  • 01-31-2013, 12:20 PM
    doc havoc
    If it's running 10-25 minutes, I highly doubt it is a flame sensor or control board issue. As others have stated, cycling on limit, satisfying call for heat at the stat or plugged/restricted condensate drain.
  • 01-31-2013, 12:11 PM
    Dowdhvac
    Check unit for proper gas pressure, furnace will tell you the minimum gas pressure required for the furnace. But like the other guys said, check air flow, flame sensor & check to see if you have proper draft.
  • 01-30-2013, 11:36 PM
    craig1
    Is this a condensing furnace? The drain could be clogged and backing up.
  • 01-30-2013, 07:31 PM
    kw10925
    you should check air flow,make sure its not shutting off on high limit.Also make sure that prving switch is not loosing its draft ,may have clogged tube on the inducer.
  • 01-30-2013, 05:39 PM
    Rammerjammer
    Sounds like high limit like snupytcb said. Check airflow. Dirty blower wheel. Dirty filter or stopped up evap
  • 01-30-2013, 10:44 AM
    snupytcb
    are you sure it is not tripping high limit? or even satisfing t=stat?
  • 01-30-2013, 10:41 AM
    hvac86

    furnace ignites then after 10-25min cuts off

    Rookie tech working on a Sears brand furnace model 867.764221
    The furnace comes on and stays lit for 10-25 min then shuts off. has a spark ignition that is also combination with the flame sensor. Is it a dirty flame sensor with a combination of a failed spark box? Used my multi meter and also turned on furnace disconnected
    the flame/ignition sensor write and