  • 08-12-2012, 12:17 PM
    Pete954
    Had this same problem numerous times 4 summers ago and that's how we solved it. Braze and leakcheck first so you can pull your vacuum while doing everything else. That way it can run for a good while before making any adjustments. Also turned out we getting trigger happy since 410 takes longer to register an adjustment.
  • 07-30-2012, 12:11 AM
    sparky05
    Quote Originally Posted by hvacmike85 View Post
    1 deg says it wasnt your filter dryer, but the txv, and I always do the dryer exp when theres a problem, manf says change dryer when system is opened for any reason but some people just dont wanna pay for a 20$ dryer, some H/O are just smarter than us I guess, anymore I just include it in the pric3 and dont tell em cause it will just raise questions
    Not according to the Manufacturers Technical Rep, They came out to see how a unit could have a negative S/C, after checking through the system with me he determined it was probably a clogged up filter dryer, the recommendation to change the TXV was so we would not have to pump down the system again to change it if there were other problems.
  • 07-29-2012, 11:07 PM
    hvacmike85
    Quote Originally Posted by hurtinhvac View Post
    If they are sincerely trying, they are probably not letting it run long enough before adding and in between shots. The liquid line temp that appears not to be dropping in response to adding Puron can suddenly take a dive quickly if the system is allowed to run long enough.

    I usually start cleaning and do pretty work while letting a new install cook for a half an hour, give it a shot and go back to clean up, putting away tanks and tools and loading up the old equipment - coming back periodically to check and give it another shot if needed.
    it can't run too long before checking charge on new exp
  • 07-29-2012, 10:30 PM
    hurtinhvac
    Quote Originally Posted by Tinner67901 View Post
    Here's what I have been finding. I keep getting sent back on our installers new installs. When I get there I keep finding overcharged units. Its usually 90 inside and 90-100 outside when they are setting these units. They say they are charging them to 10 degrees subcooling. When I go back the indoor temp is usually 70-80 depending on the person. The outdoor temp is still 90-100. My subcooling is extremely high around 40-50 degrees. I always remove refrigerant to reach 10 degrees subcooling. What is going on here and how can I help them stop overcharging these units?
    If they are sincerely trying, they are probably not letting it run long enough before adding and in between shots. The liquid line temp that appears not to be dropping in response to adding Puron can suddenly take a dive quickly if the system is allowed to run long enough.

    I usually start cleaning and do pretty work while letting a new install cook for a half an hour, give it a shot and go back to clean up, putting away tanks and tools and loading up the old equipment - coming back periodically to check and give it another shot if needed.
  • 07-29-2012, 10:14 PM
    hvacmike85
    Quote Originally Posted by sparky05 View Post
    On that unit, I got there and figured it was low on charge because it had had a leak, put a whole can of 410 into system and the S/C went from -5F to +4F it was when I looked at the name plate rating to see it should only take a little over 17 Lbs that I realized there was something drastically wrong so I recovered nearly 30 Lbs of 410A and weighed in the correct amount, but S/C only got to 2F.
    I found that there was a 1F drop across the bi flow filter dryer, and I decided to change out the TXV the same time so I would not have to do it again just in case, it might have been stuck in full open position.
    1 deg says it wasnt your filter dryer, but the txv, and I always do the dryer exp when theres a problem, manf says change dryer when system is opened for any reason but some people just dont wanna pay for a 20$ dryer, some H/O are just smarter than us I guess, anymore I just include it in the pric3 and dont tell em cause it will just raise questions
  • 07-29-2012, 10:09 PM
    sparky05
    On that unit, I got there and figured it was low on charge because it had had a leak, put a whole can of 410 into system and the S/C went from -5F to +4F it was when I looked at the name plate rating to see it should only take a little over 17 Lbs that I realized there was something drastically wrong so I recovered nearly 30 Lbs of 410A and weighed in the correct amount, but S/C only got to 2F.
    I found that there was a 1F drop across the bi flow filter dryer, and I decided to change out the TXV the same time so I would not have to do it again just in case, it might have been stuck in full open position.
  • 07-29-2012, 10:00 PM
    sparky05
    Did you chance out the filter dryer? had a situation here on Friday where I could not get the Sub cooling correct on a unit, it was actually a negative 5 when it should have been a positive 12F, changed out the TXV and liquid line filter dryer, recharged the unit now everything is working correctly.
  • 07-29-2012, 08:33 PM
    hvacmike85
    Quote Originally Posted by coronachris0711 View Post
    I came across this problem today.... not the first time this has happend to me...

    I changed out a indoor r410 a coil. Factory charge was 5 lbs 5 oz. Line set was about 40 feet. I charged in 6 lbs 5 oz. The system called for 14 degree subcooling.

    Head was 350 PSI
    Liquid line temp was 101
    Indoor ambient 75
    Supply air temp 59
    Suction pressure 150
    Outdoor temp 90

    I needed liquid line to come down to 96 or so.... I tried adding 410 to pull down liquid line temp but everytime i did the liquid line temp would stay the same. Any one know what could cause this?

