Topic Review (Newest First)

  • 09-10-2012, 03:37 PM
    jdblack
    Quote Originally Posted by artdavila View Post
    If they haven't asked ACCA to officially back it then he cannot advertise it being ACCA approved, but he can base it on the Manual J, just not promote it that way.

    All about the $$$$ with ACCA
    This is the scenario.

    Sent from my ERIS using Tapatalk 2
  • 09-10-2012, 11:58 AM
    Artietech
    Quote Originally Posted by jdblack View Post
    I'm asking the developer about the Manual J edition, but I don't think it will be based on that or else he would promote it as such. We will see.
    If they haven't asked ACCA to officially back it then he cannot advertise it being ACCA approved, but he can base it on the Manual J, just not promote it that way.

    All about the $$$$ with ACCA
  • 09-10-2012, 11:45 AM
    jdblack
    I'm not sure if it's acceptable to local code departments. That would be something you would need to take up with your officials. Around these parts they don't ask. A majority of contractors don't do them. Also most homeowners don't know about them. When I mention it I sometimes get the look like I'm a snake oil salesman.

    I'm asking the developer about the Manual J edition, but I don't think it will be based on that or else he would promote it as such. We will see.
  • 09-10-2012, 11:04 AM
    Artietech
    Is the print out acceptable to local code departments? Is this based on Manual J 8th edition? or 7th?
  • 09-10-2012, 10:53 AM
    jdblack
    Project Rental @ 102 Lawrence Totals
    ==========================================
    Cooling Load : 30,600 Btuh
    Cooling Load tons : 2.5499875373362264
    Latent Cooling Load : 2,611 Btuh
    Sensible Cooling Load : 27,989 Btuh
    Sensible Heat Ratio : 0.91
    Airflow : 1339 cfm
    CFM/Ton : 525.2
    Cooling Temp Diff : 19 °F
    Cooling Volume : 10,935 ft³
    Floor Cooling Area : 1,215 ft²
    Latent Cooling Duct Load : 0 Btuh
    Latent Cooling Infiltration Load : 2,011 Btuh
    Latent Cooling Ventilation Load : 0 Btuh
    Sensible Cooling Duct Load : 0 Btuh
    Sensible Infiltration Cooling Load : 1,818 Btuh
    Sensible Ventilation Cooling Load : 0 Btuh
    Heating Load : 44,627 Btuh
    Heating Load tons : 3.718887744762697
    Heating Temp Diff : 48 °F
    Heating Volume : 10,935 ft³
    Floor Heating Area : 1,215 ft²
    Heating Duct Load : 0 Btuh
    Heating Infiltration Load : 10,869 Btuh
    Heating Ventilation Load : 0 Btuh
    Project Loads
    ==========================================
    Above Grade Wall, North, North wall kitchen heating 1,106 Btuh, cooling 726 Btuh
    (2) Windows, [North], North window kitchen heating 1,411 Btuh, cooling 780 Btuh
    Above Grade Wall, East, East wall heating 1,131 Btuh, cooling 417 Btuh
    (3) Windows, [East], East window heating 2,117 Btuh, cooling 2,745 Btuh
    Above Grade Wall, South, South wall heating 964 Btuh, cooling 355 Btuh
    Window, [South], South window heating 706 Btuh, cooling 525 Btuh
    Wood/Metal Door, South door heating 393 Btuh, cooling 254 Btuh
    Above Grade Wall, West, West wall heating 1,062 Btuh, cooling 250 Btuh
    (4) Windows, [West], West window heating 2,822 Btuh, cooling 3,660 Btuh
    Above Grade Wall, South, South wall Copy heating 1,020 Btuh, cooling 376 Btuh
    (2) Windows, [South], South window Copy heating 1,129 Btuh, cooling 840 Btuh
    Above Grade Wall, East, East wall Copy heating 1,718 Btuh, cooling 634 Btuh
    (3) Windows, [East], East window Copy heating 1,693 Btuh, cooling 2,196 Btuh
    Above Grade Wall, North, North wall dining room heating 449 Btuh, cooling 295 Btuh
    Window, [North], North window dining room heating 706 Btuh, cooling 390 Btuh
    Above Grade Wall, North, North wall bedroom heating 760 Btuh, cooling 499 Btuh
    Window, [North], North window bedroom heating 706 Btuh, cooling 390 Btuh
    Above Grade Wall, East, East wall kitchen heating 293 Btuh, cooling 108 Btuh
    Window, [East], East window kitchen heating 706 Btuh, cooling 915 Btuh
    Wood/Metal Door, East door kitchen heating 393 Btuh, cooling 254 Btuh
    Above Grade Wall, West, West wall kitchen heating 391 Btuh, cooling 144 Btuh
    Window, [West], West window kitchen heating 706 Btuh, cooling 915 Btuh
    Above Grade Wall, North, wall heating 1,080 Btuh, cooling 398 Btuh
    Ceiling, Ceiling heating 1,677 Btuh, cooling 1,922 Btuh
    Ceiling, Ceiling Copy heating 909 Btuh, cooling 1,041 Btuh
    Ceiling, kitchen ceiling heating 237 Btuh, cooling 271 Btuh
    Floor, floor heating 6,550 Btuh, cooling 2,612 Btuh
    Floor, kitchen floor heating 924 Btuh, cooling 368 Btuh
    Infiltration, heating 10,869 Btuh, cooling 3,829 Btuh
    Internal Gain, heating 0 Btuh, cooling 2,490 Btuh
    Project Load Summary
    ==========================================
    Walls : heating 9,975 Btuh, cooling 4,202 Btuh
    Glass : heating 12,701 Btuh, cooling 13,356 Btuh
    Doors : heating 786 Btuh, cooling 508 Btuh
    Ceilings : heating 2,822 Btuh, cooling 3,234 Btuh
    Floors : heating 7,474 Btuh, cooling 2,980 Btuh
    Infiltration : heating 10,869 Btuh, cooling 3,829 Btuh
    Internal Gains : heating 0 Btuh, cooling 2,490 Btuh
    ==========================================
  • 09-10-2012, 10:50 AM
    jdblack
    Quote Originally Posted by Home&Marine View Post
    Looking for more info (too). I hate to drop $40.00 on it if its junk. Printing is Necessary!

    Anyone?

    Thanks JD. Your post showed while I was pecking!


    Looking closer, it looks pretty good and all the ratings are excellent.

    I have a Vizio Tablet that's Android.
    If you want something that looks great printed I would suggest using a template and then populate the data into it manually. The stuff I pasted in lost all of it's formatting through my phone. I'll edit it from this desktop now.
  • 09-10-2012, 09:34 AM
    jdblack
    I did a room load calc for the same job and it came out to 28000 BTU roughly. Its stored on the tablet at home.

    I did email the developer and they are looking at developing cloud storage to store project files.

    Sent from my ERIS using Tapatalk 2
  • 09-10-2012, 09:31 AM
    jdblack
    ============================== ============ Cooling Load : 30,600 Btuh Cooling Load tons : 2.5499875373362264 Latent Cooling Load : 2,611 Btuh Sensible Cooling Load : 27,989 Btuh Sensible Heat Ratio : 0.91 Airflow : 1339 cfm CFM/Ton : 525.2

    Cooling Temp Diff : 19 °F Cooling Volume : 10,935 ft³ Floor Cooling Area : 1,215 ft² Latent Cooling Duct Load : 0 Btuh Latent Cooling Infiltration Load : 2,011 Btuh Latent Cooling Ventilation Load : 0 Btuh Sensible Cooling Duct Load : 0 Btuh Sensible Infiltration Cooling Load : 1,818 Btuh Sensible Ventilation Cooling Load : 0 Btuh Heating Load : 44,627 Btuh Heating Load tons : 3.718887744762697 Heating Temp Diff : 48 °F Heating Volume : 10,935 ft³ Floor Heating Area : 1,215 ft² Heating Duct Load : 0 Btuh Heating Infiltration Load : 10,869 Btuh Heating Ventilation Load : 0 Btuh

    Project Loads ============================== ============ Above Grade Wall, North, North wall kitchen heating 1,106 Btuh, cooling 726 Btuh (2) Windows, [North], North window kitchen heating 1,411 Btuh, cooling 780 Btuh Above Grade Wall, East, East wall heating 1,131 Btuh, cooling 417 Btuh (3) Windows, [East], East window heating 2,117 Btuh, cooling 2,745 Btuh Above Grade Wall, South, South wall heating 964 Btuh, cooling 355 Btuh Window, [South], South window heating 706 Btuh, cooling 525 Btuh Wood/Metal Door, South door heating 393 Btuh, cooling 254 Btuh Above Grade Wall, West, West wall heating 1,062 Btuh, cooling 250 Btuh (4) Windows, [West], West window heating 2,822 Btuh, cooling 3,660 Btuh Above Grade Wall, South, South wall Copy heating 1,020 Btuh, cooling 376 Btuh (2) Windows, [South], South window Copy heating 1,129 Btuh, cooling 840 Btuh Above Grade Wall, East, East wall Copy heating 1,718 Btuh, cooling 634 Btuh (3) Windows, [East], East window Copy heating 1,693 Btuh, cooling 2,196 Btuh Above Grade Wall, North, North wall dining room heating 449 Btuh, cooling 295 Btuh Window, [North], North window dining room heating 706 Btuh, cooling 390 Btuh Above Grade Wall, North, North wall bedroom heating 760 Btuh, cooling 499 Btuh Window, [North], North window bedroom heating 706 Btuh, cooling 390 Btuh Above Grade Wall, East, East wall kitchen heating 293 Btuh, cooling 108 Btuh Window, [East], East window kitchen heating 706 Btuh, cooling 915 Btuh Wood/Metal Door, East door kitchen heating 393 Btuh, cooling 254 Btuh Above Grade Wall, West, West wall kitchen heating 391 Btuh, cooling 144 Btuh Window, [West], West window kitchen heating 706 Btuh, cooling 915 Btuh Above Grade Wall, North, wall heating 1,080 Btuh, cooling 398 Btuh Ceiling, Ceiling heating 1,677 Btuh, cooling 1,922 Btuh Ceiling, Ceiling Copy heating 909 Btuh, cooling 1,041 Btuh Ceiling, kitchen ceiling heating 237 Btuh, cooling 271 Btuh Floor, floor heating 6,550 Btuh, cooling 2,612 Btuh Floor, kitchen floor heating 924 Btuh, cooling 368 Btuh Infiltration, heating 10,869 Btuh, cooling 3,829 Btuh Internal Gain, heating 0 Btuh, cooling 2,490 Btuh

