Plant maintenance guy was probably in the main adding or changing a circuit and swapped phases to your unit? If scroll was only 3 phase in package unit, this could go unnoticed until cooling season. If you ask the guy he will likely do a Sgt Schultz on ya. (I know nothiiiiiing)
I had this to happen to Carrier RTU HP in 1998 when the power company changed out a transformer. The unit ran for several days in that condition and after corrected it is still in use today. Hope you have the same luck.
Originally Posted by commtech77 Sure they will. You didnt wire it in wrong and what Carrier doesnt know wont hurt them. Your customer comes first. First off, MFR's are strict on taking back compressors. Once they hook it up at the factory and test it and find nothing wrong, since he changed it before it failed, Carrier will foot him the bill for the new compressor.
Originally Posted by hands So was the blower also running backwards or was the compressor wired wrong from the factory? Blower was single phase running fine. I dont think comp was wired incorrectly. Unit never started up to check rotation.
Originally Posted by Dallas Duster You are probably right but how would they ever know? on some compressors you can tell by the paper the label is made of. When it gets too hot the label turns brown. I know that is true on some Lennox units. When they see that it can void the warranty. Went out to pm location that was installed in the winter and 6 of 13 units were running backwards. after cooling off all worked fine but as somone said time will tell. Also on a Lennox the variable speed drive for the blower will self correct for wrong phase. This will cause trouble for the lazy tech who checks proper phase by blower rotation and does not check the compressors.
if the balancer gets in there first he will reverse the disconnect for the supply fan to do his air balancing and walk away.if the paint isn't melted off the top of the hi side your good.had Trane-command air ceiling units and the balancer did his trick to balence and blew out the scroll compressor terminals on 10 out of 15 units...
Originally Posted by markettech They run 3 phase blower motors? Most of the 3 phase gas pack RTU's I've seen, have single phase blowers.....but I don't get a steady diet of 'em either. Most 3 PH RTU's I've seen have 3 PH blower motors. They may only use a two pole contactor, but they run a wire to the motor that is hot all the time. I'm not saying that your unit has a 3 PH blower, but you may want to check it if you're not sure.
Something to consider- If you have a unit that has 3 phase compressors and blower motor, they should both be phased properly from the factory (A-B-C). That doesn't mean they can't be wired wrong in the field, but if one is running backwards, they both should be. (though "should" doesn't mean "always is the case") Maybe when they started it up it in the field it was too cold to start up cooling, and the compressor was phased wrong at the factory-maybe they meant to do a cooling startup when conditions were better, and would certainly have caught it then. If the compressor is 3 phase and the blower is single, it's still possible that the compressor was started up and running in the right rotation at one point, but if someone changed the contactor and accidentally crossed up the wiring, that would reverse rotation also. Not to mention: there could have been a phase reversal at the pole, coming into the building (though that would affect all 3 phase motors from that feed), the panel could have been changed, and that breaker had wiring crossed. All I'm really getting at is just because we run into equipment running backwards, doesn't mean it was always running backwards...things happen. Sometimes equipment gets started up correctly, and outside forces change things. And....sometimes folks just hit the go button, hope for the best, and head for the bar.
Something to consider-
Originally Posted by commtech77 Sure they will. You didnt wire it in wrong and what Carrier doesnt know wont hurt them. Your customer comes first. Don't get me wrong...I agree with you 100%. I would take care of the customer anyway I could and definitely do what I can. This thread also reminds me...on new Carriers....make sure and look at the voltage ratings on the blower motor. Already seen it a couple times where they put a 208 volt motor in a 460 volt unit. The motor doesn't usually last long lol.
Originally Posted by pvc1984 I agree too it's probably fine. But I really doubt carrier is gonna warranty a compressor that was wired improperly to begin with. Sure they will. You didnt wire it in wrong and what Carrier doesnt know wont hurt them. Your customer comes first.
Originally Posted by hands So was the blower also running backwards or was the compressor wired wrong from the factory? They run 3 phase blower motors? Most of the 3 phase gas pack RTU's I've seen, have single phase blowers.....but I don't get a steady diet of 'em either.
So was the blower also running backwards or was the compressor wired wrong from the factory?
Good advice document your work so it does not come back to bite you later. that has saved me on several occasions.They cannot say you were at fault that way and believe me they will.
Originally Posted by pvc1984 I agree too it's probably fine. But I really doubt carrier is gonna warranty a compressor that was wired improperly to begin with. You are probably right but how would they ever know?
Originally Posted by commtech77 Usually they heat up and trip the internal overload , reset and the do it all over again. Im guessing this thing is under warranty ? Ask the customer if they want to swap out the comp. If they will pay labor that is. Reaaly I thinks its probably fine. I had a data aire that ran backwards for two days. That was 3 years ago. and its still running. I agree too it's probably fine. But I really doubt carrier is gonna warranty a compressor that was wired improperly to begin with.
I would've checked pressures, temperatures, ohmed out the compressor, and recorded amp draws on my paperwork. Record everything to CYA!! If all that checked out and the compressor sounded okay, just hope for the best....that's all you can do really.
Usually they heat up and trip the internal overload , reset and the do it all over again. Im guessing this thing is under warranty ? Ask the customer if they want to swap out the comp. If they will pay labor that is. Reaaly I thinks its probably fine. I had a data aire that ran backwards for two days. That was 3 years ago. and its still running.
Originally Posted by kamikaze126 No cooling call. A new 3 phase Carier Rtu that was installed in winter. 4 ton scroll. Installing contractor MIA. It Never ran in cooling until today. It ran backwards for about 6 hours im guessing. Comp was off on IO I let it cool, reversed leads and everything was normal. What can be expected for the future of this unit? Only time will tell!
Scroll running backward No cooling call. A new 3 phase Carier Rtu that was installed in winter. 4 ton scroll. Installing contractor MIA. It Never ran in cooling until today. It ran backwards for about 6 hours im guessing. Comp was off on IO I let it cool, reversed leads and everything was normal. What can be expected for the future of this unit?
Scroll running backward