Topic Review (Newest First)

  • 09-10-2012, 06:05 PM
    jnsrose
    Quote Originally Posted by lioni hvac View Post
    Yes reuse lineset, yes purge linset, Evacuation good. I pulled blower motor wire and ran a/c All feed tubes froze. Subcooling 3, airflow good my spilt is 10
    Are you saying you ran the ac with no blower? This would sure cause all your tubes to freeze.
  • 09-10-2012, 08:16 AM
    craig1
    get your subcooling up to 10 and see what happens.

    It sounds like you're undercharged.
  • 09-10-2012, 02:28 AM
    coolwillis
    only half of coil getting cold? 3 degree SC? not sure what spilt is... If its milk, you aint supposed to cry. I know that. I've heard old timers call the temp difference the "split". If thats what you're talking bout, 10 just wont do. I'm probably wrong but I'm thinking under charged.
  • 08-07-2012, 02:19 AM
    jim147
    Quote Originally Posted by Cmstech View Post
    Orifice clogged from install?
    Negative points for





    jim
  • 08-07-2012, 01:02 AM
    comfort comando
    Any filter dryers that could be pluged?
  • 08-06-2012, 10:58 PM
    Cmstech
    Orifice clogged from install?
  • 08-14-2011, 11:04 PM
    hceptj
    Quote Originally Posted by wsykes View Post
    sounds like you got a bad evap coil form the factory and its restricted
    get your post up and get your pro membership and post this on the pro side
    Ditto
  • 08-14-2011, 08:39 PM
    ChaseAir
    You need to know subcool and superheat. Your subcool should be higher than 3. Sounds undercharged. What was the superheat?
  • 08-14-2011, 10:30 AM
    wsykes
    sounds like you got a bad evap coil form the factory and its restricted
    get your post up and get your pro membership and post this on the pro side
  • 08-14-2011, 09:45 AM
    lioni hvac
    Yes i removed flow rater.
  • 08-14-2011, 08:00 AM
    SouthTex
    had one one time installers installed txv didn't take out the flow rater, low suction poor split unit was charged by subcooling to specs
  • 08-13-2011, 10:51 PM
    gregp

    Are these

    Quote Originally Posted by lioni hvac View Post
    Yes reuse lineset, yes purge linset, Evacuation good. I pulled blower motor wire and ran a/c All feed tubes froze. Subcooling 3, airflow good my spilt is 10
    readings correct? You only have 3 degree subcool?
  • 08-13-2011, 07:52 PM
    lioni hvac
    Also feed tubes does not freeze with system not running.
  • 08-13-2011, 07:49 PM
    lioni hvac
    Yes reuse lineset, yes purge linset, Evacuation good. I pulled blower motor wire and ran a/c All feed tubes froze. Subcooling 3, airflow good my spilt is 10
  • 08-13-2011, 07:35 PM
    Keith73
    Reuse lineset? Purge lineset? Evacuation to what micron level? Feed tubes freezing one side only? What is the superheat and subcool values? Airflow measured?

    More information and maybe a few pics may help.
  • 08-13-2011, 07:33 PM
    lioni hvac
    company 15 years first time this happen to me and my friends
  • 08-13-2011, 07:30 PM
    MM#7
    Quote Originally Posted by lioni hvac View Post
    case coil system laying on its side a coil
    how long have you been doing this type of work, do you have a co. or work for some one?
  • 08-13-2011, 07:22 PM
    lioni hvac
    case coil system laying on its side a coil
  • 08-13-2011, 07:18 PM
    MM#7
    Quote Originally Posted by lioni hvac View Post
    I did the same system last week it works fine.
    ok maybe one of the pros has a suggestion, good luck!
  • 08-13-2011, 07:17 PM
    MM#7
    Quote Originally Posted by lioni hvac View Post
    coil is on furnace
    yeah i got that, but the coil is horizontal, correct? which means its lying on its side, did the other coil have a a-coil or a horizontal coil. what was wrong with the old coil? was this a easy swap, or did you modify the duct coming off furnace! how much space is from the furnace top to the horizontal coil.1 ft. or is the coil jammed up against the furnace and did you just fill in the gaps with tape/metal, trying too get a mental picture here!
This thread has more than 20 replies. Click here to review the whole thread.