  • 03-02-2014, 05:19 PM
    captaincompressor
    popping could be liquid refrigerant flooding back hitting the hot oil in the compressor crank case?
  • 03-01-2014, 12:00 PM
    nchvac
    Quote Originally Posted by hewitt View Post
    With 134a-10 to-20 would be operating in a vaccum
    So? They can handle it.
  • 03-01-2014, 09:24 AM
    CFESAmasterEGSR
    Quote Originally Posted by hewitt View Post
    Check the temperature at wal-mart on box of the thermometer when u by your ice cream. I set evap.at o on gauges for packeged ice which holds box temp of 15 to 20
    Ice? Or ice cream?

    15 deg is about the temp soft serve ice cream (around 45% overrun) is dispensed at. Soft serve is extra soft at 20 deg. At zero degrees it is hard as a rock.

    Commercially packaged ice cream (around 100% overrun) is nearly melted to all liquid at 20 degrees. At zero degrees it is at it's properly frozen thickness, not rock hard.
  • 03-01-2014, 02:01 AM
    hewitt
    Check the temperature at wal-mart on box of the thermometer when u by your ice cream. I set evap.at o on gauges for packeged ice which holds box temp of 15 to 20
  • 02-28-2014, 09:36 PM
    CFESAmasterEGSR
    Quote Originally Posted by jpsmith1cm View Post
    Still gotta make temp...

    I would return a freezer that wouldn't hold but 20 degrees.

    Yes

    How cold does boxed ice cream have to be to be froze hard? 0 or below in my experience.

    I did residential appliances for a few years, seems like a unit that settled in running much over 5 psi on the low side was usually a bad sign. They would cycle down into a vacuum at end of on cycle. That was normal I think.

    Weird little systems, very starved evaps. And factory suggested charging procedures that would scare most of you guys. Lol
  • 02-28-2014, 09:21 PM
    jpsmith1cm
    Quote Originally Posted by hewitt View Post
    With 134a-10 to-20 would be operating in a vaccum

    Still gotta make temp...

    I would return a freezer that wouldn't hold but 20 degrees.
  • 02-28-2014, 07:15 PM
    hewitt
    With 134a-10 to-20 would be operating in a vaccum
  • 02-28-2014, 06:41 PM
    nchvac
    Quote Originally Posted by hewitt View Post
    Set the evaporator temp at 0 therefore your box temp will be at 20 degrees if there is no label to distinguish amount of charge.
    Why would he want the box temp at 20? This is a side by side residential refrigerator, so the evap coil is in the freezer section, which he will want that side to be at around 0, so the evap coil needs to be around -10 to -15
  • 02-27-2014, 09:32 PM
    hewitt
    Set the evaporator temp at 0 therefore your box temp will be at 20 degrees if there is no label to distinguish amount of charge.
  • 02-26-2014, 10:00 PM
    Dad
    No Nitro integration. I buttoned it up and am sitting back in the EZ Chair with a can of red paint.

    The box continues to chug right along holding temp. It still makes weird noises but so do I... nothing to lose right?

    During the winter the chattering is gone replaced with compressor crank up creaks & shutdown knocks. We'll see when the weather warms up again.

    (The red paint is for the target circle and a fun day at the pistol range)
  • 02-26-2014, 08:33 PM
    Apprenticanic
    Quote Originally Posted by Dad View Post
    This is a 10 yr old box.. never an issue with it. As said, it is in the garage and on the way out the door to my truck so it just holds truck drinks and some over flow during holidays. Well, OK... maybe a few beers too..

    The CAPT-032S holds about 4 oz of liquid. The exit end is pointed straight down so there is a liquid seal at the cap tube. With the spun drier the data tag said 5.25 oz 134. When the new compressor stopped working (heat) I knew that the charge was wrong or the spun drier was plugged or maybe the beginning of the cap tube. Pressures were -10 and 80 high.

    I pulled the spun off and clipped the first inch of the cap tube entrance end. I also blew nitrogen through the system and put a paper towel at the cap tube open end... I did get a little oil but no gunk. Remember, I also did an acid test that was negative.

    Installed the CAPT and pulled a vacuum. My micron meter stops at 400 microns, it is just old like me. It sat over night until I could get back to it the next day... still 400 microns.

    Set everything up and weighed in 5.25 after filling the hose first. Started the system and it headed south on the suction side again. I came back to the garage a few hours later and it was still running. Once again I was down to -10 suction. Knowing the CAPT takes extra liquid I added another 3.75 oz. That's when I got 9 pounds. The compressor was cooling back but no frost so I let it run.

    After I started this thread I took another look to pull a cow fart of gas out. I had 0 and 110 with slight frost. I pulled a 4' hose amount of 134 out of the high side. This was mostly liquid and about an oz. After I fired it up and let it run for a while, (still close temp), and had -8 and 100. There was no frost on the suction line seen but I did hear the the return of Orville popping corn and not as loud or frequent.

    After it running since my last post the box doesn't seem to run as long and the pop corn sound is gone. The box is holding temp fine but I really haven't spent a lot of time in the garage since.

    I'll keep checking it and listening but unless Orville comes back from the grave I'll probably leave well enough alone.

