Topic Review (Newest First)

  • 10-16-2012, 01:24 PM
    automig
    going out and buying a bluevac!

    i have one of those yellow jackets in the case, it cost a million dollars, the fittings all leak and the thing barely stayed calibrated for a year. i just buy a new supco from united two or three times a year, whenever i start feeling uneasy about its accuracy.

    many of my co-workers swear by wet-bulb types, brand name of Vac-in-ol. this type of thing http://www.wetbulbinstruments.com/
  • 10-16-2012, 01:02 PM
    itsiceman
    My BluVac has been beat to hell and I would still put it up against any other one out there.
  • 10-16-2012, 09:32 AM
    joeyd
    I don't toot my own horn much, but I thought this was worth sharing, especially in this thread.

    I was contacted a few days ago by a university student doing post graduate work involving deep vacuum. The lab in which he works has high quality vacuum instrumentation, but he wanted a personal micron gauge of his own. He purchased the UEI DMG100 (the yellow version of the BluVac LTE), and was having problems getting readings less than 100-200 mTorr (microns). We exchanged a few phone calls and emails, and I gave him some suggestions. I received an email from him this morning:

    I used your suggestion #2 and I was able to pull down to 0 mtorr -- the
    accuracy of your gauge matched the accuracy of our gauge within a few mtorr
    -- your gauge performed better than advertised. I appreciate our
    communications as you are very astute, clear and helpful. You have designed
    an amazing product and I will speak very highly of your gauge.
    It is for comments like this that I do what I do...
  • 10-12-2012, 12:31 PM
    joeyd
    Quote Originally Posted by PDImeters View Post
    ...because I honestly think that it is one of the best available today.
    A sincere 'thank you' for the compliment!

    Quote Originally Posted by PDImeters View Post
    ...all of them eventually will loose their accuracy as they are producing heat and in layman's terms will eventually burn out.
    The BluVac operates at a *very low* temperature compared to other gauges. This is one of the reasons why it has such a long battery life. The sensor will never burn out. But, the sensor can, and will, change slowly over time. Not just from usage and wear, but also due to contaminants settling on the sensor. The self-calibration feature takes these issues into effect and negates them through time.

    Quote Originally Posted by PDImeters View Post
    Is there any limit to the number of times that you can "reset" the calibration?
    There is no limit whatsoever. The BluVac can be recalibrated as often as desired, and each recalibration compensates for any wear or drift of the sensor over time. In fact, *full* factory accuracy is restored via recalibration.
  • 10-12-2012, 11:22 AM
    PDImeters
    Quote Originally Posted by itsiceman View Post
    The 69075 is a Yellow Jacket not J/B
    The OP wants to know about the J/B DV-40 vs the BluVac. Have you used the J/B DV-40 and compared it to anything like the OP?
    FWIW you should add a link to your web site on your youtube videos. Had to do the kevin bacon game to find your web site
    It did not come up well with a google search either
    I saw that thing the other day and it looks nice
    Itsiceman,
    First, thanks for the recommendation. I have the web address in the videos but no link on the channel. I will fix that. Also thanks for taking the time to Kevin Bacon my site. I appreciate it. I am working with some stuff to improve my google results but unless you want to just write a big check it takes some time to get the search results you want. Oh the fun that is internet marketing and search engine optimization.

    As for the DV-40 Supernova, I have used it. I was not impressed. I got one when they first came out. The first one i bought had some sort of defect right out of the box. The readings were all over the place but my local distributor and JB were great about the replacement. I am a manufacturer so I know that sometimes these things happen and I didn't hold anything against it for this. However, I was just not very impressed with its' accuracy repeatability/reliability. Full disclosure, I never put it to use in a field setting. All testing I did was in a "lab" or factory setting so some of the things that we put it through were a bit unrealistic and I was testing it with a $2,000 NIST certified vacuum gauge. That is how we evaluated all commercial gauges.

    Second, thanks for catching my mistake. The 69075 is Yellow Jacket. I brain farted that and didn't catch my slip. That being said, I still think that the YJ 69075 is a pretty okay micron gauge. It is certainly not as compact as the Supernova or the BlueVac and the BlueVac is more accurate and reliable. The price and durability (probably because of the big honking case) of the 69075 made it one of the more preferred gauges I have used. Although, we would regularly (every 6 months or so) line it up with the NIST gauge and identify any drift in the readings. Then I would just add a little sticker to the case with a "+50 microns" or "-100 microns" or whatever the case so that the guys using it would know if they had any additional compensation to factor in their readings.

