Reply to Thread

Post a reply to the thread: Daikin D-BACS Interface

Your Message

 
 

You may choose an icon for your message from this list

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Additional Options

  • Will turn www.example.com into [URL]http://www.example.com[/URL].

Topic Review (Newest First)

  • 03-05-2024, 07:32 PM
    Joemar
    Thank you.
  • 03-05-2024, 06:17 PM
    clogic
  • 03-04-2024, 10:00 PM
    Joemar
    Hello, I am looking for copy of D BACS MS3setup does anyone have here?

    Thanks in advance.
  • 06-23-2023, 11:24 AM
    blacktigra
    Hello everyone

    Does anybody have an expirience with older version of bacnet gateway DMS502A51? It was made probably in 2008, but it is completely new, and was sold by Daikin last year.
    Somehow I managed to change IP address, and now i can't get any response from it.
    I tried to use RS232 25 pin cable, but I can't connect to the gateway from my laptop win Win 7.
    Is it possible to make a hard reset on it?
  • 02-17-2023, 01:39 AM
    Andrew Taljaard
    Quote Originally Posted by TRap250 View Post
    Changing the IP address on the PC was what did it! I did not see this note anywhere. YOURE THE MAN! MANY THANKS!
    Schweet... Happy to hear you came right ;-)
  • 02-16-2023, 12:43 PM
    TRap250
    Changing the IP address on the PC was what did it! I did not see this note anywhere. YOURE THE MAN! MANY THANKS!
  • 02-16-2023, 01:11 AM
    Andrew Taljaard
    Quote Originally Posted by TRap250 View Post
    Hi All,

    I have read thru this thread and tried everything but I continue to get the cannot communicate error in the setup software. I used wireshark and found the ip address (192.168.222.3) but it will not connect. I tried with a crossover cable and straight cable using a switch. I also purchased a serial to usb cable but that doesnt show any communication at all. If anyone has any suggestions I am all ears, PLEASE.
    Good morning TRap250

    Here are my notes on setup:

    Daikin Bacnet Gateway (D-BACS) DSM502B51 Communication Procedure:

    1. RS232-C Cable (Null Modem Partial Handshake) – ONLY MEANS OF COMMS IF THE GATEWAY’S IP ADDRESS IS UNKNOWN
    1.1. Create a Null Modem Via: Control Panel/Network Settings/Phone and Modem Options
    1.2. Create a new connection: Office network using the above modem to connect
    1.3. Set PC IP address in Null Modem Connection properties to 192.168.3.x (x>1)
    1.4. Connect Null Modem Partial Handshake Cable to RS232C-1
    1.5. Run SetupBACnet.exe and enter IP: 192.168.3.1 (When using the Null Modem Cable, the Gateway’s IP is forced to this value)
    1.6. CHECK/SET the gateway’s IP Address and mask and default gateway (used for Ethernet connection)
    2. Ethernet - FASTER MEANS OF COMMS WHEN THE GATEWAY’s IP ADDRESS IS KNOWN
    2.1. Change PC IP Address in LAN Connection: Match the IP confirmed in 1.6 HOWEVER change the last number of the IP Address to one decimal value higher
    2.2. Connect Cross-over Ethernet 100BASE-TX cable from the PC to the Ethernet port on the Gateway
    2.3. Run SetupBACnet.exe and enter IP: IP confirmed in 1.6
    2.4. CHECK/SET the gateway’s IP Address and mask and default gateway (used for Ethernet connection)


    NOTE: Please make sure you UN-plug the gateway from the network when re-booting the device, as it may get stuck in a boot-loop otherwise.
  • 02-15-2023, 10:14 AM
    TRap250
    Hi All,

    I have read thru this thread and tried everything but I continue to get the cannot communicate error in the setup software. I used wireshark and found the ip address (192.168.222.3) but it will not connect. I tried with a crossover cable and straight cable using a switch. I also purchased a serial to usb cable but that doesnt show any communication at all. If anyone has any suggestions I am all ears, PLEASE.
  • 07-15-2022, 04:17 PM
    ear197201
    Could someone kindly email me the DBACS Setup software. Email in profile

    Thanks

    Disregard I just went back and seen the drop box

    Thanks
  • 10-26-2021, 01:02 PM
    clogic

    Here tis'

    Quote Originally Posted by scottleyva View Post
    Does anybody know if the SetupMS3 software is available for an online download? I am also looking for the excel points list that can be configured and downloaded into the D-BACS.
    https://www.dropbox.com/sh/jii42hlww...xx8pykFra?dl=0
  • 10-26-2021, 10:40 AM
    kheide
    Is there any chance someone could send me a copy of SetupMS3? I need to change the IP address on the D-BAC. Thanks in advance.
  • 08-23-2021, 05:10 AM
    fundi_wa_dbacs
    Quote Originally Posted by MaxBurn View Post
    We do the schedule natively in our front end with tridium or ALC for example. That outputs a binary value we write via bacnet to Daikin or whatever.

    I’ve looked into writing directly to bacnet schedule objects before but not actually done it. Some of them don’t support all the different possibilities operators would put in anyway.
    Thanks MaxBurn

    Are there any Open Source bacnet front-ends that could possibly do this?
    [ currently doing a ton of googling to find any that can help me with scheduling ]

    Thanks!
  • 08-15-2021, 06:32 AM
    MaxBurn
    We do the schedule natively in our front end with tridium or ALC for example. That outputs a binary value we write via bacnet to Daikin or whatever.

