    ashif
    sir i have replace and put new one but facing same issue , initially i got this alarm after 5 to 6 hour runnig , but nowadays when i start the compressor first got 10 min timer ,and when timer finish then motor current alarm active ratherthan starting the compressor.
  • 09-29-2011, 11:52 PM
    jayguy
    Quote Originally Posted by Taicool View Post
    ...2. measure the motor vibration, the result is as attached,...
    was the vibration data taken with the motor connected to the compressor? if so, at what loading/RLA?

    the best open rotor test using vibration equipment is by measuring the dB of the current...see attached.

    the main peak in the middle is the line frequency (60 Hz) and the large peak to the left is the rotor turning speed (57.469 Hz). the difference is about 32 dB. anything less than 45 dB indicates the beginning of a problem...<30 dB means that the motor is going to try to walk out of the door!
  • 09-29-2011, 09:57 AM
    Taicool
    Sure, just wait for a couple of days,
    Have to say thanks for your concern and the good suggestions.
  • 09-29-2011, 09:46 AM
    Nuclrchiller
    Quote Originally Posted by jayguy View Post
    me too...then i can get my tools back!
    I saw that post where Moparmyway mentioned he borrowed your tools. I thought to myself "aha, a clue as to who, and where, the mysterious Jayguy is". And then, dang it Jay, you went and changed your secret identity!
  • 09-29-2011, 09:41 AM
    Nuclrchiller
    Quote Originally Posted by Taicool View Post
    Next step for me to do is to ask a motor shop to help on confirm the rotor problem as they are professional and they have some precision instruments for a good test.
    That sounds like a good idea, Taicool. By the way, the first open rotor test I was involved in, I went along with an older, more experienced technician. I was basically a trainee. I hate to think how lost I would have been on my own for the first one. Don't forget to keep us updated. Billy.
  • 09-29-2011, 09:27 AM
    Taicool
    Next step for me to do is to ask a motor shop to help on confirm the rotor problem as they are professional and they have some precision instruments for a good test.
  • 09-29-2011, 09:15 AM
    Taicool
    Good evening, Gentlemen;
    Yesterday I kept fighting with this onerous chiller for a whole day,below are those moves I have carried out,
    1. I tested the rotor with variac again, the variation is about 0.35 amps(when the first time I did it two days ago, I think I have misread the reading, for one division on the analog clamp-on ammeter, it is only 0.5amps, I apoligize for the mistake!),
    2. measure the motor vibration, the result is as attached,
    3. run the motor with coupling disconnected to the compressor, the amp reading on the analog ammeter is pretty stable, the needle swing slightly, I have to keep staring at it carefully to find the motion, while on chiller's control panel, the FLA% jump about between 24%-25%,
    So far I am still inclined to believe the problem is caused by an open rotor, just not 100%.
  • 09-28-2011, 07:06 PM
    jayguy
    Quote Originally Posted by Nuclrchiller View Post
    ...I too have been watching Moparmyway's thread. Looking forward to seeing how it ends.
    me too...then i can get my tools back!
  • 09-28-2011, 08:44 AM
    Nuclrchiller
    Quote Originally Posted by RichardL View Post
    Thankee' Billy..I been waiyng on Taicool to post his findings.
    Now...If we can just get Moparmyway to let us know what the hell was wrong with his "Speed-Changing" motor, the all will be well in the universe.
    This has been an interesting, and informative, thread. I too have been watching Moparmyway's thread. Looking forward to seeing how it ends.
  • 09-27-2011, 11:33 PM
    jayguy
    i just started to read this thread since it keeps popping up!

    side bands occur due to vibration amplitude modulation (changes in vibration amplitude or 'quantity')

    if the side bands are spaced at pole pass frequency, then open rotor bars are suspected (especially if you can see them on the vibration spectrum!)

    while a 'failed' variac reading indicates an open rotor bar, you may still have a rotor bar issue. a rotor bar with a high resistance joint might show that it is ok, but after it heats up, you can get a rotor bar issue.

