  • 06-26-2010, 11:43 PM
    Joe Harper
    Look around the air handler for the piston and put it back in.
  • 06-26-2010, 11:37 PM
    timebuilder
    Quote Originally Posted by beenthere View Post
    Sh and SC can tell you a lot about what is happening in a system.

    Ding, ding, ding, and we have a winner!
  • 06-26-2010, 09:34 PM
    beenthere
    Sh and SC can tell you a lot about what is happening in a system.
  • 06-26-2010, 09:04 PM
    h-to-the-vac
    will do see you in pro technical
  • 06-26-2010, 09:00 PM
    timebuilder
    Quote Originally Posted by h-to-the-vac View Post
    well, at first thought TXV, but it is fixed orifice. 500 microns. i ran out of time yesterday and will dig deeper. i thought maybe a little blockage in the fixed? wendo, will look into what you have pointed out, much appreciated.
    timebuilder, two possibilities? thanks for your time y'all.
    i am new to this forum and did not realize there is a pro technical forum, excuse my etiquette.
    No problem. If you are a working pro, get the pro status and we will see you in pro technical.

    We don't want people being able to search for info and get hurt trying to DIY, and the pro status is how we keep that from happening.
  • 06-26-2010, 08:52 PM
    h-to-the-vac
    well, at first thought TXV, but it is fixed orifice. 500 microns. i ran out of time yesterday and will dig deeper. i thought maybe a little blockage in the fixed? wendo, will look into what you have pointed out, much appreciated.
    timebuilder, two possibilities? thanks for your time y'all.
    i am new to this forum and did not realize there is a pro technical forum, excuse my etiquette.
  • 06-26-2010, 08:11 PM
    Wendo
    How about an improperly sized or malfunctioning TXV valve? How many microns did you pull the system down to? Is there a crankcase pressure regulating valve on the system or something like that?
  • 06-26-2010, 07:12 PM
    timebuilder
    We usually don't address technical issues in open forums. We have a Pro Technical forum for that. A few more posts and you can apply for that status.

    Speaking in the general sense, I would look at what variable is changing that could cause the reaction you describe. If no variable is changing, then something is changing without a changing input variable. I can only think of two possibilities right now.
  • 06-26-2010, 06:25 PM
    h-to-the-vac

    suction pressure bouncing

    i pulled a vacuum for over 24hrs, unit stayed in a vacuum. charged unit to nameplate weight. unit pressures will look great at 68 low and 270 high. then all of a sudden suction will drop to 50psi then rise back up to almost 70psi, stabilize for a minute and do it all over again. any ideas for me? i appreciate your time.