  • 08-04-2013, 08:43 AM
    demidos89
    As far as the vsd on the cw pumps, that seems to be an unnecessary method of controlling cw temp. if you have a 3 way bypass valve and vsd on the fan motors that should allow for max efficiency both electrically and on the refrigeration side. Most everything I have read and worked on seems to call for consistent flow through the condenser. As knewyork posted the york chilers with vsd will provide your biggest cost savings by lowering the heat output to the condenser on the chiller when possible. also centrifugal compressors with the prv's help cost savings too.
  • 06-11-2013, 11:44 PM
    spinning wheel
    It is amazing how we made it this far. Must have been dumb luck.
  • 06-11-2013, 10:03 PM
    klove
    I must have slept thru the part of Water Flow & Heat Transfer 101 that talked about enhanced tubes not creating turbulence in the internal flow pattern of a tube. Anyone care to bring me up to speed, 'cause I just read the last two pages of this thread and realized how ignorant I must be about this subject. Reckon I need to go get my chemical engineering degree.....
  • 06-11-2013, 02:58 PM
    DANI25486
    That means we answer all his questions
  • 06-11-2013, 01:25 AM
    KnewYork
    The guy who asked the question hasn't been back since a day after he asked the question over a year ago.
  • 06-10-2013, 04:34 PM
    JMunoz
    I realize this thread is old, but I would like to correct some of the misinformation you have received. Most centrifugal chillers have no issue with variable condenser water flow. I recommend that you contact your chiller sales engineer about your chiller's specific requirements. The chiller O&M manual or design manual usually provides the minimum or maximum allowable flows. These limits are based on tube velocity.

    The sequence of operation for the condenser water pump VFD can be designed to maintain the chiller's design condenser water temperature range or it can be designed to maintain a specific refrigerant head. The sequence needs to include the minimum and maximum chiller flow limits as required by the manufacturer.

    To determine the savings associated with lower condenser water flow, I recommend you calculate the energy consumed by the pump, chiller and cooling tower under different conditions (temperature and flow). The most efficient operation will be the one with the lowest combined energy of all three components. Systems that have relatively long distance between the chiller and the cooling tower or systems with more than two chillers will benefit the most from the use of variable condenser water flow.

    Regarding cooling tower temperature control, the best sequence again should consider the energy consumed by the pump, cooling tower and chiller combined. Setting the temperature at a constant 80 deg F is the least efficient method. Setting the fan speed to achieve the lowest allowable temperature is better, but not the best. The best method is to reset the condenser water supply setpoint based on the wet bulb temperature (WBT) plus the approach temp. The approach temp will vary with the WBT and load, so there should be a reset schedule for the approach. For example, the approach may be 6 deg F when the WBT is 78 deg F and the load is 100%, but it could be 10 deg F when the WBT is 60°F at 100% load.

    Hope this helps.
  • 05-15-2012, 10:30 AM
    JRINJAX
    There seem to be a lot of generalizations being proposed here. All systems have common tenants of operation, but like some have pointed out, every system has differences in the equipment used and the way it is installed. Enough straight pipe before a condenser or an evap to generate concentric flow changes a host of other variables that improves performance. Poor design/installation is often masked by increasing flows/HP needed.

    The high MHZ choppers in the newer drives can produce a "designer waveform" in response to the "stored software profile" of the motor that was produced when "auto tune" was run.

