feature. I meg motors and compressors using the 1 minute/10 minute method whose name escapes me at the moment.
Originally Posted by jayguy Don't buy the supco toys! I personally love my amprobe amb1. Fluke makes 1 that is better but costs about double. what model fluke are you referring too? I see there are a couple of fluke meters that are multimeters with the megger function built in. I know I was looking at two different models one was about 450.oo the other was like 600.00 is something like that any good?
Originally Posted by anthonyac1 just curious what type of megger do you use? people mention the supco but id rather buy a quality tool once and know I can trust what its saying especially if im condemming a large motor!!! Don't buy the supco toys! I personally love my amprobe amb1. Fluke makes 1 that is better but costs about double.
Originally Posted by jayguy Meg your motors and fully checkout your connections. There was a batch of tr1 drives that had a faulty set of ribbon cables in it that caused this issue. I don't have my brain with me right now (computer) but when I do I can look it up. Can you get the serial number and/or the date of manufacture? just curious what type of megger do you use? people mention the supco but id rather buy a quality tool once and know I can trust what its saying especially if im condemming a large motor!!!
Originally Posted by jayguy Meg your motors and fully checkout your connections. There was a batch of tr1 drives that had a faulty set of ribbon cables in it that caused this issue. I don't have my brain with me right now (computer) but when I do I can look it up. Can you get the serial number and/or the date of manufacture? I spoke with another guy and he did tell me one time he replaced the ribbon cable for the same model about 10 months ago it was giving the same fault ever since then its still running but I thought maybe he was throwing something at me. that could be the problem. nameplate on the drive trane m#tr16016gt4cn1strodlf00aooco S#033032h117
Meg your motors and fully checkout your connections. There was a batch of tr1 drives that had a faulty set of ribbon cables in it that caused this issue. I don't have my brain with me right now (computer) but when I do I can look it up. Can you get the serial number and/or the date of manufacture?
I had a drive a little while ago that took a bath in water then started hoeing a ground fault. Did everything you just did then replaced the drive, and it's all good now. Did you not have a megger on you?
Meg your motor, check wiring for weak insulation. Could also be coming from ground issues outside of the unit. Last resort would be to disable the alarm but not recommended.
trane intellipak vfd the vfd had a fault that said earth fault. to me it would mean it sensed a ground fault ohmed the blower motor and traced all the power cables leaving the drive going to the motor. I did not meg the motor maybe the insulation is breaking down. I didn't find anything bad so I restart unit and it operated fine. I restarted unit 2 times just to see if it will reoccur. I called one of the top dogs in the company and told them he said this unit has a history with that same fault so now im curious to know what causes it and what are some things to check for?? im sure I wont be going back another tech would but for future reference I would like to know..... it was the tr1 series trane vfd I was told its the same as a danfoss.