  • 10-22-2012, 01:12 AM
    xarralu
    I know prices can't be posted in the open forum, but I was wondering if anyone has any idea of the cost of the 10 ton multiaqua chiller is? I talked to multiaqua a couple of weeks ago just for them to tell me that Trane is the distributor for their equipment in the Dallas/Fort Worth area. I have called and e-mailed every contact in the D/FW Trane office and still have not heard anything. Good 'ol Trane. Their reputation will never change!!!!
  • 10-11-2012, 11:20 PM
    xarralu
    Great, thanks for the info.
  • 10-11-2012, 03:01 PM
    CraziFuzzy
    Quote Originally Posted by xarralu View Post
    I was just trying to run some numbers of my own and I was wondering how you can up with your 2,500 mark. The last thing I have run across is this from ASHRAE.

    All in all I'm coming up with some pretty broad numbers and I was wanting to nail something down.
    my 2500 gallon number is considerably oversized, but that is for a couple reasons. part of the space has to be taken up by the termocline layer, so not the entire volume of the storage is 'usable'. also, I figured bigger is better, as tanks really aren't THAT expensive in this size range (I was looking at splitting the storage among say 3 separate tanks plumbed in series). My actual 'conservative calc' was based on how much it would take to store 24 hours of the 2 ton chiller's capacity. As such, that's:

    24,000 BTU/hr * 24 hr * 1 lb/BTU°F ÷ 8.34 lb/gal ÷ 30°F = 2302 gallons

    Previously, I had determined how much it would take to provide absolute worst case cooling on my home for the entire peak power period, which is about 3.5 tons for 8 hours. As such:

    42,000 BTU/hr * 8 hr * 1 lb/BTU°F ÷ 8.34 lb/gal ÷ 30°F = 1342 gallons

    so if all you are looking to do is shift load from the peak power period (for Time-of-use metering), it doesn't take THAT much of a storage system. It's also something that can easily be expanded upon. Starting with just 500 gallons will minimize the cycling, but adding tanks can seriously start to shift load.
  • 10-11-2012, 01:03 PM
    motoguy128
    Quote Originally Posted by xarralu View Post
    I was just trying to run some numbers of my own and I was wondering how you can up with your 2,500 mark. The last thing I have run across is this from ASHRAE.

    All in all I'm coming up with some pretty broad numbers and I was wanting to nail something down.
    That's a good question. I assume you'd have to know your average heat gain during design conditions. Then you determine what the 24 hour average is and then size your storage so your chiller is sized for hte average load and run continously but you have enough water storage.

    Its' just thermal mass. You can accomplish a similar effect if you had enough concrete or masonry walls in a home. This is why IMO, energy efficient structure design needs ot encorporate materials when possible with a lot of thermal mass. SO using ICF's. I've mentioned in another thread, that I think you could easily raise the sill plate up to at least a point level with the bottom of the 1st floor windows. Homes should be 2 story and use stucco, brick or stone on the exterior. Have deep overhangs for shading the building in the summer, and less in the winter, use interior walls (non of this open concept garbage) and use stone, brick or plaster, instead of gypsum for interior walls too. Close cell spray foam of course and unvented attics with cool roofs.

    Actually, with enough thermal mass in the structure, the need for water storage could then be sized to target a minimum cycle time at low load conditions.
  • 10-11-2012, 11:30 AM
    xarralu
    Quote Originally Posted by CraziFuzzy View Post
    I've actually figured out that I would only need about 2 tons if running at night, to provide the cooling i need during the day, with about 2500 gallons of storage...
    I was just trying to run some numbers of my own and I was wondering how you can up with your 2,500 mark. The last thing I have run across is this from ASHRAE.

    All in all I'm coming up with some pretty broad numbers and I was wanting to nail something down.
  • 10-10-2012, 01:40 PM
    CraziFuzzy
    Quote Originally Posted by Dallas Duster View Post
    Makes me wonder if you read an article in "supply house times" talking about small scale chilled after cooling as a developing market. The article was by John Siegenthaler, P.E..
    I have not, but I'm not surprised to see the article. It IS a natural progression, and a single change that opens up much more opportunities with little extra engineering. Water is the perfect medium for heat transfer in homes, mainly because of it's safety, and, if for no other reason, is already piped to every home. It takes nothing to add on 'extra features' to an established chilled water system. Want to stretch out cycle times? add in some buffering storage. Want to shift loads (something that is a much harder proposition with direct cooling), just add a larger tank. Want to zone? sure, that's simple. Want to expand the system to that new addition? sure, just add another fan-coil there. Did the chiller just die? okay, go to the store and buy another one off the shelf - they are self contained units, not requiring any recovery, charging, vacuum, etc. I know THAT part the residential part of the industry doesn't want, but in the end, it's going to happen.
  • 10-10-2012, 01:16 PM
    Dallas Duster
    Makes me wonder if you read an article in "supply house times" talking about small scale chilled after cooling as a developing market. The article was by John Siegenthaler, P.E..
  • 10-08-2012, 07:01 PM
    CraziFuzzy
    Quote Originally Posted by beenthere View Post
    Is that 2500 gallons with or without the A/C also running during the day.
    For my example, that was enough to keep the chiller OFF during the peak demand period (8 hours a day - 10am to 6pm). Power costs are the same for the other 16 hours of the day, so that was enough. That system i drew up a couple pages ago, that ran the chiller based on storage tank temps, would pretty much start topping off the tank as soon as the peak period ended.

