  • 03-17-2012, 09:55 AM
    icemeister
    Quote Originally Posted by HighTekk^ View Post
    I have seen many recommendations to use that refrigerant and luckily I obtained a bottle of it. What would you recommend for a powerhead on the expansion valve I have replaced. I have a head good for 134a, 12 and 401a. Then I have a head for 404a, 502, 402a and 507. I wanted to be sure I had to the correct one so I got two while at the part supplier.
    Use the one for R134A/R12/R401A...if it's a low temperature charge. The Sporlan charge designation would be FZ...or FZP if it's a pressure limiting MOP type charge.
  • 03-17-2012, 08:15 AM
    HighTekk^
    Quote Originally Posted by icemeister View Post
    That's a Bill Of Material number, but my Tecumseh info says it's an AHA2445AXD, which is an R12 low temp compressor. Whoever "converted" this to R404A didn't know what he was doing.

    If you are to use this compressor, your one and only hope is R401B (MP66) and that the compressor itself is fully functional...ie, no bad valves and it's not worn out.

    Otherwise, go with a new R404A condensing unit of equal capacity, change the TEV and charge her up with orange juice.
    I have seen many recommendations to use that refrigerant and luckily I obtained a bottle of it. What would you recommend for a powerhead on the expansion valve I have replaced. I have a head good for 134a, 12 and 401a. Then I have a head for 404a, 502, 402a and 507. I wanted to be sure I had to the correct one so I got two while at the part supplier.
  • 03-16-2012, 06:25 PM
    icemeister
    Quote Originally Posted by HighTekk^ View Post
    Its a techum. M#AH410EF-509-A4
    That's a Bill Of Material number, but my Tecumseh info says it's an AHA2445AXD, which is an R12 low temp compressor. Whoever "converted" this to R404A didn't know what he was doing.

    If you are to use this compressor, your one and only hope is R401B (MP66) and that the compressor itself is fully functional...ie, no bad valves and it's not worn out.

    Otherwise, go with a new R404A condensing unit of equal capacity, change the TEV and charge her up with orange juice.
  • 03-16-2012, 06:11 PM
    HighTekk^
    Its a techum. M#AH410EF-509-A4
  • 03-16-2012, 06:03 PM
    icemeister
    Quote Originally Posted by HighTekk^ View Post
    Not too sure about that but I do know this about the box...
    If the compressor is designed for R12 LT, I'm quite sure of that.

    Quote Originally Posted by HighTekk^ View Post
    Was originally an R-12 Low temp box that was converted to 404a(which I recently found out after working on another piece of equipment that described changing everything onsite to 404a).
    You somehow failed to mention that little piece of information earlier. Was the compressor changed to an R404A LT or is it still the original R12 compressor?

    Quote Originally Posted by HighTekk^ View Post
    The old expansion valve had failed shut so it was replaced with a sporlan EFSE-1/2-ZP. As you know this is good for low temp R-404A, R-502, R-402A or R-507.

    In addition to replacing the valve I also had ordered an additional powerhead for the TEV that would work for R-134A, R-12 and R-401A. As the 401a was the cheapest refrigerant I could buy I opted to go with it but it never cooled the box below 10 degrees.

    So now I am considering using the HP80, MP66 or 404A, which I have a bottle of each in my possession. I just don't want to wast another day reclaiming, changing dryer, pressure-testing, evacuation and so on.

    I would like to keep the box at -10 degrees if possible when its fully loaded on a warm day.

    What do you think? I have read many threads on here but there is a lot of conflicting posts.

    This box has thrown me through a loop, just when you try to experiment and cut a itty bitty corner it turns around and bites you in the a**. So I was wondering if anyone has any particular experience in this overall situation.
    The first thing you must realize is the refrigerant you must use is determined by what compressor you have. You can't dump R404A into a system with an R12 compressor and expect it to work.

    What is the model number of the compressor you're dealing with? That would be a major help for us who want to help you with this.
  • 03-16-2012, 05:14 PM
    sgagne199
    I myself would convert back to 404a i like that refrigerant
  • 03-16-2012, 04:07 PM
    HighTekk^
    Quote Originally Posted by icemeister View Post
    You can't use HP-80 (R402A) because it would overload that compressor which was designed to run on R12.
    Not too sure about that but I do know this about the box...

    Was originally an R-12 Low temp box that was converted to 404a(which I recently found out after working on another piece of equipment that described changing everything onsite to 404a).

    The old expansion valve had failed shut so it was replaced with a sporlan EFSE-1/2-ZP. As you know this is good for low temp R-404A, R-502, R-402A or R-507.

