  • 08-18-2012, 11:18 AM
    joeyd
    Quote Originally Posted by eddiegoodfellar View Post
    So if we are sitting at 1000 microns on the Bluvac

    It would be in the 1045 micron to 945 micron range?
    As you indicated in your correction above, 945 to 1055.
  • 08-18-2012, 10:16 AM
    eddiegoodfellar
    Thank you.
  • 08-18-2012, 09:51 AM
    joeyd
    Quote Originally Posted by eddiegoodfellar View Post
    So if we are sitting at 1000 microns on the Bluvac

    It would be in the 1045 micron to 945 micron range?
    As you indicated in your correction above, 945 to 1055.
  • 08-18-2012, 12:33 AM
    eddiegoodfellar
    No tongue in cheek intended. I have been tricked in the past with accuracy,scale,resolution and count on meters before.

    **I should have wrote 1055microns not 1045microns
  • 08-17-2012, 11:56 PM
    Itstony
    Quote Originally Posted by eddiegoodfellar View Post
    So if we are sitting at 1000 microns on the Bluvac

    It would be in the 1045 micron to 945 micron range?
    It would be good eddie if anybody that uses the 557/570 along with a stand alone vac-gauge could contribute.
    Your statement may be tongue in cheek, but that is exactlty what Testo's spec sheet says.
    For HVAC it makes me wonder if this feature is "Showing us what we could have won".
  • 08-17-2012, 09:35 PM
    eddiegoodfellar
    So if we are sitting at 1000 microns on the Bluvac

    It would be in the 1045 micron to 945 micron range?
  • 08-17-2012, 10:13 AM
    joeyd
    Quote Originally Posted by eddiegoodfellar View Post
    what is the accuracy of the bluvac?
    The BluVacs' rated accuracy is +/- 5% (of reading) +/- 5 microns from 10°F to 122°F (-12°C to 50°C).

    Additionally, the BluVacs can be recalibrated to factory specifications simply by placing it in your freezer. No return to factory necessary for calibration.
  • 08-17-2012, 08:41 AM
    Itstony
    Quote Originally Posted by itsiceman View Post
    IMO Stick with the vacuum indicator in the testo gauge till you can afford anything but the very best micron gauge like a Thermal or BluVac. Anything else will be a headache
    OK, I will go for the BluVac lite. Just waiting for Jim from Trutech to get back to me.
  • 08-17-2012, 08:17 AM
    itsiceman
    Quote Originally Posted by Itstony View Post
    I'm getting a Testo anyway. Just deciding on which vacuum gauge.
    The fieldpiece look good value at $126.
    IMO Stick with the vacuum indicator in the testo gauge till you can afford anything but the very best micron gauge like a Thermal or BluVac. Anything else will be a headache
  • 08-17-2012, 01:27 AM
    Itstony
    I'm getting a Testo anyway. Just deciding on which vacuum gauge.
    The fieldpiece look good value at $126.
  • 08-16-2012, 10:35 PM
    eddiegoodfellar
    what is the accuracy of the bluvac?
  • 08-16-2012, 11:57 AM
    joeyd
    Quote Originally Posted by itsiceman View Post
    That is confusing how they wrote it.
    So is "±1 Digit" ±1 micron? Thats better than a BluVac
    Looks like ±1 digit translates to one tic on their scale which is ±500 microns
    Hi, Ice.

    Looking at the Testo 557 datasheet, it rates vacuum accuracy as +/- 1% FS (Full Scale) +/- 1 digit (at 22C).

    This is a helluva way to rate a micron gauge! I don't know what they consider as "full scale", but, generally, when working with vacuum, I would consider FS to be 760,000 microns. Therefore, 1% FS would be 7,600 microns! In addition, 1 digit, represents 500 microns, as you have indicated.

    From my vantage point, then, a reading of +/- 8,100 microns (at any vacuum level and at 22C) would be within factory spec. And no specs are given outside of the 22C temperature point. TIFWIW!

    Full disclosure for those who don't know: I am the inventer, designer, and manufacturer of the AccuTools BluVac & BluVac LTE gauges.

    Edit: Upon further reading of the datasheet, the vacuum range is 0 to 1 bar. So, one bar, or 750,064 microns, should be "full scale".
  • 08-16-2012, 08:32 AM
    eddiegoodfellar
    i think u are right
  • 08-16-2012, 06:08 AM
    itsiceman
    That is confusing how they wrote it.
    So is "±1 Digit" ±1 micron? Thats better than a BluVac
    Looks like ±1 digit translates to one tic on their scale which is ±500 microns
  • 08-15-2012, 09:11 PM
    eddiegoodfellar
    I was wrong.It is listed in the manual as:
    ±1% fs (±1 digit)
  • 08-15-2012, 07:27 PM
    rtufixer
    Dont waste your time or money one of the worst manifolds i have owned. On my second set and getting ready to send this set back.
  • 08-15-2012, 04:47 PM
    itsiceman
    Quote Originally Posted by eddiegoodfellar View Post
    725psi on high and low side with a 0.5% accuracy. I think the micron and temp are also 0.5% accurate.
    I don't think the micron function of the testo gauge is 0.5% accurate.
    I believe they list ±500 microns with a 500 micron resolution.
  • 08-15-2012, 03:05 PM
    jim bergmann
    Quote Originally Posted by Itstony View Post
    Sent an e-mail to JLB via the but no reply :-(
    Sorry about that that email goes to a general email box at the office with hundreds and hundreds a day.

    My email addresses in my profile you can contact me directly there.
  • 08-15-2012, 01:51 PM
    Itstony
    Quote Originally Posted by Itstony View Post
    JLB,
    I have checked your website and must say a lot of thought and care has been made.
    Very good tips and areas to be concerned with, prices very competative.
    I shall look to contact you for my equipment soon.
    Sent an e-mail to JLB via the but no reply :-(
  • 08-13-2012, 01:54 AM
    Itstony
    Quote Originally Posted by jim bergmann View Post
    The reason to by the 557 is increased accuracy over the 550. Although the 557 can read vacuum, you are far ahead to eliminate the manifold from the evacuation process and use large diameter hoses, core tools and a stand alone micron gauge connected with a brass fitting. Hoses leak, and a manifold with 1/4" hoses slows the process even further.

    We sell a lot of Testo 557 and Testo 570 gauges, but we do not sell them nor any micron gauge equipped gauge with the intent of selling an all in one tool. The vacuum gauge was an industry driven feature that was added by several manufacturers that did not have experience with the mechanics of evacuation. I would use it if I did not have anything else, but the times savings with large hoses is so huge, I would not use a manifold for evacuation as an every day tool.
    JLB,
    I have checked your website and must say a lot of thought and care has been made.
    Very good tips and areas to be concerned with, prices very competative.
    I shall look to contact you for my equipment soon.
This thread has more than 20 replies. Click here to review the whole thread.

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •