    54regcab
    Correctly sizing equipment is the way to go. Unfortunately its oversized more often than not, especially on the heat side. I have yet to see a properly operating furnace that can't keep the setpoint, regardless of how cold it gets. The analogy of not letting the truck run all night so it will be warm in the morning is valid in oversized situations..

    DOE is removing setback thermostats because they are rarely set correctly, not because they don't work. We are entering a time of variable electricity prices/smartgrid technology. With this, using your house to "store" cool air made with cheap power then raising the setpoint becomes an effective strategy. Once the power peak is over, drop the temperature back down.
    http://www.ogepet.com/programs/smarthours.aspx
  • 07-28-2012, 10:11 AM
    skippedover
    How do you decrease temps in summer and increase temps in winter? The real answer lays in the equipment design temperatures.

    If the design temp is 90°F and at that temperature 35,000 Btu's is just break even with a 74°F indoor temp with 50% RH, then the fact is that there is 35,000 Btu's of energy coming into the home every hour and the unit runs continuously to remove that 35,000 Btu load (both sensible and latent). Now let's run the temperature up to 80°F for the day and set the 74°F for a 5pm arrival home from work. The savings of the setback (setup) temperature of 80°F is comprised of both the dwell time between a call for cooling at 74°F and a call at the new temperature of 80°F, as well as the temperature difference by maintaining a higher temperature during the day. So now the outdoor temperature reaches design conditions at 1pm. How many Btu's of capacity must the system provide to maintain 80°F and 50% RH? Something less than 35,000 Btu's because we're only holding 80°F, not 74°. So let's assume for discussion it's 30,000 Btu's.

    Now it's nearing 5pm and time to decrease the temperature to 74°F. Since that is a lower ambient indoors, the relative humidity will begin to increase as the system tries to bring the temperature down. This is where the potential rub comes into play. As the indoor temp comes down, the RH is trying to move in the opposite direction and more of the Btus are being diverted to latent work than sensible work. In all likelihood, the bulk of the 5,000 Btu's saved per hour at 80°F is going to latent heat removal now, thus leaving a system sensible capacity to pull down the temperature to 74°, all while battling a temperature influx of 35,000 Btu's/hour.

    So the answer to the question of do I or don't I is really an answer predicated on how much excess capacity there may be in the system at any given outdoor set of conditions up to design temperature. The closer the system is to design size, the less 'excess' capacity is available to return to the occupied set-point. This is just as true for heating as for cooling, except you don't have the diversion of Btu's to latent work. But as the OAT approaches design temp on heating, the amount of excess capacity available to raise temps from set-back is less and less. Many people have discovered this limitation on setback t-stats and just as many have abandoned the use of set-back due to discomfort at near design temperatures. In fact, the DOE has entertained removing set-back t-stats from the rebate program due to lack of proper use and the resulting insufficient energy savings.

    The best savings for heat are the systems that actually reference the outdoor temperature and control the output of the heating system accordingly. Thus they provide the necessary Btu's under all conditions without the need to actually vary the room temperature and it's all done without the homeowner/building manager needing to thoroughly understand the needs and limits of the heating equipment. We're now beginning to see this in the variable speed heat pumps that are available, where they can deliver an infinite number of Btu settings from 30% of maximum all the way up to or slightly above their rated maximum, thus allowing for larger systems to be installed for extreme temperatures for heating but still have the smaller outputs needed for proper cooling and latent heat removal.
  • 07-28-2012, 09:20 AM
    7X
    Strictly speaking from the combustion heating side - I remember quite a while back there was some testing done and conclusions made. I was told years ago that you could save 1%/degree/8hrs. Set back 10 degrees for 8 hours and potentially save 10%. I certainly think it is site specific but as long as you are not cooling the thermal mass in the building (and most buildings will "coast" pretty well for a while), it does not take all that much time or fuel to reheat mostly the air. This is also essentially what DoE states on their EERE website.

    I simple analogy for the layperson would be that you did not leave your truck running all night long so it would be warm for you in the morning.