    In addition to replacing the valve I also had ordered an additional powerhead for the TEV that would work for R-134A, R-12 and R-401A. As the 401a was the cheapest refrigerant I could buy I opted to go with it but it never cooled the box below 10 degrees.

    So now I am considering using the HP80, MP66 or 404A, which I have a bottle of each in my possession. I just don't want to wast another day reclaiming, changing dryer, pressure-testing, evacuation and so on.

    I would like to keep the box at -10 degrees if possible when its fully loaded on a warm day.

    What do you think? I have read many threads on here but there is a lot of conflicting posts.

    This box has thrown me through a loop, just when you try to experiment and cut a itty bitty corner it turns around and bites you in the a**. So I was wondering if anyone has any particular experience in this overall situation.
  • 03-16-2012, 10:51 AM
    HighTekk^
    Looking at the pt chart hp80 would give me the lowest temp possible for the pressures I have, ya think that might pan out better?
  • 03-16-2012, 09:38 AM
    HighTekk^
    MP 39 was a failure, I couldn't get the box below 25 degrees without starving the system for refrigerant and creating flash before the tev. Gonna reclaim and try out mp 66, as I have heard is the only low temp. replacement for r-12. After clearing the sightglass my suction psig at the compressor was around 16-20 which won't really do me any good. I'll be out there probably tomorrow to fool around with it some more.
  • 03-05-2012, 08:42 PM
    ar_hvac_man
    like he said, charge until glass is clear. then 6-8 deg s.h. at the bulb. copeland wants 20 at the inlet of the compressor, sometimes thats hard to do depending on the length of the lineset. focus on the s.h. at the bulb. once i get it to 6 at the bulb its usually very close. ill then adjust very slightly until i get it to its most stable point.

    thats all the unit will do at that point. squeezing down the txv to lower your suction in attempt to get a colder evap will only starve the evap and make the txv hunt
  • 03-05-2012, 08:30 PM
    icemeister
    Quote Originally Posted by HighTekk^ View Post
    Its an old bohn evaporator that had r12 in it, converted a while ago, then sat for about a year when some other contractor tried condemning it. Owner said the contractor reported it had multiple leaks and a bad compressor, quoted him a really high price for replacement and repair. So coming into it I had my doubts. But today I finally was able to get the box down to 6-8 degrees. I played with the valve and charge and ended up with a suction of 8 and a head of 110 and my superheat as measured at the condenser was 8-12. This was after removing refrigerant until I seen flash in the sightglass for at least a 20 min period. Everything was done for at least 20 minutes at a time, including expansion valve adjustments and refrigerant adding/subtracting. But little by little I added refrigerant until the sg cleared and then that's when I started adjusting the tev. I'm just trying to understand why they went with 401a to begin with and was really unsure if it could maintain what they wanted. I was already committed to the 401a because I had ordered it from the supply house and broke the seal before I started having doubts that it would work. Funny how it all works out though. I'll check tomorrow to see if the box has reached proper temps. My question now is how do I get down to a 2-3 suction without causing flash in the sightglass?
    Thanks for the blow-by-blow description. That's helpful in letting me know where you are at this point.

    Stop playing with the charge trying to affect a change in suction pressure.

    Just charge to a full SG. Add a pound or two more to be sure it'll stay clear and forget about it for the time being.

    Set the TXV superheat leaving the evaporator, not at the entrance of the condensing unit. The location of the TXV's sensing bulb is precisely where I'm referring to.

    Once all this is done, please remember this advice. You cannot force the suction to where you want it to be, as it will always tend to go to a point at which the system is balanced with the load imposed upon it.

    That basically says, "What you'll see is what you'll get."
  • 03-05-2012, 07:55 PM
    HighTekk^
    Its an old bohn evaporator that had r12 in it, converted a while ago, then sat for about a year when some other contractor tried condemning it. Owner said the contractor reported it had multiple leaks and a bad compressor, quoted him a really high price for replacement and repair. So coming into it I had my doubts. But today I finally was able to get the box down to 6-8 degrees. I played with the valve and charge and ended up with a suction of 8 and a head of 110 and my superheat as measured at the condenser was 8-12. This was after removing refrigerant until I seen flash in the sightglass for at least a 20 min period. Everything was done for at least 20 minutes at a time, including expansion valve adjustments and refrigerant adding/subtracting. But little by little I added refrigerant until the sg cleared and then that's when I started adjusting the tev. I'm just trying to understand why they went with 401a to begin with and was really unsure if it could maintain what they wanted. I was already committed to the 401a because I had ordered it from the supply house and broke the seal before I started having doubts that it would work. Funny how it all works out though. I'll check tomorrow to see if the box has reached proper temps. My question now is how do I get down to a 2-3 suction without causing flash in the sightglass?
  • 03-05-2012, 03:57 PM
    icemeister
    Quote Originally Posted by VTP99 View Post
    Others are R408 & R422C used for R502 replacement. Low temp. Was your box refrigerant originally R12 or R502 ?
    We're assuming this was originally an R12 LT system.
  • 03-05-2012, 03:55 PM
    icemeister
    Quote Originally Posted by HighTekk^ View Post
    Good deal, I think I see the light. I'm currently adjusting the sh, adding refrigerant as the box cools. That seem normal? Lots of frost to. Seems to be going in the right direction.
    Properly charging the system brings up another set of issues.