    If I were to buy a gauge for field use, I would probably go with the BluVac for two reasons. 1- It is very accurate, compact, reliable and durable. and 2- The people that you would be dealing with if you bought that gauge would be people like Jim or Bill from TruTech and JoeyD. That is a value that goes beyond what you could normally expect. I prefer to deal with these more personal companies than massive corporations.

    But that is just my opinion and I have been wrong once before although I wouldn't admit that to my wife.

    Last, Fantastic quote at the bottom of your postings.

    Thanks
  • 10-12-2012, 10:45 AM
    PDImeters
    Quote Originally Posted by joeyd View Post
    Not entirely true. Yes, since the thermal conductivity sensors are exposed directly to the atmosphere being measure, all TC base micron gauges lose accuracy over time. But, the BluVac is the *only* micron gauge that will both tell you if it is out of calibration (or, if it is contaminated with oil), and that allows you to recalibrate it back to factory specifications simply by placing it in your freezer. No additional hardware or reference gauges required.

    JoeyD, thanks for the additional information. Also, let me be upfront here and say that I am certainly not saying anything bad about the Bluevac, your gauge, because I honestly think that it is one of the best available today. I am just trying to offer some insight I have gained about the mysterious world of vacuum and vacuum gauges. I understand how these sensors work and I do believe, please correct me if I am wrong, that all of them eventually will loose their accuracy as they are producing heat and in layman's terms will eventually burn out. The freezer recalibration function of the BlueVac is a brilliant addition and from what I have seen, the BlueVac's life is head and shoulders over most. About that, I have one question. Is there any limit to the number of times that you can "reset" the calibration?

    Further, many micron gauges are only rated for accuracy at a particular micron level or narrow micron range, *and* at a specific temperature (normally, room temperature). The BluVacs are rated for full accuracy from 0 to 25,000 microns throughout the entire temperature range of -10C to 50C.

    Full disclosure: I am the inventor, designer, and manufacturer of the BluVac/BluVac LTE.
    Finally, not to just continue and blow sunshine but I have to say that your did it right with this large of a range. Even with a small leak in a system, it is possible to get down to this range of 25,000 microns so the tech knows that their gauge is working and can then go about finding the leak or other issue when their gauge doesn't look to be dropping quickly. Some of the gauges that don't start accurately registering until the lower ranges (10K micron or 5K microns) make it very difficult to know if it is the system or the tools.

    Thanks for the contribution and information.
  • 10-11-2012, 09:03 PM
    joeyd
    Quote Originally Posted by PDImeters View Post
    I have seen and used almost every single commercially available micron gauge. Bluevac and JB(69075) do well and so does Inficon. All of them loose accuracy over time...
    Not entirely true. Yes, since the thermal conductivity sensors are exposed directly to the atmosphere being measure, all TC base micron gauges lose accuracy over time. But, the BluVac is the *only* micron gauge that will both tell you if it is out of calibration (or, if it is contaminated with oil), and that allows you to recalibrate it back to factory specifications simply by placing it in your freezer. No additional hardware or reference gauges required.

    Quote Originally Posted by PDImeters View Post
    Commercial micron gauges have sensors designed to start reading vacuum only under a certain level. That level could be 20,000 microns 15,000 micron 5,000 micron or even as low as 1,500 microns.
    Further, many micron gauges are only rated for accuracy at a particular micron level or narrow micron range, *and* at a specific temperature (normally, room temperature). The BluVacs are rated for full accuracy from 0 to 25,000 microns throughout the entire temperature range of -10C to 50C.

    Full disclosure: I am the inventor, designer, and manufacturer of the BluVac/BluVac LTE.
  • 10-11-2012, 07:01 PM
    itsiceman
    Quote Originally Posted by PDImeters View Post
    I have seen and used almost every single commercially available micron gauge. Bluevac and JB(69075) do well and so does Inficon. All of them loose accuracy over time and none of them can accurately measure the full range from Atmosphere to deep vacuum. The only gauges that accurately and reliably measure the full range for extended periods of use are the big money bench top ones for lab use and they wouldn't survive in the field.

