  • 05-15-2012, 07:50 PM
    ruuufuhbock
    I'm new to markets but in my short experience I would have to agree that this case probably needs to stripped down and cleaned, and possibly even tape off some of the lower louvers to forc
    e.the air north. It's very rinky.dink.but it works.
  • 05-04-2012, 10:05 PM
    Fridge Repairer
    Check your superheat too make sure your feeding the evaporator coil properly.
  • 05-02-2012, 01:53 AM
    therock
    Quote Originally Posted by jpsmith1cm View Post
    This is almost NEVER a good idea.

    There is a proper position for a fan blade within the plenum, and installing a larger (or smaller) sized motor can and WILL change that postition, altering airflow for the worst!

    Replace the motor with the proper sized one.
    Yes JP and it would be a very bad idea for me to disagree with another fellow
    CM that has all those rounds on his profile page
    By all means always take my 45 years of information with a grain of salt as I
    don't mean to criticize others and there are how many grains in those rounds?

    I am so thankful for this forum as it often shows many of us that some of the
    tactics we have used in the past that worked actually turned out to be
    incorrect

    Always go by mfg specs first then if that doesn't work go right to the source
    and ask the mfg application engineer
    They will help you as they are proud of their product and their reputation
  • 05-01-2012, 11:08 PM
    Phase Loss
    Quote Originally Posted by jpsmith1cm View Post
    This is almost NEVER a good idea.

    There is a proper position for a fan blade within the plenum, and installing a larger (or smaller) sized motor can and WILL change that postition, altering airflow for the worst!

    Replace the motor with the proper sized one.
    X3

    Look here page 2 & 3. Pay attention to wattage and motor dimension.

    http://www.aosmithmotors.com/uploade...Web.pdf?n=5332

    Going higher in wattage will use a thicker motor and place the blade above the plenum. Going lower in wattage will use a thinner motor and place the blade below the plenum.
  • 05-01-2012, 10:57 PM
    jpsmith1cm
    Quote Originally Posted by crackertech

    Really!!! I guess you don't work on a contract Market.
    Some of the new Barker cases, I'm doing them all at once.

    The whole case has to be pulled, you've got to pull the plenum out just to get at the fans.

    Yep, a couple of cheap 9watts make good sense in that case
  • 05-01-2012, 10:03 PM
    crackertech
    Quote Originally Posted by jpsmith1cm View Post
    This is almost NEVER a good idea.

    There is a proper position for a fan blade within the plenum, and installing a larger (or smaller) sized motor can and WILL change that postition, altering airflow for the worst!

    Replace the motor with the proper sized one.

    X2
  • 05-01-2012, 10:02 PM
    crackertech
    Quote Originally Posted by therock View Post
    There's not a grocer born that doesn't overload a produce case!!!!
    You can't stop them and health (temperature) inspectors know that
    They stack it up for impulse buying almost 2 feet out of the air flow
    then all the cold air falls on the floor and none makes it to the top shelf
    My IR thermo shows 59 to 60 at times on produce
    Give them a picture of max load lines and they smile at you and then
    as soon as you leave they overload the case so they won't get fired
    Some would rather stock a non refrig product on the top shelf so they
    can continue overloading the lower shelves and dump horsepower on the
    floor but it makes a good cold display for beer on sale on the floor LOL

    If one fan motor has failed they all have to be replaced as they have
    the same hours history on the bearings and you can't see lowered rpms
    and don't allow any bent blades which do cause lower rpms = lower cfms

    If you unloaded and power washed all possible air flow restriction areas
    replace all fan motors, check for correct blades and balance the blades
    If the motors are replaced I increase wattage size to at least 9w if smaller
    than (4 or 6watt) that, check superheat and coil temp defrost clock and
    mfg settings, check the R-22 compressor for blow by caused by case
    overloading for 5 years then remark case load limit lines and call it a day

    Really!!! I guess you don't work on a contract Market.
  • 05-01-2012, 09:47 PM
    jaybee
    Quote Originally Posted by icemeister View Post
    Here's the case specs for the RIN3:


    If the case in question is a different model, go to their search page here and enter the case model you have.

    The RIN3 calls for a 20ºF evap temp and 27ºF discharge air with 4 defrosts/day, time terminated at 20 minutes.

    Verify your store conditions are at or below 75ºFdb/55%RH.

    Also, the shelf sizing and load limits are critical on these cases.
    THANKS
  • 05-01-2012, 09:26 PM
    jpsmith1cm
    Quote Originally Posted by therock View Post
    If the motors are replaced I increase wattage size to at least 9w if smaller
    than (4 or 6watt) that,
    This is almost NEVER a good idea.

    There is a proper position for a fan blade within the plenum, and installing a larger (or smaller) sized motor can and WILL change that postition, altering airflow for the worst!

    Replace the motor with the proper sized one.
  • 05-01-2012, 04:48 PM
    beb
    Quote Originally Posted by jpsmith1cm View Post
    Your case is too friggen warm


    Set it down to 32 supply air or so.


    While you're at it, make CERTAIN that the product stocked is cold enough (below 35F)

    If it isn't you're BOTH wasting your time.
    X2 Ive run into this often at same store after health dept visit.
  • 05-01-2012, 10:32 AM
    therock
    There's not a grocer born that doesn't overload a produce case!!!!
    You can't stop them and health (temperature) inspectors know that
    They stack it up for impulse buying almost 2 feet out of the air flow
    then all the cold air falls on the floor and none makes it to the top shelf
    My IR thermo shows 59 to 60 at times on produce
    Give them a picture of max load lines and they smile at you and then
    as soon as you leave they overload the case so they won't get fired
    Some would rather stock a non refrig product on the top shelf so they
    can continue overloading the lower shelves and dump horsepower on the
    floor but it makes a good cold display for beer on sale on the floor LOL

    If one fan motor has failed they all have to be replaced as they have
    the same hours history on the bearings and you can't see lowered rpms
    and don't allow any bent blades which do cause lower rpms = lower cfms

    If you unloaded and power washed all possible air flow restriction areas
    replace all fan motors, check for correct blades and balance the blades
    If the motors are replaced I increase wattage size to at least 9w if smaller
    than (4 or 6watt) that, check superheat and coil temp defrost clock and
    mfg settings, check the R-22 compressor for blow by caused by case
    overloading for 5 years then remark case load limit lines and call it a day
  • 01-31-2012, 09:55 PM
    mspanky
    Quote Originally Posted by thefreezerguy View Post
    If you believe this case to be a Hussmann "RI" island case, the supply air spec is 26 - 27. In addition, there are several supply air metering plates inside the case that get plugged solid and need cleaned.
    Also, the defrost spec is 6 times (every 4 hours) / day for 20 minutes. I set the duration for 25 minutes given the region I am in. It is not "too much" defrost if the case is set down to the proper supply air temp and it builds the expected frost load on the coils.
    x2. These cases plug up with dirt faster than any other case in a supermarket. There is a horizontal baffle mounted in the 'tower' the same height as the pans and I would bet money it's plugged solid. You will need to remove all the bottom product and wash it out with a hose. A velometer is a must-have tool for working on cases.
  • 01-31-2012, 01:39 AM
    thefreezerguy
    If you believe this case to be a Hussmann "RI" island case, the supply air spec is 26 - 27. In addition, there are several supply air metering plates inside the case that get plugged solid and need cleaned.
    Also, the defrost spec is 6 times (every 4 hours) / day for 20 minutes. I set the duration for 25 minutes given the region I am in. It is not "too much" defrost if the case is set down to the proper supply air temp and it builds the expected frost load on the coils.
  • 01-30-2012, 01:29 PM
    MeÐiC
    We recently removed one of these cases because it would not hold temp on the ends.

    I agree with jp. Reduce the defrosts to 4x a day. 30min duration is plenty.

    As icemeister indicated, shelf sizing/placement and load limits are very critical in these island cases.
  • 01-18-2012, 08:34 AM
    icemeister
    Here's the case specs for the RIN3:


    If the case in question is a different model, go to their search page here and enter the case model you have.

    The RIN3 calls for a 20ºF evap temp and 27ºF discharge air with 4 defrosts/day, time terminated at 20 minutes.

    Verify your store conditions are at or below 75ºFdb/55%RH.

    Also, the shelf sizing and load limits are critical on these cases.
  • 01-18-2012, 12:18 AM
    Blackmira
    Call hussmann and get case specs
  • 01-17-2012, 09:37 PM
    Iceneck
    Did you check the honeycombs themselves? They can get a nice blanket of crap on top of them that will impede airflow quite a bit. I'd think the week holes in the back of the case may be able to keep the lower shelves at temp? Maybe?
  • 01-17-2012, 09:29 PM
    jpsmith1cm
    First off, I'm going to say too much defrost.

    A case like that will do fine with 4 a day, although you might need to stretch them out to 35 minutes or so.


    Those can be a royal pain to get to hold temp.

    You MUST cover all of the bases. Get your superheat down, your suction pressure is a bit high for a case like that. I'd like to see an evap down closer to 15-18 rather than 21.
  • 01-17-2012, 09:21 PM
    mpr73
    island style with 3 total levels. defrosts 6 times a day for 30 mins. I arrived on site 2 hours after the last defrost. and the clock was set fro the proper time.

    defrosts at 4, 8, 12 a/p

    the case is a hussman and very closely resembles the RI3N model

    I did check the supply temp getting down to 29-30 and middle and low shelf were at 35-36. Product came from the WIC which was also at 35
  • 01-17-2012, 09:17 PM
    jpsmith1cm
    Quote Originally Posted by mpr73 View Post
    i have case set down to 28 or so on the stat to hold a mid 30 reading and i re stocked the case with product from the walk in at is at temp
    Not trying to be a jerk, but did you VERIFY that?

    If not, then it wasn't at temp.