    If anyone has any empirical data on this topic, I would be interested in seeing it.
  • 07-25-2012, 12:37 PM
    midhvac
    Quote Originally Posted by WeebMan View Post
    I realise settings are going to vary according to personal preference. I wasn't asking what is the most efficient and comfortable way to operate the system. Just, what is the most efficient? Thats all. Would it cost less to leave my stat on 68 from the beginning to the end of the summer, or is setting it back during the day (like I'm doing) more cost effective.
    It will always use less kWh per season by setting it back. How much less depends on numerous variables. But if the electric co. is charging you more per kWh at "peak" hours of the day, that must be factored into the savings equation.
  • 07-25-2012, 09:37 AM
    WeebMan
    Quote Originally Posted by CraziFuzzy View Post
    If it was a simple yes or no answer, thermostats wouldn't have any adjustments in them, and they would all be set permanently at the 'right' setting.
    I realise settings are going to vary according to personal preference. I wasn't asking what is the most efficient and comfortable way to operate the system. Just, what is the most efficient? Thats all. Would it cost less to leave my stat on 68 from the beginning to the end of the summer, or is setting it back during the day (like I'm doing) more cost effective.
  • 07-25-2012, 09:10 AM
    CraziFuzzy
    Quote Originally Posted by WeebMan View Post
    I didnt realize what an open ended question this was. Lol.
    If it was a simple yes or no answer, thermostats wouldn't have any adjustments in them, and they would all be set permanently at the 'right' setting.
  • 07-24-2012, 09:26 PM
    KevinAdv
    I wish I could afford to run mine at 68. Although I don't even know if it will cool that low
  • 07-24-2012, 03:58 PM
    WeebMan
    And comfort wasnt my reason for asking. I was just wanting to know which was gonna cost less on the electric bill.
  • 07-24-2012, 03:55 PM
    WeebMan
    Quote Originally Posted by CraziFuzzy View Post
    Sounds like you should just keep it at 80 and be satisfied then...
    Well, I think it has something to do with dehumidifying for 5 degrees that maked 80 feel okay. Plus the fact that theres cool air circulating. Cuz to just set it at 80 doesnt cut it for me.

    I didnt realize what an open ended question this was. Lol.
  • 07-24-2012, 03:18 PM
    CraziFuzzy
    Quote Originally Posted by WeebMan View Post
    Mine doesnt catch up till after I go to sleep... but Idc cuz by the time it brings it down from 85 to 80 it feels good. Then it spends the rest of the evening bringing it down to 68.
    Sounds like you should just keep it at 80 and be satisfied then...
  • 07-24-2012, 12:01 PM
    midhvac
    Quote Originally Posted by hvac wiz 79 View Post
    who the hell wants to wait for a system to recover while being uncomfortable?
    LOL, that's a huge part of the variables involved here. I have some customers that are willing to make that sacrifice in comfort to save x $ over the course of an entire cooling season. But those aren't the norm. And this is one reason I mentioned the "intelligent recovery" thing.
    EVERYONE'S system is oversized during the vast majority of the cooling season. So they could be saving money the rest of the cooling season if they had an effective way of doing that. And there would be little or no loss in comfort level if the stat was smart enough to ensure it.
    But as someone mentioned, some of the electric company's are starting to charge more per kWh during peak demand hours. And that obviously reduces the potential savings.
  • 07-24-2012, 11:13 AM
    hvac wiz 79
    who the hell wants to wait for a system to recover while being uncomfortable? .. set it for what you like & leave it unless if you plan on going away for extended periods of time. im not one to figure the calculations but couldnt all that time during a hot pulldown every day cost considerably close to what a few cycles an hour would be when your at your desired setpoint during the day? .. i leave mine to cycle as needed & have very low utility bills. granted this is a building constructed in 2011 but still ....
  • 07-24-2012, 10:58 AM
    midhvac
    And with most programmable stats, there's the variable of whether or not you have the stat set to "automatically recover" from the setback, i.e. the "energy management" algorithm, where the stat decides how early the system must come back on to cool the house down to the programmed temp at the programmed time.
    That feature is selected by default on the stats I sell. But it can be deselected.
  • 07-24-2012, 12:09 AM
    WeebMan
    Mine doesnt catch up till after I go to sleep... but Idc cuz by the time it brings it down from 85 to 80 it feels good. Then it spends the rest of the evening bringing it down to 68.
  • 07-23-2012, 11:33 PM
    KevinAdv
    unless the system is way oversized setback does not work here

    A couple of degrees is okay but if you turn it up to 85 during the day the unit will still run and not recover till probably midnight.

