  • 11-30-2012, 11:13 PM
    Andr00
    Quote Originally Posted by joeblo View Post
    If you jumper R to G and the fan switch on the thermostat is in the auto position the A/C cond will come on, this is normal. Disconnect the Y when doing this. The relay on the circuit board that turns the blower on is one of the most common failures I have seen with circuit board.
    Usually taking the form of the back of the circuit board being charred crispy under the relay. I think I've already replaced about a dozen BBQ'd single-stage Carrier circuit boards this month.
  • 11-30-2012, 07:28 PM
    hurtinhvac
    Pull the blower and inspect the heat exchanger on any 58PAV you come across - there's a good chance you needn't go any further.

    Most of the time you don't even need a mirror to find the cracks, only to get a better look and verify. Front of cells, 2nd bend upward, right at the dimple. I've found five or six so far and it's not even December 1 yet.

    Otherwise, this is a very simple furnace and easy to trouble shoot
  • 11-30-2012, 07:00 PM
    Rob_in_WV
    Whats the model and serial numbers and have you verified 24 volts between W and C? Also if it has an LED, what diagnostic code does it give? I wouldn't jump anything out until I verified what code is being given and that proper call for heat is being received at the board terminals.
  • 11-30-2012, 05:11 PM
    beenthere
    Quote Originally Posted by Elhuezo View Post
    Wow what a cluster I've made, I meant the R to G see if the blower motor will turn on, the condeser started but not the blower motor. My bad for stating the wrong terminal. Yes I know it's better to have a senior tech to back me up but when ones not around should I just wait? So any how, I jumped the R to W and no induction motor running or gas valve opening. R to Y and same no response. So I jumped the test terminal to C and the LED was flashing fast. So to me it seems as though it's the control board. Yes it was the HSI that I ohmed out
    What your calling side work, isn't side work since your not working in the trade. Your working under the table(presuming your not going to file this income with the IRS).
  • 11-30-2012, 04:34 PM
    joeblo
    If you jumper R to G and the fan switch on the thermostat is in the auto position the A/C cond will come on, this is normal. Disconnect the Y when doing this. The relay on the circuit board that turns the blower on is one of the most common failures I have seen with circuit board.
  • 11-30-2012, 02:53 PM
    Elhuezo
    Yes the igniter was unplugged otherwise you'd be omhing out the rest of the system.
  • 11-30-2012, 02:47 PM
    syndicated
    You said you ohm'd the igniter, what value did you get? And was the igniter unplugged from the harness?
  • 11-30-2012, 01:49 PM
    Elhuezo
    It is wired correctly also from the statement that she stated that the unit used to work properly then the heater stopped working (due to the Hot Surface Ignitor being out) than the blower motor stopped. So that leads me to believe that it's the control board. I have to also check the manual restart button to ensure that it is the board. Thanks for the reply and encouragement. After all it's just the internet. Think skin is what is needed in the world not PC BS.
  • 11-30-2012, 12:57 PM
    JohnBrumfield
    If you are jumper r and g and the outdoor unit comes on it could be a few thing. First I would check the wiring to insure that it is wired correctly. If it is wired correctly the I would start looking at the control board. Don't give up as a tech and don't listen to the down talk here if someone is talk down to you it is just because they don't know.
  • 11-30-2012, 12:43 PM
    Elhuezo
    Wow what a cluster I've made, I meant the R to G see if the blower motor will turn on, the condeser started but not the blower motor. My bad for stating the wrong terminal. Yes I know it's better to have a senior tech to back me up but when ones not around should I just wait? So any how, I jumped the R to W and no induction motor running or gas valve opening. R to Y and same no response. So I jumped the test terminal to C and the LED was flashing fast. So to me it seems as though it's the control board. Yes it was the HSI that I ohmed out
  • 11-30-2012, 11:22 AM
    buford
    Jumping c to g ! that will always cause things to work.keep jumping things out and you will be calling out a tech to repair.
  • 11-30-2012, 06:25 AM
    beenthere
    He Saw It.
  • 11-30-2012, 06:16 AM
    dandyme
    you don't need to jumping anything out until you understand what it is you are jumping and the consequences of any incorrect action.

    I'm still trying to understand what "heating element" you ohmmed out; ?
  • 11-30-2012, 06:02 AM
    beenthere
    I am "qualified"
    What makes you "qualified" to work on your own without a senior tech to support/back you up?

    Yes, everyone needs a little help once in awhile.
  • 11-30-2012, 05:30 AM
    beenthere
    Moved to Tech to Tech Residential forum.
  • 11-30-2012, 12:48 AM
    Elhuezo

    Carrier 58PAV Trouble

    Have a clients furnace that isn't working correctly, stated that the furnace doesn't turn on. Due to heat element that I ohmed out and no continuity. But she stated that now the fan (blower motor) doesn't work. Troubleshooted and motor works, bypassed control board and motor turns on. The trouble is when I jump C to G, the condenser turns on and not the blower motor. Did the test connector to C and the led light does rapid flash. I'm thinking the board is shot. Any advice? I'm new to the field and trying to get some experience by doing some side work. I am "qualified" have EPA cerification and went through the proper training but like life. Experience isn't learned in books.