Reply to Thread

Post a reply to the thread: 30 HXC not Starting

Your Message

 
 

You may choose an icon for your message from this list

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Additional Options

  • Will turn www.example.com into [URL]http://www.example.com[/URL].

Topic Review (Newest First)

  • 09-05-2012, 06:17 PM
    Gibbo
    I am doing ok Dallas even better now i have seen your latest batch of cheerleaders off to have a lie down to recover lol.
  • 09-04-2012, 09:37 PM
    Dallas Duster
    Merci pour l'affirmation sur ce refroidisseur français a fait, Gibbo.
    The controls on your chillers are somewhat different from ours but I kinda like the control panel.
    How are things going in your part of the world???
  • 09-04-2012, 04:50 PM
    Gibbo
    As Dallas Duster has said your suction pressure (SST) is below freeze point and circuit will be held off on Mode 13.
    To verify this press menu button until the light stops at the information icon top left then press the down arrow on the right until item 1 appears in left display now you will see active mode on the right.
    Do you have the controls manual there is a list of active modes in there.
    Guys this is a French made Carrier chiller, the Pro Dialog Plus controller is mainly for Europe, Africa and the Far East markets, some of the 60HZ units have ended up on drill ships and oil rigs. Freshwater seem to have quite a few of them.

    Nice to see your alive and kicking Dallas.
  • 09-04-2012, 01:55 PM
    Tommy knocker
    Sorry for the double post. Server keeps kicking out says it can't post so I retyped and resent then TADA it magically sends the original too. Haha.
  • 09-04-2012, 12:49 PM
    Tommy knocker
    Log it. Go through pressure, temps etc and write it all down and look at it. If not sure what data should look like shut B down let it sit 30 min or so and log it then compare.
  • 09-04-2012, 12:43 PM
    Tommy knocker
    Log it. Go through temps and pressures etc. write everything down and then look at it. If your not sure what the data should look like shut B down let it sit for 30 min or so then log it and compare. If you have no alarms I would suspect, as others have pointed out, it's not being told to run.
  • 09-04-2012, 06:35 AM
    Dallas Duster
    Quote Originally Posted by Offshorefool View Post
    I get an alarm on everything else, if I disconnect any other sensor it will give me an alarm.
    Well duh.
  • 09-04-2012, 01:46 AM
    Offshorefool
    I get an alarm on everything else, if I disconnect any other sensor it will give me an alarm.
  • 09-03-2012, 11:17 PM
    Dallas Duster
    Sure it would if the compressor comes on and try's to run but probably not since the compressor will not start . Like I said most likely there is a mode 13 .

    So in other words alarms not mode yes.
  • 09-03-2012, 11:12 PM
    Offshorefool
    Will there be an alarm if the unit is low on charge and not starting because of this?
  • 09-03-2012, 10:46 PM
    Dallas Duster
    Quote Originally Posted by Offshorefool View Post
    Thats correct, circuit A not running. My fluid setpoint is 4.7 deg C
    My theory is that your SST is below the brine freeze point and either your circuit A is low in charge or the transducer is reading incorrectly. You may need to get someone to check it out.

    Also you may have a mode 13 showing.
  • 09-03-2012, 10:29 PM
    Offshorefool
    Thats correct, circuit A not running. My fluid setpoint is 4.7 deg C
  • 09-03-2012, 10:13 PM
    Dallas Duster
    Quote Originally Posted by Offshorefool View Post
    Dallas Duster, Under active modes in the i menu there is nothing at the 1st parameter, it only starts from the 2nd parameter.
    The pressure for A is High = 317 and Low is 165
    The oil level input is high and the oil diff press is 13 kpa for comp A and 20 kpa for B
    In my manual I do not have the paramer legend for the service menu, I copied the parameters on a paper and compared them with another chiller that is in good running condition and it is the same.
    What is your fluid set point?

    And those pressures are on cir A not running right?

    What is your brine freeze point?
  • 09-03-2012, 09:29 PM
    Offshorefool
    Dallas Duster, Under active modes in the i menu there is nothing at the 1st parameter, it only starts from the 2nd parameter.
    The pressure for A is High = 317 and Low is 165
    The oil level input is high and the oil diff press is 13 kpa for comp A and 20 kpa for B
    In my manual I do not have the paramer legend for the service menu, I copied the parameters on a paper and compared them with another chiller that is in good running condition and it is the same.
  • 09-03-2012, 06:06 PM
    Offshorefool
    The model number is 30HXC140-A0427-PEE with Pro Dialog Plus Software version 5.3
  • 09-03-2012, 05:39 PM
    milkyway
    Quote Originally Posted by Offshorefool View Post
    I have been through the manual now a couple of times but I cannot find anything that will disable or enable one of the compressors at a time. If someone can direct me to this parameter I will appreciate it.
    Ccs posted this earlier
    If this is a Comfortlink panel,,, look in configuration and go to service menu. In that menu look for Compressor A1 enable. Is that compressor enabled or disabled. If your not getting alarms or alerts and the compressor is enabled. Get out the service manual and start at the beginning in configs and check all settings. I agree with Dallas Duster, it appears most likely the compressor is disabled. It would help if we knew what version we are dealing with. Provide the full model number.

    Here is ur answer
  • 09-03-2012, 02:17 PM
    Dallas Duster
    What modes are displayed under the i menu?

    What is the control point?

    What are pressures and temps of circuit A according to the PD plus?

    What is the circuit load sequence?

    Plus a log of circuit B may help converted to US.

    What is the position of the oil level input ,high or low?
  • 09-03-2012, 01:51 PM
    Offshorefool
    I have been through the manual now a couple of times but I cannot find anything that will disable or enable one of the compressors at a time. If someone can direct me to this parameter I will appreciate it.
  • 09-03-2012, 01:35 PM
    Offshorefool
    The full model is 30HXC140-A0427-PEE with Pro Dialog Plus
  • 09-03-2012, 12:31 PM
    Dallas Duster
    Quote Originally Posted by rscamaro View Post
    If that was a problem it would have alarmed a pre oil or low oil flow. Sounds like a compressor is disabled to me as you said earlier.

    ...Ron
    Exactly why I was wanting to know what the oil pressure is.

    I would also want to know what the discharge gas thermistor is reading for the effected compressor..