    That calc was also based on a chilled water supply temps of 44°F, and a full return temp of 74°F, which is why it would require a large multi-stage coil, but the higher the delta-t, the better stratification you get, and the more storage you can have per gallon.
  • 10-08-2012, 06:54 PM
    beenthere
    Is that 2500 gallons with or without the A/C also running during the day.
  • 10-08-2012, 06:46 PM
    CraziFuzzy
    I've actually figured out that I would only need about 2 tons if running at night, to provide the cooling i need during the day, with about 2500 gallons of storage, but I wouldn't be able to use an off-the-shelf fan coil. I need one with a much larger chilled water coil, to provide full approach to return air temp to maximize the storage capacity. I think that's the primary problem with using that variable primary type system you posted - It is harder to ensure that max delta-t with that setup, and no way to always provide a fixed supply temp, regardless of return temp. You have to have that primary pump and 3-way recirc valve around the chiller, to ensure the outlet temp going to the storage tank is always at your supply setpoint. Running warm water into the cold end of a stratified tank is bad, as it destroys the thermocline, and overall degrades your recovery capability.
  • 10-08-2012, 06:19 PM
    xarralu
    I see what your saying, but depending on how large the tank is it might take a while before the chiller can catch up, and before you could have a decent enough leaving water temp. With the way I have it drawn out the FCU(s) can have presidence.

    If I was able to actually build a system like the way I wanted it, I would want the tanks to be very large (3,000+ gallons total). I have free electricity after 10 pm and I would like to have thermal storage if possible. In the hottest of summers my unit runs 14 hours a day (3 ton unit). So I would need 42 ton/hrs. storage plus be able to recharge the tanks. Just shootin' in the wind I would guess that a 10 ton chiller like this that CraziFuzzy had mentioned earlier would work.

    Yea, I know I'm dreaming...
  • 10-08-2012, 09:40 AM
    motoguy128
    I wonder if the buffer tank should move to the retrun side of the chiller, and the chiller draws from the top and loop return is to the top, but the bypass is to the bottom of the tank. That way you get the warmest water to the chiller most of the time even when below minimum load.

    I assume to lengthen minimum cycle times you might run the chiller to start at 44-45F and shut off at 40F.
  • 10-08-2012, 12:07 AM
    xarralu
    Attachment 315761

    If was able to do it, this is how my setup would look. Minimal amount of equipment to buy and maintain.
  • 10-07-2012, 10:11 PM
    CraziFuzzy
    While yes, it WOULD work with a single pump, it is not as flexible as a 2 pump system. This difference is even more significant when dealing with multiple 'secondary' zones. So, yes, decoupled would require a different pump, but with the 3-speed pumps on the market not costing much more than a single speed, I think I'd rather run a 3-speed pump on the secondary with a 3-stage t-stat, and no valve at all, than a single pump and 3-way valves. Remember, it's important that the system maximizes the delta-t to maximize the effectiveness of the buffer.
  • 10-06-2012, 11:30 PM
    xarralu
    I just PM'd you Dallas. Without being able to quickly draw it out, I would only use one pump. I would use a three way valve at the chiller and the storage tank and maintain CHW delta T across the FCU(s). Give me a few and I will whip up my drawing
  • 10-06-2012, 11:17 PM
    xarralu
    Quote Originally Posted by motoguy128 View Post
    The goal is more for zoning and comfort, not direct energy savings. .
    Correct, I was referencing the absorption chiller when I said that.

    Why are they noisy? The condenser shouldn't be any different from a residential condenser. .
    Not the machine that Dallas Duster posted the picture of! It would be too noisy for residential use.
  • 10-06-2012, 11:15 PM
    Dallas Duster
    Quote Originally Posted by xarralu View Post
    Exactly my point. You just basically said the same thing I did.
    But don't you add the need for an extra chilled water pump? I think the important thing to do is keep it simple and straight forward lets not try to over think this. How was your training class?
  • 10-06-2012, 11:07 PM
    xarralu
    Quote Originally Posted by CraziFuzzy View Post
    Actually, with a decoupling buffer tank, you don't have to have the temperature swings. The air handler can maintain a nice steady temperature control, and the chiller will cycle as needed to maintain the buffer's charge.
    Exactly my point. You just basically said the same thing I did.
  • 10-03-2012, 12:32 PM
    CraziFuzzy
    Quote Originally Posted by motoguy128 View Post
    So you put the storage on the return side. I'm used to primary/secondary system where the storage is the point where the 2 loops combine together. I figured in this case, the storage would be on the supply side and you'd store cold water. I do see how it's better to store return water and create a heat sink and have a wider temperature swing. The downside, is that the RWT would be lower on average at the chiller.

    If you have a zone system, you would end up with a primary/secondary set-up anyway, since you'd want to maintain water flow across the chiller, but wouldn't need as much flow to the zones.

    Using delta T is a good way to modulate or stage a chiller.
    No, I am talking about the storage being the decoulper between the primary and secondary, just as you describe. I'm just talking about using it as a stratified tank, using the stratification as the indicator of energy storage, and use THAT to stage the chiller.
    Example:
    Attachment 314291
  • 10-03-2012, 10:52 AM
    motoguy128
    So you put the storage on the return side. I'm used to primary/secondary system where the storage is the point where the 2 loops combine together. I figured in this case, the storage woudl be on the supply side and you'd store cold water. I do see how it's better to store return water and create a heat sink and have a wider temperature swing. The downside, is that the RWT would be lower on average at the chiller.

    If you have a zone system, you would end up with a primary/secondary set-up anyway, sicne you'd want ot maintain water flow across the chiller, but wouldn't need as much flow to the zones.

    Using delta T is a good way to modulate or stage a chiller.