    What you need to know about whatever gauge you use is this. What is the actual range of the sensor? Commercial micron gauges have sensors designed to start reading vacuum only under a certain level. That level could be 20,000 microns 15,000 micron 5,000 micron or even as low as 1,500 microns. Everything the gauge shows you above that is only an estimate and not based on the sensors designed capabilities. If your not sure where you gauge sensors range is, contact the manufacturer or their rep. This piece of information is crucial to using any micron gauge.

    My recommendation is to pick the most appealing one based on price, range and specified accuracy and then do everything you can to ensure a tight and isolated system when you evacuate. Always put the micron gauge as far away from the pump as possible and isolate the pump from the system and gauge for a true reading of depth.
    The 69075 is a Yellow Jacket not J/B
    The OP wants to know about the J/B DV-40 vs the BluVac. Have you used the J/B DV-40 and compared it to anything like the OP?
    FWIW you should add a link to your web site on your youtube videos. Had to do the kevin bacon game to find your web site
    It did not come up well with a google search either
    I saw that thing the other day and it looks nice
  • 10-11-2012, 05:17 PM
    PDImeters
    I have seen and used almost every single commercially available micron gauge. Bluevac and JB(69075) do well and so does Inficon. All of them loose accuracy over time and none of them can accurately measure the full range from Atmosphere to deep vacuum. The only gauges that accurately and reliably measure the full range for extended periods of use are the big money bench top ones for lab use and they wouldn't survive in the field.

    What you need to know about whatever gauge you use is this. What is the actual range of the sensor? Commercial micron gauges have sensors designed to start reading vacuum only under a certain level. That level could be 20,000 microns 15,000 micron 5,000 micron or even as low as 1,500 microns. Everything the gauge shows you above that is only an estimate and not based on the sensors designed capabilities. If your not sure where you gauge sensors range is, contact the manufacturer or their rep. This piece of information is crucial to using any micron gauge.

    My recommendation is to pick the most appealing one based on price, range and specified accuracy and then do everything you can to ensure a tight and isolated system when you evacuate. Always put the micron gauge as far away from the pump as possible and isolate the pump from the system and gauge for a true reading of depth.
  • 10-11-2012, 11:19 AM
    cuervo
    Thanks for taking the time to make the videos and posting! I guess trust no vacuum gauge.
    My question though is..... Which vacuum gauge will you continue to use?
    I would love to hear what Accutools would say about the video.

    Quote Originally Posted by Pascone10 View Post
    http://www.youtube.com/watch?v=G_6iOKzAuDA

    http://www.youtube.com/watch?v=idWheO5bogQ

    http://www.youtube.com/watch?v=IeHpFOgvhY0

    I had doubt in micron gauges as well so I did some non-scientific tests. My conclusion.. THey all like to read differently.. Some are way further off then others.. In my experience that Supernova gauge is JUNK..
  • 10-10-2012, 10:05 AM
    nsula_country
    I bought it used, lightly used. EBAY, about $170 shipped! Do not be too judgmental, I was using my manifold to evacuate. I did get around 300 millitorr on each unit. Called it good enough, they are my units.

    Attachment 316451

    CT
  • 10-09-2012, 07:53 PM
    supertek65
    wow
    just looked at it

    is it for use in the field??????????
  • 10-09-2012, 07:51 PM
    primmers
  • 10-09-2012, 07:50 PM
    supertek65
    wow
  • 10-09-2012, 07:47 PM
    primmers
    the yellow jackets list price..
  • 10-09-2012, 07:42 PM
    supertek65
    what is $750???????
  • 10-09-2012, 07:40 PM
    primmers
    at $750 it better work....
  • 10-09-2012, 07:21 PM
    supertek65
    if i do a small res split

    i just put the micron gauge on the high side only, no hose.

    then vacuum from the suction side.

    this way i trust the micron gauge reading.

    as for which one is correct?

    who knows?
    are they both temperature compensated?
  • 10-09-2012, 07:13 PM
    valdelocc
    Quote Originally Posted by itsiceman View Post
    valdelocc How old is your DV-40? I had two DV-40's close to when they came out and they were both where a joke compared to my Thermal. I only ever saw reading in the same ballpark when to was a hot summer day.
    got it last year as a Christmas present, I'll take pictures next time I use them.
  • 10-09-2012, 07:10 PM
    itsiceman
    valdelocc How old is your DV-40? I had two DV-40's close to when they came out and they were both where a joke compared to my Thermal. I only ever saw reading in the same ballpark when to was a hot summer day.
This thread has more than 20 replies. Click here to review the whole thread.