    JMO.....
  • 05-14-2012, 07:51 PM
    flange
    waterworld, who sees no value in vfd's on a condenser pump.
  • 05-14-2012, 07:34 PM
    KnewYork
    Quote Originally Posted by flange
    so please, explain why setting a pump speed to to exact frequency required for a given flow is less efficient than setting it at 60htz and then choking back flow with a balancing valve?
    I'm not sure to whom this question is directed, but I am in your camp with a VSD on a pump set to the correct frequency to maintain a desired flow. Many people don't understand the savings of a VSD is a cube function. A 100 HP motor running at 30 Hz is equivalently 12.5 HP, run at 45 Hz and the equivalent is 42 HP. There are many advantages to eliminating the triple duty valve and controlling flow with a VSD controlled pump.
  • 05-14-2012, 07:28 PM
    flange
    soft start is great, as it reduces inrush, and helps to prolong the life of components. the real benefit is that a properly selected pump/vfd combo will see greater hydrauic efficiency at lower speeds in many instances, thereby reducing actual horsepower used dramatically depending upon nameplate horsepower. the larger the motor, the greater the savings. this is true, in general, down to about fifty percent of design flow.
  • 05-14-2012, 06:46 PM
    Six
    The soft start option a VFD gives you compared to across the line is the only advantage I can think of on a system that uses constant flow.
  • 05-14-2012, 05:22 PM
    flange
    so please, explain why setting a pump speed to to exact frequency required for a given flow is less efficient than setting it at 60htz and then choking back flow with a balancing valve? I am trained t o think the opposite is more correct. hell, make me a beliver, and it will save me tens of thousands on my next design build project by eliminating vfd's and control wiring.
  • 05-13-2012, 10:30 PM
    jayguy
    Quote Originally Posted by waterworld View Post
    No disrespect to any of you at all... but I really don't like shots being taken at my 'schooling'....
    i did not mean any disrespect to your schooling.


    Quote Originally Posted by waterworld View Post
    ....jayguy: Turbulent flow is the most efficient form of heat transfer. That's not debatable. Look it up or read the documents I attached. I didn't write them. Laminar flow relies completely on thermal conductance to transfer heat while turbulent is well mixed and distributes the collected heat within the stream.
    i completely agree with you here. i did not disagree with you on the turbulent flow being the most efficient form of heat transfer...it IS the most efficient...plain and simple. my argument was with your statement of: 'you MUST have turbulent flow in order to have efficient heat transfer'. while this may generally be true, it isn't always NECESSARY (or possible, like low load situations) to have efficient heat transfer.

    i think that water flow and its associated uses is a ridiculously simple concept and it is not that difficult to understand...to engineer is different...but to understand and use (already engineered products) seems quite simple to me.
  • 05-13-2012, 08:23 PM
    waterworld
    Quote Originally Posted by flange View Post
    using a vfd on a condenser pump typically eliminates the triple duty valve( pressure drop) and allows use of only a check valve. Setting a pump to run a sixty hertz, then neutering it back with a triple duty is less effiicent than running the vfd at the correct frequency to maintain proper flow. its a fact that has somehow missed your schooling. Its why every utility and their mom here is giving rebates for them.

    As far as variable flow through a condenser, thats a whole other discussion, but lets say for example, you have three 150 ton compressors, and one is running. why is it imperative to run full desgin flow through there? you arent gaining anything. your head will only get to a certain point, as determined by desing approach, cleanliness, and water temps. its not like it will drop off lower if you run three times the water flow through the condenser.
    No disrespect to any of you at all... but I really don't like shots being taken at my 'schooling'. I didn't bring that up until Knew York called me a Know it All. Anyhow, you don't have to believe me; it doesn't change my life one bit. Facts are facts and you can choose to believe them or not. I didn't make this stuff up; it is standard heat exchange physics.

    And why does it matter if only one compressor is running? Because even though only 1/3 of the load is being utilized your condenser remains the same size at all times. In theory, if you could restrict the size of the condenser tubes to correlate with the lower flow rates then fine... but you can't. Once you vary the flow rate low enough you drop to laminar and you inhibit heat transfer. Heat transfer is not linear, you may vary the flow by 40% or whatever but that doesn't equal a 40% less efficient heat transfer. It likely equals a 70 to 80% less efficient heat transfer. And pressures are not 'missing from my schooling'. The more turbulent the flow the greater the pressure drop through the exchanger or condenser. The more laminar the less the pressure drop... and yes the more the pressure drop the more the pumping power required. But what do you think the electricity cost is when you have a fouled condenser?

    Read this document titled The Fundamentals of Heat Exchangers and argue with that. Again, I didn't make this up and I'm not devising this as I write. You can choose what facts to believe all you want.