    I’ve looked into writing directly to bacnet schedule objects before but not actually done it. Some of them don’t support all the different possibilities operators would put in anyway.
  • 08-15-2021, 02:18 AM
    fundi_wa_dbacs
    Hallo peeps!

    The information in this thread helped me to setup a Daikin D-Bacs DMS502B51 gateway from scratch and to troubleshoot multiple VRVs
    Many thanks to everyone here

    The sofwares that helped me the most for setup and discovery were:

    1. SetupBACnet v6.34
    2. Yabe
    3. Wacnet

    The thing I have been unable to do and have no idea about is SCHEDULING.

    I can't find the feature/software for it.

    By scheduling, I mean to have D-Bacs switch the units ON and OFF based on calendar days or days of the week

    Any ideas on how to do this?

    Thanks!
    Fundi
  • 04-27-2021, 09:19 AM
    RJS_Controls

    Has this continued to work?

    Quote Originally Posted by AlexM View Post
    Well, this got interesting. Posting back to save someone else 6 months of fault finding.

    It appears that between the DBACS and the JACE the auto negotiation for port speeds on the IP ports gets lost. Every now and again they end up with the DBACS insisting on switching down to 10 speed and not moving back to 100 speed. With an older AX JACE this causes issues every now and again but generally the JACE switches back to 10 speed and all is good, most of the time. On the newer JACE800 it appears that it will not switch unless you reboot or disconnect/reconnect the cable so when the DBACS decides it's moving back in time and refuses to switch back up to 100 speed you're stuck until you reboot or unplug it.

    I've solved it by installing a small managed switch between the two and fixing the port connected to the DBACS at 10 speed. So far so good.
    I have to ask, How has this worked to date?
    My previous method of remotely powering OFF the 24v to the DBAS, initially worked, but I am finding the time between resets has decreased.
    One of the DBACS seems to have lost its configuration, so now although "alive" in the JACE, there are only 5 BACNet objects discovered.
    The managed switch locked in @ 10m would be my next try.
    Rich
  • 02-21-2021, 09:39 AM
    JSLLC4Life
    Quote Originally Posted by AlexM View Post
    I've solved it by installing a small managed switch between the two and fixing the port connected to the DBACS at 10 speed. So far so good.
    Not sure if it is the same underlying problem with JACE, but I've had a couple of Cisco switches refuse to communicate with a JACE 8. These were gigabit switch (also supported 10/100 megabit). The solution was to lock the port speed at 100 megabit.
  • 02-21-2021, 06:32 AM
    AlexM
    Well, this got interesting. Posting back to save someone else 6 months of fault finding.

    It appears that between the DBACS and the JACE the auto negotiation for port speeds on the IP ports gets lost. Every now and again they end up with the DBACS insisting on switching down to 10 speed and not moving back to 100 speed. With an older AX JACE this causes issues every now and again but generally the JACE switches back to 10 speed and all is good, most of the time. On the newer JACE800 it appears that it will not switch unless you reboot or disconnect/reconnect the cable so when the DBACS decides it's moving back in time and refuses to switch back up to 100 speed you're stuck until you reboot or unplug it.

    I've solved it by installing a small managed switch between the two and fixing the port connected to the DBACS at 10 speed. So far so good.


    Quote Originally Posted by RJS_Controls View Post
    I have a problems where the DBAC stops Ethernet communications after a few days to the Jace (both 600s in Ax in one job & in 8000 N4 another).
    The DBAC is "alive", but only a power reset with re-establish Ethernet communications.

    I am plugged directly DBAC to the Jace with a crossover cable & I brought it in as "DAIKIN MasterStation III" as a BACNet device.
    Should I go through a unmanaged network switch with a patch cable?

    Do I need to periodically write to the DBAC to keep communications alive?
    Right now I am just monitoring space temps.

    Thanks
    Rich
  • 02-02-2021, 02:21 PM
    Balibe
    The DBACS was a pain and thankfully they no longer using them in my area on new systems. The last 3 Daikin systems I have integrated they have supplied the ITM with the BACnet Server Gateway license. Each VRV comes in as a separate device with it's own points instead all the points with **001/**002 in one device. They also added dual setpoint control. If the startup tech names/tags them correctly in the ITM it follows to bacnet, no need to know the DIII-Net link/address. If the ITM has rev2.06 or higher you can also see all the outdoor units which has status, press, temp, comp speed, etc.
  • 02-01-2021, 07:03 PM
    MaxBurn
    Pretty much. I posted elsewhere the one we had that was dying worked in isolation, just our module talking to that panel worked fine. Put both on the customer network and it dies eventually. I’m speculating you could spend a bunch of time with captures and eventually find what it can’t deal with. But what would you do with such info?
  • 02-01-2021, 06:06 PM
    AlexM
    Quote Originally Posted by RJS_Controls View Post
    I never found out the what & why, but it was confirmed by others on this board it is a real problem.
    A suggested work around is to wire the 24VAC power to the DBACS through a NC relay and tie it to a controllable output.
    I have a button on the GUI to reset the power manually, but I also set up the Status demux (fault- out) to a one shot to trigger it automatically.
    I haven't tried the automatic yet, but it should work.
    Thank you. What an absolute piece of **** kit.
    For the price it should be bomb proof! And make tea when asked. I’m messing about with Adpu timeouts and poll times as a last attempt but at least it does seem to come back to life if I reboot (restart doesn’t work, only a reboot) the Jace via the platform so I can do that with a program rather than install relays and IO. On top of this the user interface thing Daikin literally just installed stopped working ... uses flash on its web pages. My least favourite manufacturer of this decade.
This thread has more than 20 replies. Click here to review the whole thread.