  • 11-05-2012, 09:41 AM
    KB Cool
    Quote Originally Posted by Dallas Duster View Post
    You do what ever you want to it It's the customers machine and he can pay you to make any modifications to it that he wants. For all I care you can put a TXV on it and go with it.
    Yeah, it'll be a good learning experience!!!
  • 11-05-2012, 05:52 AM
    ckartson
    Carrene #2 you made the most sense. I figured a plugged drier but couldn't figure high pressure trips. I also assumed a pressure switch not a DDC controller. I am not familiar with the equpment being described. Was this an actual pressure switch shutting the comp down or a program in the controller? What brand?
  • 11-05-2012, 12:28 AM
    Dallas Duster
    You do what ever you want to it It's the customers machine and he can pay you to make any modifications to it that he wants. For all I care you can put a TXV on it and go with it.


    Quote Originally Posted by KB Cool View Post
    Ok i'll keep that in mine if i have to go back!! I figured i couldn't go wrong by following the manual's charging instructions!
  • 11-05-2012, 12:11 AM
    KB Cool
    Ok i'll keep that in mine if i have to go back!! I figured i couldn't go wrong by following the manual's charging instructions!
  • 11-04-2012, 10:36 PM
    rscamaro
    Quote Originally Posted by KB Cool View Post
    Come on! Who's to say my thermocoupler aint off by 2 degrees!!!
    With the microchannel coils I pretty much always go to the low side, and I don't think 15-17 degrees SC is correct for the microchannel unit, I may be wrong but I don't think so. Sounds right for the standard copper/aluminum coils though.

    If you haven't seen just what the MC coils look like, you really need to take a look. What you have is pretty much a 1"x 1/8" flat piece of aluminum with say 10 to 15 capillary tubes running the length of the aluminum bar. They don't hold very much refrigerant in them. It is very easy to trip the HP switch with even a slight overcharge.

    ...Ron
  • 11-04-2012, 08:29 PM
    KB Cool
    Quote Originally Posted by Carrene #2 View Post
    Damn, I swore to myself that I was done with this.
    I'm weak.

    Do the words "critical charge" ring a bell?

    Best of Luck :

    Dick
    Come on! Who's to say my thermocoupler aint off by 2 degrees!!!
  • 11-04-2012, 07:57 PM
    Carrene #2
    Quote Originally Posted by KB Cool View Post
    Why? IOM says 15°-17°. I figured 1 degree over aint gonna matter.
    Damn, I swore to myself that I was done with this.
    I'm weak.

    Do the words "critical charge" ring a bell?

    Best of Luck :

    Dick
  • 11-04-2012, 08:38 AM
    AiResearch
    The digital scroll is actually a cool
    device. It allows a greater range of capacity control than traditional unloaders on a recip.

    It is designed to load / unload frequently to deliver a specific output. 40% load time = 40% capacity. Better load matching.

    Most units are sized for peak load and run there a small percentage of time. So you have an oversized 10 ton scroll cycling on and off. Over and over. Hard on the compressor for sure. This compressor can stay running and stay healthy.

    Oil management with these is a whole different topic.
  • 11-04-2012, 01:13 AM
    KB Cool
    Quote Originally Posted by rscamaro View Post
    Too much subcooling for a 410a unit with microchannel coils.

    ...Ron
    Why? IOM says 15°-17°. I figured 1 degree over aint gonna matter.
  • 11-04-2012, 12:27 AM
    supertek65
    Sometimes EEV controls condenser fans.

    This could do it.
  • 11-04-2012, 12:06 AM
    rscamaro
    Quote Originally Posted by KB Cool View Post
    Yeah i blocked off the condensor to 120° CST and gave it 18° SC.
    Too much subcooling for a 410a unit with microchannel coils.

    ...Ron
  • 11-01-2012, 09:03 PM
    KB Cool
    Quote Originally Posted by Dallas Duster View Post
    I guess the boss wins over common sense what is there a whopping 9 pounds or refrigerant in that machine.
    8.6 lbs. There's about eleven in it now!!!!
  • 11-01-2012, 08:28 PM
    Dallas Duster
    I guess the boss wins over common sense what is there a whopping 9 pounds or refrigerant in that machine.

    Quote Originally Posted by KB Cool View Post
    I know i didn't want to add the dryer. Would have been much easier just to go back in w/ the 165s. But, my Boss talked the owner into doing the replacable core as thier maintenace men will be able to replace it on the fly as needed!!!
  • 11-01-2012, 06:22 PM
    KB Cool
    Quote Originally Posted by Carrene #2 View Post
    Thanks, but no thanks.
    What a D!ck!!!




    Nah, he aint a bad guy afterall!! Thanks for the 33% tip Carrene. Well definetly look into it if this compressor decides to lock up!!!
  • 11-01-2012, 06:13 PM
    KB Cool
    Quote Originally Posted by Dallas Duster View Post
    He might be ok charging it up now since he added a small receiver to the system.
    I know i didn't want to add the dryer. Would have been much easier just to go back in w/ the 165s. But, my Boss talked the owner into doing the replacable core as thier maintenace men will be able to replace it on the fly as needed!!!
  • 11-01-2012, 06:06 PM
    KB Cool
    Quote Originally Posted by chilbrig View Post
    With the Micro coils the head will spike at startup then come back down to normal operating conditions. On a hot day it should not spike much over five hundred psig. If you must weigh in the charge subtact about five percent of what it says on the tag. If you overcharge just a little, it will trip. There should be a charging procedure in the OM book, that is the best way to charge it up. Again, if you have any restriction in the drier you will have problems.

    Yeah i blocked off the condensor to 120° CST and gave it 18° SC.
  • 11-01-2012, 06:06 PM
    Dallas Duster
    He might be ok charging it up now since he added a small receiver to the system.


    Quote Originally Posted by chilbrig View Post
    With the Micro coils the head will spike at startup then come back down to normal operating conditions. On a hot day it should not spike much over five hundred psig. If you must weigh in the charge subtact about five percent of what it says on the tag. If you overcharge just a little, it will trip. There should be a charging procedure in the OM book, that is the best way to charge it up. Again, if you have any restriction in the drier you will have problems.
  • 11-01-2012, 05:57 PM
    chilbrig
    With the Micro coils the head will spike at startup then come back down to normal operating conditions. On a hot day it should not spike much over five hundred psig. If you must weigh in the charge subtact about five percent of what it says on the tag. If you overcharge just a little, it will trip. There should be a charging procedure in the OM book, that is the best way to charge it up. Again, if you have any restriction in the drier you will have problems.
  • 11-01-2012, 05:53 PM
    Carrene #2
    Quote Originally Posted by KB Cool View Post
    Well, the customer knew they could not possibly run a 10 ten system on 1" pipe. But, they did think the unit was a true varible speed "digital" scroll and it would be ok ! Serious!!!

    P.S. I just saw your edit a little bit ago!! I'll tell them to call you next time!!
    Thanks, but no thanks.
  • 11-01-2012, 01:51 AM
    KB Cool
    Quote Originally Posted by Carrene #2 View Post
    Just got one like that! Misapplied!
    Well, the customer knew they could not possibly run a 10 ten system on 1" pipe. But, they did think the unit was a true varible speed "digital" scroll and it would be ok ! Serious!!!