    And, I don't care what they give rebates for. It just show the lack of understanding that the municipalities have for HVAC systems. Not only that, but this discussion has been limited to flow through a condenser and hasn't included flow through the tower. Tower's require a minimum flow in order to reject the appropriate amount of heat as well. Often those minimum's are ignored when a VFD is utilized.

    Don't let the facts get in the way of the truth.

    jayguy: Turbulent flow is the most efficient form of heat transfer. That's not debatable. Look it up or read the documents I attached. I didn't write them. Laminar flow relies completely on thermal conductance to transfer heat while turbulent is well mixed and distributes the collected heat within the stream.
  • 05-13-2012, 07:55 PM
    flange
    using a vfd on a condenser pump typically eliminates the triple duty valve( pressure drop) and allows use of only a check valve. Setting a pump to run a sixty hertz, then neutering it back with a triple duty is less effiicent than running the vfd at the correct frequency to maintain proper flow. its a fact that has somehow missed your schooling. Its why every utility and their mom here is giving rebates for them.

    As far as variable flow through a condenser, thats a whole other discussion, but lets say for example, you have three 150 ton compressors, and one is running. why is it imperative to run full desgin flow through there? you arent gaining anything. your head will only get to a certain point, as determined by desing approach, cleanliness, and water temps. its not like it will drop off lower if you run three times the water flow through the condenser.
  • 05-12-2012, 03:59 PM
    jayguy
    Quote Originally Posted by waterworld View Post
    ...You can't escape physics my friend. It's heat transfer 101, you MUST have turbulent flow in order to have efficient heat transfer...
    you don't have to have turbulent flow to have efficient heat transfer...efficiency is a matter of in's and out's. i will agree that higher water flows generally gain you more efficient heat transfer on the water side, however, at what cost? more pump electricity? maybe, maybe not...it depends on the EXACT situation and we just don't know enough about THIS OP's situation to make a well informed thought. there may be times (lower loads) that 'high efficiency' heat transfer is not necessary. we also can not control the refrigerant flow rate on the refrigerant side of the tube...as the chiller unloads and slows down the refrigerant flow rate, there is going to be less heat transfer on that side of the tube as well...if the heat doesn't get into the copper of the copper tube, then the water can not remove it no matter how perfect the water flow rate is.


    Quote Originally Posted by waterworld View Post
    ...A centrifugal chiller must have 3 gpm per max design ton in the condenser. If you have less, by even 20%, no matter what your load is, then you will create laminar flow.....
    please be careful in stating generalized terms such as this. i have a chiller whos design evaporator is 566 gpm. subtracting 20% gives me a flow rate of 453 gpm...the minimum allowable gpm is 173. 453 is >250% better than the allowable low end...i would not think that i would have laminar flow if the flow dropped to 453 gpm...more laminar than 566? sure, but at what point do you cut things off? it depends on the design. lets keep the generalizations to the politicians.


    Quote Originally Posted by waterworld View Post
    ...if it were water it would 'rifle' and resistance from the 'rifling' would create friction.....
    water in a non-rifled tube creates friction too.


    since it seems that you have quite a bit of education and experience AND that you are going to be an engineer of some kind, please make sure that EVERY job has at least 10 pipe diameters of straight pipe before entering the chiller bundle...if you do, you will be one of the only ones that will do that and for that i thank you.
  • 05-12-2012, 02:41 PM
    waterworld
    Quote Originally Posted by KnewYork View Post
    Another know-it-all. Use an analogy that supports my argument. The rifling inside a barrel puts a "spin" on the projectile, which is exactly what a rifled or an enhanced tube does to the fluid inside of it. Without rifling inside a rifle barrel the projectile would not spin just like laminar flow, no? Internally enhanced tubes create two benefits...enhanced heat transfer and the opposite of laminar flow. Call it what you will...turbulence, non-laminar...whatever. HRS heat transfer has a good video on YouTube if you care to watch it.
    Wow... that's not really fair. I have a Master's in Chemistry and I am preparing to take my exam for my P.E. in chemical engineering and I have been in the water treatment industry for many years. I think that gives me some standing to give an opinion even if it does not agree with yours. Furthermore your video is an illusion. It shows a corrugated tube diverting air bubbles. There is no flow of water, only air bubbles. What you aren't understanding is that if it were water it would 'rifle' and resistance from the 'rifling' would create friction and therefore would tend to create a laminar condition, not turbulent.

