  • 07-13-2013, 08:40 PM
    54regcab
    Quote Originally Posted by CoolShowers View Post
    I found out about weathering the hard way haha! They're a sub company of rheem/ruud I think?
    Also Thermalzone and a few others.
  • 07-13-2013, 08:31 PM
    CoolShowers
    Quote Originally Posted by klee7013 View Post
    x2 weatherking also

    Also some of the older amana models energized in heat. I think.
    I found out about weathering the hard way haha! They're a sub company of rheem/ruud I think?
  • 07-13-2013, 08:06 PM
    klee7013
    Quote Originally Posted by 54regcab View Post
    +1, I have yet to run into a Rheem/Ruud that energizes in cool.
    x2 weatherking also

    Also some of the older amana models energized in heat. I think.
  • 07-13-2013, 08:02 PM
    Texanna Slim
    Somewhere a jumper may need clipped...
  • 07-13-2013, 03:54 PM
    zleinenbach
    ive got a question very similar to this. installed a new comfortsense tstat with new lennox heat pump and air handler. reversing valve wouldnt energize ( allow cooling). i double checked wiring and programming and didnt find anything wrong. condemned tstat and replaced with same thing, all seems to work fine
    but here is the kicker. very next week did essentially same system changeout and it does same deal. am i missing something obvious or did i find two bad tstats in a row?
  • 07-13-2013, 06:41 AM
    54regcab
    Quote Originally Posted by Kevin O'Neill View Post
    Last Ruud unit I worked on still energized the reversing valve in heat. Rheem too.
    +1, I have yet to run into a Rheem/Ruud that energizes in cool.
  • 07-12-2013, 09:17 PM
    Kevin O'Neill
    Last Ruud unit I worked on still energized the reversing valve in heat. Rheem too.
  • 07-12-2013, 07:49 PM
    jcrew4242
    Thanks guy.
  • 07-12-2013, 07:41 PM
    CoolShowers
    Depends on the manufacturer. Rheem, Ruud, and their subdivisions were notorious for the reversing valve energizing in heating. I think they've switched and pretty much any new heat pump reversing valve energizes in cooling, which is the "O" terminal. The "B" terminal was used on older stats for energizing in heat. Now, pretty much all stats give you the option of how the reversing valve energizes in the installer options.
  • 07-12-2013, 07:39 PM
    catmanacman
    yes b energizes the rv in heat mode mainly ruud/rheem
  • 07-12-2013, 07:29 PM
    jcrew4242

    Heat pump thermostats

    I am working on a Goodman 3 ton heat pump and
    I notice there is a B port and O port for heat pump t-stat.
    I know that O will be energized the 3 ways reversing valve during cooling mode. Does B work the other way around? which B will energized during heat mode??
    Is all reversing valve work the same way, which only energized during cooling mode?