  • 07-17-2012, 11:42 PM
    hvac meister
    Sorry everyone.... I meant the RLA rating is 10.6. Rated Load Amps. Check out this link I found on an earlier thread... https://opi.emersonclimate.com/CPID/...AEB/ae1250.pdf
  • 07-17-2012, 10:07 PM
    Music Seeker
    It lasted about two seconds before the breaker tripped. If it's pulling that kind of amps and DOESN'T trip the breaker? Try a hard start kit first. That's a sure-fire way to condemn the compressor.
  • 07-17-2012, 09:58 PM
    edward301
    Should have blown the fuse or breaker quick.
  • 07-17-2012, 09:17 PM
    Music Seeker
    I had this happen as well, it was an '06 Goodman with a compressor drawing 198, LRA was 165. The scrolls must have come loose, as it was just rattling around inside before stopping that to just hum and then trip the breaker. Replace that junker!
  • 07-17-2012, 09:07 PM
    akelesis
    usually when any motor pulls anything close to the LRA it needs replacing

    * remember this RLA x 5 = LRA (approx estimate)
    This comes in handy when the rating plate is gone and you wanna know what the LRA is.
  • 07-17-2012, 08:51 PM
    Andy Schoen
    Quote Originally Posted by hvac meister View Post
    On the condenser data plates you find the LRA. I assume this is the locked rotor amps. What exactly does this mean??
    It is motor amp draw with the rotor "locked". It will be the maximum amp draw you should expect on start up.
  • 07-17-2012, 08:25 PM
    mjohnson2981
    I could see it run more the RLA, but I don't think it is possible to be more than the locked rotor amps... and be doing anything other than fireworks!
  • 07-17-2012, 08:07 PM
    second opinion
    Quote Originally Posted by hvac meister View Post
    On the condenser data plates you find the LRA. I assume this is the locked rotor amps. What exactly does this mean?? I had a small 1.5 ton unit today I'm pretty sure has a mechanical problem in the compressor. The compressor was shaking violently and drawing more amps than the LRA.
    Your amp probe is defective!
  • 07-17-2012, 08:04 PM
    Huntinwalkerstyle
    The LRA on the plate is what that compressor is tested at. I have seen alot of units run past that rating but not very long.
  • 07-17-2012, 08:01 PM
    Huntinwalkerstyle
    If compressor is pulling LRA then it needs to be replaced.
  • 07-17-2012, 07:53 PM
    hvac meister

    LRA

    On the condenser data plates you find the LRA. I assume this is the locked rotor amps. What exactly does this mean?? I had a small 1.5 ton unit today I'm pretty sure has a mechanical problem in the compressor. The compressor was shaking violently and drawing more amps than the LRA.