    Project Load Summary ============================== ============ Walls : heating 9,975 Btuh, cooling 4,202 Btuh Glass : heating 12,701 Btuh, cooling 13,356 Btuh Doors : heating 786 Btuh, cooling 508 Btuh Ceilings : heating 2,822 Btuh, cooling 3,234 Btuh Floors : heating 7,474 Btuh, cooling 2,980 Btuh Infiltration : heating 10,869 Btuh, cooling 3,829 Btuh Internal Gains : heating 0 Btuh, cooling 2,490 Btuh ==============================
    Attachment 307081Attachment 307091Attachment 307101

    Sent from my ERIS using Tapatalk 2
  • 09-10-2012, 09:16 AM
    Home&Marine
    Looking for more info (too). I hate to drop $40.00 on it if its junk. Printing is Necessary!

    Anyone?

    Thanks JD. Your post showed while I was pecking!


    Looking closer, it looks pretty good and all the ratings are excellent.

    I have a Vizio Tablet that's Android.
  • 09-10-2012, 09:15 AM
    jdblack
    Quote Originally Posted by mofotech View Post
    I haven't gotten the program yet. But let me ask you something. After you do a load calculation, can it be printed out? How detail of information does this give? Will it give also the cfm required for each room or area?

    thanks
    You can email the report and then it can be printed out. It has graphs also. If you do a room calc it does give the cfm per room. I have a block calc done. I will try and upload here.

    Sent from my ERIS using Tapatalk 2
  • 09-10-2012, 08:41 AM
    mofotech
    Quote Originally Posted by jdblack View Post
    Yes its the hvac load -calc by power trade. It was 39.99

    Sent from my ERIS using Tapatalk 2
    I haven't gotten the program yet. But let me ask you something. After you do a load calculation, can it be printed out? How detail of information does this give? Will it give also the cfm required for each room or area?

    thanks
  • 09-07-2012, 06:26 AM
    jdblack
    Yes its the hvac load -calc by power trade. It was 39.99

    Sent from my ERIS using Tapatalk 2
  • 09-07-2012, 05:45 AM
    mofotech
    That's a good idea. I am going to try it out. I was about to go get a tablet to run that app. But let me try bluestacks first.
  • 09-06-2012, 08:57 PM
    Joehvac25
    How much is it?
  • 09-06-2012, 08:56 PM
    SBres22
    If you have a laptop you can download "bluestacks" it is a program that lets you download android apps and use them on your computer... not sure if this helps anybody, but it is available....
  • 09-06-2012, 08:34 PM
    mofotech
    Quote Originally Posted by shaworth1 View Post
    is this app hvac buddy load calc. I was searching for it.
    I gotta try this out. Is "HVAC Load-Calc app by Powertrade" the exact name?
  • 09-06-2012, 07:58 PM
    shaworth1
    is this app hvac buddy load calc. I was searching for it.
  • 09-06-2012, 02:47 PM
    ADillon
    I used it and it came out to be close to the same load calc I did in wrightsoft. So it's not bad. It's just a pain in the a$$ to use on a little phone. I guess it could be cool on a tablet but I would just get the wrightsoft mobile consultant.
  • 09-06-2012, 02:45 PM
    jdblack

    HVAC Load-Calc app by Powertrade

    I just downloaded this app from the Android Marketplace. I've done a load calculation already and it took a little getting used to on adding loads. Commercial Calc for the desktop was much easier, but I do like the addition of partition walls on this app.

    Do any of you that have used it have any tips?