    I'll let you guys know more later.
    How has it been running since this dated post, Dad? Still chugging along? No more Orville?? Did you ever try putting in nitro as per the MFG bulletin? Just curious if you or anyone ever tried and successfully done this to rid an issue. First time hearing/reading about it. Seems very counter-intuitive.
  • 11-30-2012, 08:08 PM
    MicahWes
    I had an old fridge with a knocking noise where the cap tube entered the evap. I put a giant wad of permagum around the connection and the noise was gone.
  • 11-29-2012, 06:53 PM
    Dad
    This is a 10 yr old box.. never an issue with it. As said, it is in the garage and on the way out the door to my truck so it just holds truck drinks and some over flow during holidays. Well, OK... maybe a few beers too..

    The CAPT-032S holds about 4 oz of liquid. The exit end is pointed straight down so there is a liquid seal at the cap tube. With the spun drier the data tag said 5.25 oz 134. When the new compressor stopped working (heat) I knew that the charge was wrong or the spun drier was plugged or maybe the beginning of the cap tube. Pressures were -10 and 80 high.

    I pulled the spun off and clipped the first inch of the cap tube entrance end. I also blew nitrogen through the system and put a paper towel at the cap tube open end... I did get a little oil but no gunk. Remember, I also did an acid test that was negative.

    Installed the CAPT and pulled a vacuum. My micron meter stops at 400 microns, it is just old like me. It sat over night until I could get back to it the next day... still 400 microns.

    Set everything up and weighed in 5.25 after filling the hose first. Started the system and it headed south on the suction side again. I came back to the garage a few hours later and it was still running. Once again I was down to -10 suction. Knowing the CAPT takes extra liquid I added another 3.75 oz. That's when I got 9 pounds. The compressor was cooling back but no frost so I let it run.

    After I started this thread I took another look to pull a cow fart of gas out. I had 0 and 110 with slight frost. I pulled a 4' hose amount of 134 out of the high side. This was mostly liquid and about an oz. After I fired it up and let it run for a while, (still close temp), and had -8 and 100. There was no frost on the suction line seen but I did hear the the return of Orville popping corn and not as loud or frequent.

    After it running since my last post the box doesn't seem to run as long and the pop corn sound is gone. The box is holding temp fine but I really haven't spent a lot of time in the garage since.

    I'll keep checking it and listening but unless Orville comes back from the grave I'll probably leave well enough alone.

    I'll let you guys know more later.
  • 11-29-2012, 05:35 PM
    pauls heating &
    hack fix by mfg of a pos product
  • 11-29-2012, 01:07 PM
    nchvac
    -27 evap temp maybe needed on a walkin, but we must remember that resi units are holding units. If memory serves, the box temp is around 10 degrees over the evap temp on resis. I think they do this to decrease dehumidification so as to not dry out the product in the refrigeration side.

    I did just read the service manual, and if it wasn't written by a manufacturer this post would be 5 extra pages wrong with the word hack and hackery on each posting. None the less, when they are saying they are building back pressure, they are doing so in the condensor, as John Tomczyk points out a lot is the fact that non condensables get stuck in the top of the condensor and take up space. If it were not the case then the nitrogen would defeat the purpose which evidently is to get liquid to the cap tube sooner. I would submit for thought that if the compressor valves are tight and DAD installed a line dryer (as he did) that the line dryer should be full of liquid enough to be getting the cap tube full pretty quick. And the whole point of the Nitrogen was to keep from "having to add refrigerant", which we have already said the unit is overcharged with an extra 4 ounces and still doing the deed.
    But to further show that this isn't DAD's problem, he said in his first post that this happens at any time with no rhym or reason, and "Popcorn maker sound for 5 or 6 minutes fairly loud then it goes away as quickly as it started". The service bulletin said it happens only at compressor startup and goes away in around 60 to 90 seconds. So it may be the same symptom, but not the same cause.

    I really am taken back just a little by that service bulletin. Never heard of anything close to doing things that way, and if nothing else, if a tech misdiagnosis and adds the nitrogen, now he has two problems. And no matter if they approve or not the unit is not going to run to original specs. The head pressure and every number condenser related is going to be off during operation.
  • 11-29-2012, 10:50 AM
    pauls heating &
    dad..we had the same pos fridge. got it before the tsb came out.. about a week after we bought it (of course at 3 am ) we discovered the popcorn machine we had just bought.. and of course our dogs really liked it. of course the salesman at lowes never heard of the noise, so i do a warranty service call - the tech says its a common/ normal for the frigidaires...so no fix at that time..
    then it died (compressor ) a lil less than 2 months after 12 mo warranty expired - electrolux offered a free compressor if i paid service call/install price..tried crossing comp # into something i could buy -no luck there..so i scrapped the damn thing..sadly we let them cart off our old 20 yr old fridge which worked fine..
  • 11-29-2012, 07:38 AM
    itsiceman
    Quote Originally Posted by SBKold View Post
    Pretty high!
  • 11-28-2012, 10:49 PM
    Dad
    OK... i need a towel for the keyboard
  • 11-28-2012, 10:28 PM
    SBKold
    Pretty high!
  • 11-28-2012, 10:24 PM
    VTP99
    And we always thought it was wrong to have nitro in the operating system. What will they come up with next ? How about helium ? Wonder what that might get you.