    I guess my main question in regards to installers overcharging systems: What causes liquid line temp to stay the same or even increase after adding more 410?
    Alot of times I've noticed the liq line temp doesnt change much the liq press goes up which increases s/c that way, not sure why, but if your not getting s/c adding a ton of 410 will just result in an overcharge, you can only get so much s/c but it should let you go way past 14 if you wanted ( not that you do ) something might be wrong, always check s/h also, if your superheat is low you might have low airflow of stuck open txv, s/c is the charging method for txv systems but wont tell you all what is wrong
  • 07-29-2012, 08:14 PM
    Toddbrewster
    It seems like goodman is not a good name on here, I am a goodman dealer, so far had good luck, just was curious as to what the general opinion of goodman is. I have done a lot of commercial and residential work, worked on a ton of different brands, I have some I do not care for, carrier/bryant both commercial and residential have terrible heat exchangers, dont particularly care for rheem ruud or lennox, although as I said I will work on any brand of equipment, like the challenge of learning as much as I possibly can, plus I am in the "Service" business cant be a good service tech if I cant fix something because of "name brand"! I do like trane, though they are a little more costly. Just was curious as to what it is about goodman that is disliked, maybe I need to sell a different brand. I have had units both commercial and residential from different manufactures, that have been both over and under charged from the factory, have not noticed a "rash" of any one brand being over or under charged, I check every system i install, or service and adjust the charge as needed, have had some that were fine with the factory charge with a lineset longer than 15' also have had some really over charged with a 15' line set. I also know several other companies/techs that install a system, flip the switch on and as long as the unit starts up they go no farther, no amp draw checks, no checks of gas pressure, temp. split heat or cool, no checking sh or sc on a/c or refrigeration systems, some may do the cold and sweaty test on the suction line, but most just stick out their hand for the money and take off.
  • 07-26-2012, 05:37 PM
    coronachris0711
    I came across this problem today.... not the first time this has happend to me...

    I changed out a indoor r410 a coil. Factory charge was 5 lbs 5 oz. Line set was about 40 feet. I charged in 6 lbs 5 oz. The system called for 14 degree subcooling.

    Head was 350 PSI
    Liquid line temp was 101
    Indoor ambient 75
    Supply air temp 59
    Suction pressure 150
    Outdoor temp 90

    I needed liquid line to come down to 96 or so.... I tried adding 410 to pull down liquid line temp but everytime i did the liquid line temp would stay the same. Any one know what could cause this?

    I guess my main question in regards to installers overcharging systems: What causes liquid line temp to stay the same or even increase after adding more 410?
  • 07-24-2012, 06:35 AM
    dsprice
    These extreme conditions are what I do. Teach your subs what saturation is then instruct them to charge half the subcool. The Superheat should come in at the low to mid 20's with a split of 18 to 23. It works as long as airflow is right. Personally, I don't like for installers to do start UPS. Too many variables involved.

    I understand the weigh in method, but never felt it was accurate. I can only guesstimate the length of the lineset.

    Sent from my ADR6350 using Tapatalk 2
  • 07-24-2012, 05:35 AM
    beenthere
    Quote Originally Posted by hvacmike85 View Post
    What if you used every drop in the tank the air/non condensibles won't escape?
    Not if you don't draw out all of the vapor from the tank.
  • 07-24-2012, 12:58 AM
    TACKERDOWN
    4) Additional charge for line sets above 15 feet. Values based on suction line as follows with 3/8" liquid line.(a) 3/4" = 0.6 oz. per additional foot.(b) 7/8" = 0.7 oz. per additional foot.(c) 1 1/8" = 0.8 oz. per additional foot.
    This ones out of the install manual. I thought it was in all install manuals.
    Sent from my PC36100 using Tapatalk 2
  • 07-24-2012, 12:49 AM
    TACKERDOWN
    Quote Originally Posted by ironpit View Post
    1-800-406-2292 ReKlaim center
    If you Google it it has a location finder just put in your zip code.

    Sent from my PC36100 using Tapatalk 2
  • 07-24-2012, 12:29 AM
    jamessnevets
    Regarding R-410A, I was once given a list of formulas for weighing-in additional charge when conditions were not optimal for adding charge by subcooling. The list was confiscated by a former employer of mine, but it had different weights correspondent to lineset diameters. The only one I remember b/c I use it frequently is for a 3/8x3/4 lineset, add .6 oz of R-410A per foot only if the lineset exceeds 15'. No need to measure subcooling with excessive heat conditions in the residence, and after returning to confirm, it has never failed me and I've used it since 2007. Something to check with your favorite supply house service guru. I'll see about getting the rest of it, if anyone is interested, since my current employer deals with the same supplier with the factory technician that originally gave me the list.
  • 07-23-2012, 11:22 PM
    ironpit
    drops are liquid
  • 07-23-2012, 10:49 PM
    hvacmike85
    Quote Originally Posted by beenthere View Post
    Air won't be in the liquid. Air being a vapor will only be in the top of the tank.
    What if you used every drop in the tank the air/non condensibles won't escape?
  • 07-23-2012, 09:58 PM
    beenthere
    Quote Originally Posted by ironpit View Post
    why is that?
    Air won't be in the liquid. Air being a vapor will only be in the top of the tank.
  • 07-23-2012, 09:28 PM
    ironpit
    Quote Originally Posted by beenthere View Post
    Recharge by liquid, and yo don't have to worry that the guy before you purged his gauges.r
    why is that?
  • 07-23-2012, 09:28 PM
    ironpit
    Quote Originally Posted by sparky05 View Post
    What company can I call for that, it might be worth my while to check into it.
    1-800-406-2292 ReKlaim center
This thread has more than 20 replies. Click here to review the whole thread.

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •