  • 03-20-2014, 08:50 PM
    Jangles
    Time clock? If there isn't one, put one in. If the box is relying on off time from the stat then you can also get ice buildup over time due to inadequate defrost. Start with that first before as well as ensuring a full charge and the fact that the system does cycle off.
  • 03-20-2014, 07:54 PM
    smeq
    A coil that is filled with that greasy lint has decreased airflow, and the defrost doesn't complete itself. After the ice is gone, I usually find a layer of crud.
  • 03-20-2014, 07:42 PM
    Bobbycold
    Quote Originally Posted by HVAC LLC View Post
    What are some causes for a partially frozen evaporator (besides low charge) on a walk-in evap, 3 fan Larkin food cooler, full charge 404, was running fine, thermostat set on 38, 5 degree differential.
    Got a call on this, haven't been there yet. Customer defrosted, but may call me back.
    I know that's not much information, but it's pretty much all I have.
    I have done all commercial HVAC, not allot of refrigeration, maybe 20%.
    Thanks.
    Does the Larkin walk in have a Beacon (1) electronic controller?
  • 03-18-2014, 11:49 AM
    captaincompressor
    Maybe a starved evaporator.
  • 03-18-2014, 06:14 AM
    flangehead
    Quote Originally Posted by icemeister View Post
    Uneven icing of the evaporator coil like that can be due to an improper distributor nozzle. An oversized nozzle can lead to uneven distribution...essentially overfeed some circuits and underfeeding others.

    More than likely though, your ice buildup is a result of incomplete defrosting.

    I'm assuming this sytem has no defrost timeclock and relies strictly on the off-cycle time to clear away frost buildup. If ALL of the frost is not cleared off, it will re-freeze and become hard ice.

    Add a defrost timeclock and set it up for three 30-40 minute defrosts per day.
    30, 40 min defrosts per day, now that's funny!


    Sent from my iPhone using Tapatalk
  • 03-17-2014, 11:24 PM
    tope
    Quote Originally Posted by HVAC LLC View Post
    What are some causes for a partially frozen evaporator (besides low charge) on a walk-in evap, 3 fan Larkin food cooler, full charge 404, was running fine, thermostat set on 38, 5 degree differential.
    Got a call on this, haven't been there yet. Customer defrosted, but may call me back.
    I know that's not much information, but it's pretty much all I have.
    I have done all commercial HVAC, not allot of refrigeration, maybe 20%.
    Thanks.
    deffective txv
  • 03-13-2014, 09:49 AM
    Todd Whaley
    I do residential, so I was just at a gas station I frequent. He asked me to look at his cooler. Complaint was freezing evap. He turned off the unit the night prior. Pan full of water, so I vacuumed out. Coil was icing up immediately. WR defrost with sencing bulb set at +30 whatever that means. Drain mustbe stopped up, but I suspect the defrost Iis not Iinitiating or not running long enough. But what do I know. R-502 frezone. I passed it to a buddy that can do low and med refrigeration. Know when to say nope.
  • 09-25-2012, 06:31 PM
    coolerik
    Quote Originally Posted by crackertech View Post
    Humm.....................I just don't know were to start with this one.
    Things just went sidewayz
  • 09-25-2012, 03:15 PM
    crackertech
    Quote Originally Posted by MPHPS View Post
    I started working at a restaurant performing services and the owner asked me to look at their Larkin walk in cooler that was only at 50 degrees. Found large section of inside and outside of coils in walk in frozen up, removed all ice, rooftop unit very low on freon, recharged got temp down to 38 degrees, 3 days later all still ok and coils still clear, 1 week later top section inside and outside frozen up, charge ok but temp down to 50 degrees, is this not defrosting and where could I locate the defroster I cannot find it anywhere. Model # is 2 blade low profile


    Humm.....................I just don't know were to start with this one.
  • 09-24-2012, 09:50 PM
    MPHPS

    Larkin Walk in cooler freezing up top section only

    I started working at a restaurant performing services and the owner asked me to look at their Larkin walk in cooler that was only at 50 degrees. Found large section of inside and outside of coils in walk in frozen up, removed all ice, rooftop unit very low on freon, recharged got temp down to 38 degrees, 3 days later all still ok and coils still clear, 1 week later top section inside and outside frozen up, charge ok but temp down to 50 degrees, is this not defrosting and where could I locate the defroster I cannot find it anywhere. Model # is 2 blade low profile
  • 09-02-2009, 10:36 PM
    itsamine
    Quote Originally Posted by 270wsm View Post
    Since this is on the same subject, i have a similar question. What causes the Txv and distributer tubes to freeze to a ball of ice without the coil freezing up? I run into this alot on walk-in freezers.
    Moisture in the system.
  • 09-02-2009, 09:45 PM
    sarpanch2001
    Quote Originally Posted by jtrefrig View Post
    if its ice not frost make sure your drain is clear. jbb
    jtt x2
  • 09-02-2009, 09:37 PM
    Phase Loss
    Quote Originally Posted by 270wsm View Post
    Since this is on the same subject, i have a similar question. What causes the Txv and distributer tubes to freeze to a ball of ice without the coil freezing up? I run into this alot on walk-in freezers.
    This could happen with a starved TEV. the Liquid is literally flashing to a vapor inside of the TEV.

    Or it could be normal and the frost/ice dose not melt in defrost because usually the TEV/distributer tubes are in an enclosed section of the evaporator coil that dose not have heating elements. where as the actual evaporator is in direct contact with the heating elements.
  • 09-02-2009, 09:19 PM
    warm beer
    You're really going to need to know the pressures.High pressure the condenser is dirty or the TXV strainer is dirty,Or you're probably low on refrigerant,Or a evap fan is not working,and of course they might of left the door open all weekend or bad seals.......
  • 09-02-2009, 09:08 PM
    270wsm
    Since this is on the same subject, i have a similar question. What causes the Txv and distributer tubes to freeze to a ball of ice without the coil freezing up? I run into this alot on walk-in freezers.
  • 09-02-2009, 08:30 PM
    crackertech
    X2 check the defrost and the drain line first.
  • 09-02-2009, 06:54 PM
    jtrefrig
    if its ice not frost make sure your drain is clear. jbb
  • 09-02-2009, 01:23 PM
    icemeister
    Uneven icing of the evaporator coil like that can be due to an improper distributor nozzle. An oversized nozzle can lead to uneven distribution...essentially overfeed some circuits and underfeeding others.

    More than likely though, your ice buildup is a result of incomplete defrosting.

    I'm assuming this sytem has no defrost timeclock and relies strictly on the off-cycle time to clear away frost buildup. If ALL of the frost is not cleared off, it will re-freeze and become hard ice.

    Add a defrost timeclock and set it up for three 30-40 minute defrosts per day.
  • 09-02-2009, 10:47 AM
    HVAC LLC
    Probably not so much fun, but thanks for responding.
    I will drop by the store and check on it.
  • 09-02-2009, 09:42 AM
    mikep
    TXV probably needs to be adjusted, but if you have never done comm refrig you are in for a fun day of tweeking.