  • 02-01-2010, 02:47 PM
    shylock
    Quote Originally Posted by eyeLON View Post
    It's better to use a separate transformer.
    Why?
  • 02-01-2010, 08:48 AM
    Praetorian
    Duh ... yea. Note to self: Remember to check to see if the outputs are triac outputs or universal outputs. Thanks guys.
  • 01-14-2010, 06:58 PM
    eyeLON
    The Distech triacs are rated for 1A only. Typical you should only drive a 24VAC relay only. Don't be tempted to use the same 24V that powers the node. It's better to use a separate transformer. Also note that you need a load (relay) attached to a triac in order to read voltage. You won't read anything without some kind of load.
  • 01-14-2010, 06:26 PM
    Ducthman
    Quote Originally Posted by Praetorian View Post
    I am having trouble getting a Distech ECP-203 GFX controller online. This is the first Distech programmable controller I have installed so I am not sure if I am doing something wrong. I have written a simple program to control a baseboard heater based on room temp. The program debugs perfectly and when calling for heat illuminates the output status LED on the controller itself. However, I am not getting any voltage from these outputs to close the relay. I checked the configuration of the hardware output, and the output is configured as "digital". I have used Circon, Echelon, and Viconics products before and never had an issue. What am I doing wrong here? Any ideas?
    Put 24VAC on C1 and connect a wire from DO1 to the coil of your relay if you use output 6 to 8 you must use a 12VDC relay
  • 01-14-2010, 04:57 PM
    ctrlguy
    The triacs are not internally powered. You need to jump the 24VAC supply to the common of the output (or use a different 24V source). It allows you to use multiple transformers without dealing with isolation relays.
  • 01-14-2010, 04:55 PM
    NINAX
    Quote Originally Posted by Praetorian View Post
    I am having trouble getting a Distech ECP-203 GFX controller online. This is the first Distech programmable controller I have installed so I am not sure if I am doing something wrong. I have written a simple program to control a baseboard heater based on room temp. The program debugs perfectly and when calling for heat illuminates the output status LED on the controller itself. However, I am not getting any voltage from these outputs to close the relay. I checked the configuration of the hardware output, and the output is configured as "digital". I have used Circon, Echelon, and Viconics products before and never had an issue. What am I doing wrong here? Any ideas?
    Which output are you using?
  • 01-14-2010, 04:49 PM
    kontrolphreak
    I have not personally used the controller you mentioned, but the first thing I would check is if the output is a "dry" contact, if so you will have to wire control voltage through the output.

    kontrol out

    For post 308 I give you:

    http://www.gaprecision.net/

    kontrol out again
  • 01-14-2010, 04:06 PM
    Praetorian

    Distech ECP-203 Output Question

    I am having trouble getting a Distech ECP-203 GFX controller online. This is the first Distech programmable controller I have installed so I am not sure if I am doing something wrong. I have written a simple program to control a baseboard heater based on room temp. The program debugs perfectly and when calling for heat illuminates the output status LED on the controller itself. However, I am not getting any voltage from these outputs to close the relay. I checked the configuration of the hardware output, and the output is configured as "digital". I have used Circon, Echelon, and Viconics products before and never had an issue. What am I doing wrong here? Any ideas?