  • 07-14-2014, 05:04 PM
    Tbone39
    Quote Originally Posted by rayr View Post
    X2
    You can’t... My thermocouple was not attached correctly.
  • 07-14-2014, 03:50 PM
    rayr
    Quote Originally Posted by Capz View Post
    How can you possibly have 90F superheat? On a working freezer?
    X2
  • 07-14-2014, 12:45 PM
    Tbone39
    Quote Originally Posted by Snapperhead View Post
    im curious about the outcome ....
    I know this is an old thread, but I wanted to put this to bed...
    Thermocouple was not making a good contact…I also recalibrate all my tools...
    I replaced the compressor. Unit has been running without any problems since then.

    Thank your feedback.
  • 08-08-2013, 08:20 AM
    Snapperhead
    im curious about the outcome ....
  • 08-06-2013, 01:59 PM
    Tbone39
    Quote Originally Posted by eddiegoodfellar View Post
    where did u check the superheat?
    About 10 inches from compressor suction line.
  • 08-06-2013, 01:01 PM
    eddiegoodfellar
    where did u check the superheat?
  • 08-06-2013, 07:56 AM
    Tbone39
    Quote Originally Posted by Phase Loss View Post
    Did you put your clamp on the pipe?

    or on the insulation?

    I'm not that bad. ... pipe. I'm going to recheck calibration later today.
  • 08-06-2013, 01:50 AM
    Phase Loss
    Did you put your clamp on the pipe?

    or on the insulation?

  • 08-05-2013, 11:50 PM
    Tbone39
    I was using a calibrated SMAN3. The Clamp may have been loose .
  • 08-05-2013, 07:15 PM
    2sac
    Quote Originally Posted by Tbone39 View Post
    Since the unit is working now, do I go back, recover, pressure test, evacuate, and weigh in charge. Or should I just leave it since it is operating properly (for now). I am trying to be proactive.
    If your customer wants to pay for it, go right ahead. Otherwise hope for the best. As far as the SH, first I'd calibrate your thermometer and gauges because somethings not right. You're telling us you essentially have a 70degree suction line at the pump? That pump won't last long and I'm surprised the unit is cooling like you say it is.
  • 08-05-2013, 06:32 PM
    Capz
    How can you possibly have 90F superheat? On a working freezer?
  • 08-05-2013, 02:50 PM
    Tbone39
    And of course a 90*f Super Heat is bad... Could contaminates cause a high super heat?
  • 08-05-2013, 02:37 PM
    pecmsg
    Compressor manufactures call for 20 – 40*f SH at the compressor to prevent damage.
  • 08-05-2013, 02:24 PM
    Tbone39
    Since the unit is working now, do I go back, recover, pressure test, evacuate, and weigh in charge. Or should I just leave it since it is operating properly (for now). I am trying to be proactive.
  • 08-05-2013, 01:54 PM
    Tommy knocker
    Self contained RI freezer. All the time u took to fiddle and think about it you could have pulled charge evacuated and weighed the exact proper charge in. Not picking but I never guess on charge on RIs when the charge weight is on the data plate. Just saying
  • 08-05-2013, 12:17 PM
    Tbone39
    I am not sure if I was clear or not… but the unit is operating normal since I have serviced it (About 4 days ago).
  • 08-05-2013, 12:14 PM
    Tbone39
    Yes to the CPR Valve - 10PSIG
    Not sure what #'s are for the TXV.
  • 08-05-2013, 11:45 AM
    heresjohnnyb
    is there a cpr valve on it. whats the actual #'s on the txv valve itself.Just want to see what kind of valve you got.
  • 08-05-2013, 11:25 AM
    pecmsg
    Quote Originally Posted by Tbone39 View Post
    TXV

    It is a Carrier ULG80BC-5, Three Door Glass Freezer (Bottom Mounted Compressor).
    Forget SC with a receiver.
    Clear the SG and adjust the SH
  • 08-05-2013, 10:35 AM
    Tbone39
    TXV

    It is a Carrier ULG80BC-5, Three Door Glass Freezer (Bottom Mounted Compressor).