Topic Review (Newest First)

  • 02-21-2011, 07:19 AM
    chilbrig
    Takes an O-ring. Make real sure the internal checkvalve is holding before you unscrew the plug. Sometimes the plug can be very hard to unscrew the first time.
  • 02-18-2011, 07:12 PM
    fordtrucksrule
    3/4" ok also what seals the end is it a o-ring or just a machine seal?
  • 02-18-2011, 06:18 PM
    Dallas Duster
    Quote Originally Posted by fordtrucksrule View Post
    Another ? What size is the Allen key I need to change the internal oil fliter on the screw compressor? It looks close to 1/2 inch
    3/4" and lots of rags if you don't do it right.
  • 02-18-2011, 06:11 PM
    fordtrucksrule
    Another ? What size is the Allen key I need to change the internal oil fliter on the screw compressor? It looks close to 1/2 inch
  • 02-18-2011, 04:02 PM
    chilbrig
    15% is what it is set at from the factory. On these chillers you will get a lot of nuisance trips at that setting. I always set them at 20-22% and have never had any problems. I have been told by the Carrier 30 series guru that he has no problem at setting them up to 30%. You can only set them up to 30% with latter software.
  • 02-17-2011, 10:12 AM
    servicetrane
    the% current imbalance is 3.29 is thenormal, maximum by the plant is 15%, check electrical connections to the module cpm.etc
  • 02-16-2011, 11:03 PM
    fordtrucksrule
    ok the amp draws are as follows 76.4 78.8 and 81.4
  • 02-16-2011, 06:16 PM
    chilbrig
    The voltage imbalance setting can cause you to have alot of nuisance trips on the 30HX and 30GX chillers . It will not hurt anything to set it up to 22%. If you still have trips set it higher.
  • 02-16-2011, 03:45 PM
    servicetrane
    the percentage of voltage imbalance is 0.6%
    where maximum deviation 3volts x 100 = 300/479 = 0.626%
  • 02-16-2011, 12:12 PM
    servicetrane
    amp?
  • 02-16-2011, 12:06 PM
    fordtrucksrule
    The voltages are as flopped 477 479 482 ave is 479 so max devation is 3 volts on l3 and 2 volts on line 1
  • 02-16-2011, 09:52 AM
    servicetrane
    which is the voltage deviation? could give more details? readings of voltage and amperage
  • 02-15-2011, 11:27 PM
    emcontrols
    A1 & A2 compressor "unbalance setpoint should be 15% default" it alarms after a continuous 15% or more for 25 minutes.

    B1 "no current" if there is a call for B1 comp and there is no amp draw on all 3 legs for more than 3 seconds it will alarm.

    Are than any other alarms in history log? power fails, phase loss etc.. Thats pretty strange, might be the beggining of a board problem.

    Might check primary connections and voltages to transformers serving Klixon modules (CCP's) and secondary connections and voltages. could also be a transformer problem. It would be more logical if there are not any other alarms in history log. especially because it is with 3 compresors and it is on the amperage side (alarms) with no voltage alarms
  • 02-15-2011, 09:10 PM
    fordtrucksrule
    yes it is a wye delta starter. as far as i know no one has messed with the parameters.
  • 02-15-2011, 08:54 PM
    Dallas Duster
    Quote Originally Posted by fordtrucksrule View Post
    I had this same issue at about 3 weeks ago and i found one of the 0/1 wires going to compressor a1 at the crimp connection was bad and corroding. i had the same issue 3 weks ago same codes. ive check the contactior and check voltage drop across and they were under .03v across the contactors, so i know the contactors are good any other ideas
    Not unless someone changed the imbalance setpoint and you haven`t changed out a starter lately, it is wye delta right?
  • 02-15-2011, 07:55 PM
    fordtrucksrule
    I had this same issue at about 3 weeks ago and i found one of the 0/1 wires going to compressor a1 at the crimp connection was bad and corroding. i had the same issue 3 weks ago same codes. ive check the contactior and check voltage drop across and they were under .03v across the contactors, so i know the contactors are good any other ideas
  • 02-15-2011, 07:47 PM
    Dallas Duster
    Loose connections or you really had some sort of weird power issue with all 3 compressors going flaky.
  • 02-15-2011, 07:36 PM
    fordtrucksrule

    Carrier 30gxr

    Hey i have a carrier 30gxr225f611cl ecologic r-134a screw chiller today i walked up to it today to 4 alarms those were a152 (down due to failure) t055 (compressor b1 failure no current) and t052 and t051 (compresor a1 and a2 off due to current unbalance. I first checked the wireing to the klixon module 3 in total and check them to the mail control board and all connections were good. then i reset the chiller and got compressors a1 and b1 to come on and i check for voltage imbalance and amprage imbalance at the klixon modules and ch power at disconnect all were below 5% devation Any other ideas?