    However setback works great with a furnace here because they are always oversized. I usually just leave mine off then heat the house up to 82 before bed and then shut the thing off the rest of the night
  • 07-23-2012, 08:13 PM
    54regcab
    I have the meter connect program and have done it both ways. Setback saves money for us. The loss of efficiency by running more during the hot part of the day is more than offset by the long run cycle time. The short cycles by leaving the A/C on all day cost more than the higher temperatures during the recovery period.
  • 07-23-2012, 05:32 PM
    martyinlincoln
    I'm in with the a degree or two crowd. Reason being an average to tight home isn't going change temp more than 3-4 degrees in a 8-10 hour period even with the system off. A loose/poorly insulated house on the other hand will have wild swings and when you're at or near design temp it's not going to recover from that setback for many,many hours.
  • 07-23-2012, 11:46 AM
    Greend88
    Simplest way for them to find out if it's cost effective is to try it and log there electricity usage with setback and without setback. Pretty good programs out there for smartphone or computers that let you type your meter numbers in and get a daily report of how many KWH your using. I was just having my stat set at 76 all day long and my average KWH was 4.5 KWH and with setback I've dropped it to 2.8 KWH. BIG Difference considering I only use a degree or two setback, In the morning 7am I raise the temp to 77*; 10:30AM 78*; 7:30PM 77*; 9:30PM 76*

    These numbers are 95+ to 105+ Degree days, haven't had any days lower than that lately. A/C use to run Non-Stop during the day at 76* but cycles decently at 78*
  • 07-23-2012, 10:33 AM
    motoguy128
    Quote Originally Posted by 54regcab View Post
    Theory 1: Setback does save money, but not as much as correctly sizing equipment to begin with. Quick recovery means your unit is too big, so setback for now and replace with smaller equipment when the time comes.

    Theory 2: More utilities are going to time of use rates where power is more expensive during times of peak demand. In our area going warmer from 2-7 weekdays will has the biggest effect on your bill since that's when power is most expensive.
    +1 on both.

    I'd also add, that if you do the math, that setback only saved you roughly 20% on your heat gain for that period. The "cost" of that setback instead of running your ac all afternoon at an average temprature of lets say 85F, is now running it during the hotest part of the day when it's least efficient so it's running at least 20% less efficient than if it had cycled all day.

    Geothermal...yes, expecially one sized for heating load, absolutely use as much as your system can recover from in about 2 hours... although I'd monitor the ground water tmeps to see how much they rise during that time.

    Furnace, yes, as much as it can recover from in 2-3 hours.

    If you have a 2 stage AC, absolutely do not use setbacks. Cycling in low stage all afternoon is a LOT more efficeint than running for 1-2 hours straight on high stage in the heat of the day.


    Personally, I setback just 1 F around 8AM, then drop the temp 1F at 9PM for sleeping. At night I setbakc my downstairs from 10PM to 5:30AM by 5F, then recover back to 76F, then set to 77F at 8AM, then 76F at 8PM again for relaxing and watching TV.

    For my furnace in winter I setback downstairs at night by 8F (downstairs is way oversized) and upstairs by 2F (more for comfort). In the afternoon both are setback by only 3-4F.


    Now just ot complicate matters further. Larger homes and expecially those with a lot fo thermal mass, often heat and cool off very slowly. In my house even when 100F outside will only gain about 3F upstairs from 8AM to 5PM. But it will also take 6-8 hours to recover. Heck we lost power for just 45 minutes last week and it took it 4 hours to recover the 1 F lost since it was well above design temperatures outside.
  • 07-23-2012, 09:42 AM
    da_poppa
    I can't speak for the cooling side, but on the heat side setting temps back more than a few degrees, maybe 4-5, does not decrease operating costs. As objects in the heated area cool off, they reach a point where they seem to act as chillers when the system is trying to come back to the higher temp. This can become an issue more so if the heating system has been properly sized. If there's a new, high efficiency system, setback may turn into a difference between comfort and cost.