    And the spin you mention, laminar flow is where the center of the stream is traveling faster than the outside of the stream. Exactly what happens when the flow if water is spinning in an enhanced tube. The outside of the stream is being slowed down by the resistance created at the grooves and forced to spin while the center of the flow remains uninhibited by resistance and flows freely at a faster level. The heat transfer is inhibited by the thermal conductivity created by the resistance at the spirals. Heat transfer 101. My analogy has nothing to do with yours. The rifling of a gun stabilized the trajectory by centering the gravity of the bullet down the center of the rifle.... like LAMINAR FLOW.

    Don't like what I have to say? Read this document by about 6 chemical and mechanical engineers stating that enhanced tubes do not induce turbulent flow but tend to create friction and laminar flow and inhibit heat transfer. Maybe they are know-it-all's as well...
  • 05-12-2012, 02:09 PM
    KnewYork
    Quote Originally Posted by waterworld
    The only thing you are right about is that the 3 gpm per ton is a thumb rule. Everything else is, well wrong. Enhanced tubes create turbulence? Have you ever shot a rifle? Enhanced tubes don't do anything to create turbulence, if anything they would further the laminar condition.
    Another know-it-all. Use an analogy that supports my argument. The rifling inside a barrel puts a "spin" on the projectile, which is exactly what a rifled or an enhanced tube does to the fluid inside of it. Without rifling inside a rifle barrel the projectile would not spin just like laminar flow, no? Internally enhanced tubes create two benefits...enhanced heat transfer and the opposite of laminar flow. Call it what you will...turbulence, non-laminar...whatever. HRS heat transfer has a good video on YouTube if you care to watch it.
  • 05-12-2012, 11:27 AM
    waterworld
    Quote Originally Posted by KnewYork View Post
    This statement cannot be made unless you know the characteristics of the tube. Most manufacturers (if not all) are using enhanced tubes that promote turbulence of the water inside the tube. The manufacturer I worked for published minimum and maximum flows through the vessels based on feet per second. I believe the water treatment community has an issue with proper treatment if the flow drops below 3'/sec. That threshold isn't reached in most condenser selections at 3 GPM per ton. Your claim of a drop in 20% of rated flow will cause laminar flow just isn't true, not with tubes that have internal enhancements.
    The only thing you are right about is that the 3 gpm per ton is a thumb rule. Everything else is, well wrong. Enhanced tubes create turbulence? Have you ever shot a rifle? Enhanced tubes don't do anything to create turbulence, if anything they would further the laminar condition.

    Enhanced tubes were designed to keep a rigid structure surrounding the tube wall while have lower depressions to allow for increased heat transfer. They don't do anything for turbulence.

    Turbulence is caused by a rapid variation of velocity and pressure in a fixed space and within a fixed time. Basically shoving 12 lbs. of **** into a 5 lb bag in a second... enhanced tubes don't contribute to any of those factors.

    Oh and as for feet per second... I understand what you mean and i've not heard of feet per second being used for condensers in HVAC applications. That doesn't mean your wrong I've just no heard of it. I can say that no matter the min/max flow recommendation for a condenser in gpm/ton or ft/sec will correlate. Is has to.
  • 05-12-2012, 07:25 AM
    KnewYork
    Quote Originally Posted by waterworld
    A centrifugal chiller must have 3 gpm per max design ton in the condenser. If you have less, by even 20%, no matter what your load is, then you will create laminar flow.
    This statement cannot be made unless you know the characteristics of the tube. Most manufacturers (if not all) are using enhanced tubes that promote turbulence of the water inside the tube. The manufacturer I worked for published minimum and maximum flows through the vessels based on feet per second. I believe the water treatment community has an issue with proper treatment if the flow drops below 3'/sec. That threshold isn't reached in most condenser selections at 3 GPM per ton. Your claim of a drop in 20% of rated flow will cause laminar flow just isn't true, not with tubes that have internal enhancements.