    vibration analysis will show it while the motor is under load. a rotor bar vibration will show up as a greater vibration at greater loads and less vibration at lower loads. the motor speed will also respond accordingly. higher speeds at lower loads and lower speeds at higher loads.
  • 09-27-2011, 01:04 PM
    york56
    Glad to here that the world is somewhat back in flux.
  • 09-27-2011, 12:27 PM
    RichardL
    Thankee' Billy..I been waiyng on Taicool to post his findings.
    Now...If we can just get Moparmyway to let us know what the hell was wrong with his "Speed-Changing" motor, the all will be well in the universe.
  • 09-27-2011, 12:11 PM
    Nuclrchiller
    Richard, glad you were here to catch that.
  • 09-27-2011, 12:07 PM
    RichardL
    That 1 amp. deviation is far more than 5% and you my friend have an open rotor bar....Period
    To take a look at which one is actually the culprit, have your trusty motor shop put a "Growler" test on the rotor, then with a hack-saw blade placed over each segment of iron(one at a time) and watch the hach-saw blade do a dance when you are next to the rotor bar that has opened up.
    I do not know how much fluctuation you were expecting in the applied current, but a good rotor will have almost no detectable deviation at all,,,
    Lastly....What kind of "Welding Machine" are you going to use that will put out more than the 130 volt A/C that your newly purchased Variac puts out??
  • 09-27-2011, 12:06 PM
    Nuclrchiller
    Taicool, I have never heard of using a portable welding machine for that purpose. I would not do that. Even if I saw someone else do that with no apparent problem, I would still not do that. It has been several years since I've performed an open rotor test, and I don't recall what numbers to look for. If you were using an approved, published procedure (I hope you were), then it should have the numbers to look for. And that should indicate if the rotor is acceptible or not. Please don't follow the wrong path in your troubleshooting simply because it is more interesting.
  • 09-27-2011, 11:45 AM
    Taicool
    I also noticed the refrigerant drum is marked R-22, I have checked with my colleague, he said the drums had been cleaned and evacuated, from the current operation record, I don't think the chiller has any mix of R-22.
    Yesterday I did the rotor bar test with a variac, 110VAC input, 0-130VAC output, 10A,
    I adjust the output amps to 9.7(read by a analog clamp ammeter), then I rotate the motor shaft slowly, the amp reading swing from 9.1 to 10.1, since the variation is not so significant, I am not sure the rotor bar can be determined to be defective.
    Tomorrow I am going to test it again with a portable electric welding machine, with a higher input current, maybe it will be clearer to identify the problem
  • 09-25-2011, 07:45 AM
    cri3541
    Just a thought I had a 600 Ton Carrier with this same issue, fighting it for three weeks. Come to find out machine had a small mixture of R-22 in it, mixed with R134A. Traced records found a reclaim drum that had not been cleaned on a earlier repair. Caused machine to surge and drop out on Low Line Voltage, this safety just happened to be the one that picked the problem up.
  • 09-24-2011, 06:12 PM
    chillerguy81
    Quote Originally Posted by york56 View Post
    chillerguy81 don't always put your trust in a optiview sales order screen because if that micro has been changed and the person who did the replacement didn't take all the info. down before it was replaced there is a good possibility that the info. is garbage anybody could put anything in that screen best is to get it from the source (ie) manufacture spec. just a little tid bit of info. for you that would be for any machine with a optiview.
    Good point and thanks for the info. This is a good thread, I must have missed the pic of the panel I guess!
  • 09-24-2011, 06:00 PM
    york56
    Quote Originally Posted by chillerguy81 View Post
    Does this chiller have an Optiview display? If so you can get the design info from the sales order screen.
    chillerguy81 don't always put your trust in a optiview sales order screen because if that micro has been changed and the person who did the replacement didn't take all the info. down before it was replaced there is a good possibility that the info. is garbage anybody could put anything in that screen best is to get it from the source (ie) manufacture spec. just a little tid bit of info. for you that would be for any machine with a optiview.
  • 09-24-2011, 01:31 AM
    Taicool
    No, the chiller is YK style C, and is installed at Mitsukoshi department store in southern Taiwan.
    When I just joined York twenty years ago, I had dealed with some HT chillers with R11, but I believe all the HT chillers are obsoleted now, the last one I worked on was about ten years ago.