    What exactly is this system you're working on? Is it a walk-in box with a remote condensing unit with a receiver or a self-contained reach-in with no receiver?

    If it's a walk-in system with a receiver, you should have a sightglass in the liquid line after the filter-drier. For proper charge, just clear the glass (unless it has a Headmaster condenser flooding control...which is another matter).

    If it's self-contained with no receiver, the system would be critically charged...meaning you need to weigh-in the refrigerant. There should be a factory recommended charge stated on the data plate for the box. With R409A, since it's less dense than R12, will require less weight than the factory charge amount. This is determined by the density ratio of R409A to R12:

    Density Ratio = 76 lbs/cu ft / 81.8 lb/cu ft = R12 Weight X .93
  • 03-05-2012, 03:11 PM
    HighTekk^
    Good deal, I think I see the light. I'm currently adjusting the sh, adding refrigerant as the box cools. That seem normal? Lots of frost to. Seems to be going in the right direction.
  • 03-05-2012, 02:33 PM
    VTP99
    Others are R408 & R422C used for R502 replacement. Low temp. Was your box refrigerant originally R12 or R502 ?
  • 03-05-2012, 02:24 PM
    icemeister
    Quote Originally Posted by HighTekk^ View Post
    The thing that suck is I have already been adding the 401 a back into the system and trying to set up the tev to work with the pressures is confusing me. If you wanted a box to maintain that range temperatures (-10 - 0) that would mean that my average evap. temp would be the same right? And then I would figure in the glide of 6, because I think they say its actually <11.5 right? It would be added to the superheat? Too much math and I'm getting confused. Not too often do I have to do this but this is a first for 401a. Anyone have a better way to explain this? I feel I'm not doing it right.
    Let's see if we can help clear this up for you a little...

    First, the TXV's sole job in the system is to control refrigerant flow to the evaporator according to the superheat of the refrigerant vapor leaving the evaporator. It's not a pressure regulator.

    Secondly, if the refrigerant temperature inside the evaporator were the same as the box temperature, how could there be any heat transfer? The evaporator temp must always be at a lower temperature. With a walk-in box, this temperature difference (TD) is usually about 10ºF whereas reach-ins usually run around a 15ºF TD. (I'll use a 10ºF TD in the following for simplicity.)

    DuPont T/P Chart: http://www2.dupont.com/Refrigerants/...ofit_guide.pdf

    With a 0ºF box running R401A and a 10F TD, you should expect to run an evap temp of -10ºF. That would correspond to a saturated pressure of 2.8 psig. At that point the TXV should be set to control the superheat to approximately 6-8ºF leaving the coil...ie, the suction line temp at the sensing bulb should read around -2ºF to -4ºF.

    When you use a T/P chart, the saturated temps in the lower ranges typical are the dewpoint temperatures, which already accounts for the refrigerant's glide.
  • 03-05-2012, 01:36 PM
    HighTekk^
    The thing that suck is I have already been adding the 401 a back into the system and trying to set up the tev to work with the pressures is confusing me. If you wanted a box to maintain that range temperatures (-10 - 0) that would mean that my average evap. temp would be the same right? And then I would figure in the glide of 6, because I think they say its actually <11.5 right? It would be added to the superheat? Too much math and I'm getting confused. Not too often do I have to do this but this is a first for 401a. Anyone have a better way to explain this? I feel I'm not doing it right.
  • 03-05-2012, 01:12 PM
    icemeister
    Here's a link to info on MP-66 from DuPont:

    General Info:
    http://www2.dupont.com/Refrigerants/.../SuvaMP66.html

    Retrofit Guide:
    http://www2.dupont.com/Refrigerants/...ofit_guide.pdf
  • 03-05-2012, 12:43 PM
    fordrules
    It was My understanding that MP66 is better for low temp applications. As far as the pressures go, just get a pt chart.