  • 11-06-2021, 11:05 AM
    controldude
    Yes Trane uses standard xif files for SCC and DAC profiles The 581 is considered a generic controller so then you have to map additional points for integration they work perfectly on the Trane Summit or SC platform as is.
  • 09-23-2021, 01:27 PM
    irvedwmac
    Hello BigGuy158,

    Would doing anything like binding the points with the LON Link Manager or doing commission commands from the LON Device Manager pop the BCU's commissioned connection to the controllers?

    (sigh) I'm afraid that we weren't ready to abandon the BCU just yet...

    Thanks
    Ed Macall
  • 09-23-2021, 11:46 AM
    bigguy158
    Did you bind the LON points in the JACE?


    Sent from my iPhone using Tapatalk
  • 09-23-2021, 09:38 AM
    irvedwmac
    Hi Guys (Yeah. Like how Magnum p.i. says it...),

    Well....

    I've gotten into the MP580s with the Rover, modified their programs so that the point values in the programs are being delivered to the LON network points like how acddc showed above.

    But when I go running downstairs to see if the JACE can see any values are showing up, they're all still showing up as 0, Nan, or Nul.

    Yeah. I modified the program, compiled it, downloaded it to the MP580. The Rover has a screen that shows that the LON network points should be showing something, but the JACE is still just seeing 0, Nan, or Nul values.

    What could be the matter?

    Thanks
    Ed Macall
  • 09-16-2021, 05:39 PM
    roadgear16
    The Comm3 port is for Trane isolated Comm 3 devices, such as PCM, TCM, certain VAVs, RTUs. Its a proprietary comm link, and can't be used for BACnet. The only way to get BACnet into the BCU is BACnet/IP, and it's cumbersome. You have to create a "proxy point" for any point that you want to show or utilize.

    The BCU (BMTX) only has one Lon network.

    Here is a link I found to the hardware installation manual that lists the links and what they support.
  • 09-16-2021, 01:24 PM
    irvedwmac
    Hi Guys (Yeah. Like how Magnum p.i. says it...),

    What is the Comm 3 port on the BCU?

    Will that be another LON network? Or could it be a BACnet network?

    Where do I read up on what this is?

    Thanks,
    Ed Macall
    Campbell Inc
    216 645 5543
  • 08-18-2021, 09:15 PM
    Balibe
    Quote Originally Posted by bigguy158 View Post
    We usually just talk LON to them and remove the BCU. You do have to expose all the points using rover as shown in this thread.


    Sent from my iPad using Tapatalk
    +1

    To expand ..... these controllers are field programmed and not a factory controller with default XIF file to create an LNML like a Trane Comm5 ZN511 or ZN521. None of the points are exposed to LON as the Trane BCU does not require this. You have to add the SNVT NVO/NVI's manually for each point you need to read/control in the control program with Rover Tracer Graphical Programming as BigGuy stated and shown in the previous posts this thread.

    To note .... if you are looking to write points, there will be some modification to to the logic/program needed so the logic looks at the SNVT NVI instead of the BCU and/or display. This will depend on the existing logic/program as you can't map a BCU/display point in logic as an NVI. If there is a display on the MP581, I typically put a NVI switch into the logic writes to flip between display or NVI on the display. This way if the network is down, they can still have local control thru the display.
  • 08-18-2021, 03:33 PM
    bigguy158
    We usually just talk LON to them and remove the BCU. You do have to expose all the points using rover as shown in this thread.


    Sent from my iPad using Tapatalk
  • 08-18-2021, 01:35 PM
    irvedwmac
    Hi Guys (Yeah. Like how Magnum p.i. says it...),

    I have to confess that I am not understanding this issue of bringing the LON network points into Tridium.

    I thought that a person needed to come up with an LNML (LON Network Markup Language) file for the controllers.

    Don't the Trane controllers have standard LNML files for them?

    Or do they not have files for them, because their network variables are variable like with Honeywell Spyders?

    The Honeywell LCBS controllers like the XL10, XL15C, and XL15A had LNML files for them, because their network variables were fixed regardless of programming, but with the Honeywell Spyders, very few network variables were fixed.
  • 08-18-2021, 10:53 AM
    irvedwmac
    Hi Guys (Yeah. Like how Magnum p.i. says it...),

    I got 4 MP581s networked to a BCU (64002334?) and an old Windows 98 laptop is connected to the BCU's ethernet port.

    How should I connect Tridium to this?

    Would it be possible to put the BCU on the computer network and have Tridium to to the Trane controllers with LON over IP or something?

    Could a JACE (Titan8000) coexist on the LON network with the BCU?

    (I remember that the Command Displays for Honeywell's LCBS system didn't like to work with the JACEs and would go blank when a Niagara system would start talking with them. I thought that the XL15As or XL15Bs also had such a problem as well....)

    Which Trane manuals should I find my answers in?
  • 09-30-2012, 09:13 PM
    apprentice3
    Quote Originally Posted by acddc View Post
    Attachment 313111

    I just made this mapping table as an example for you to see what it will look like....
    Thanks a lot. This picture really helps out.
  • 09-30-2012, 09:12 PM
    apprentice3
    Quote Originally Posted by amigo View Post
    If I were you I would first see if you can get on that MP581 with your rover and see if the tgp is not password locked. Also if this a factory/oem programmed MP, ask yourself if you will be voiding the warranty if you touch it.
    my 2cents.
    Thanks amigo... I was thinking this same thing. I was going to call the factory tomorrow, and ask them if it was going to void the warranty.

    Thanks for your input
  • 09-30-2012, 02:30 PM
    acddc
    Attachment 313111
    Quote Originally Posted by apprentice3 View Post
    So lets say I want to bring a supply fan status input out of the MP581 for viewing. I would have to find the TGP programming that has that binary input in it. Then drag a line in TGP off of it to the correct SNVT type/NVO?

    Is there some sort of manual outlining this procedure?

    Thanks for all of the information.
    I just made this mapping table as an example for you to see what it will look like....
  • 09-30-2012, 09:44 AM
    shovelhead
    Quote Originally Posted by apprentice3 View Post
    So lets say I want to bring a supply fan status input out of the MP581 for viewing. I would have to find the TGP programming that has that binary input in it. Then drag a line in TGP off of it to the correct SNVT type/NVO?

    Is there some sort of manual outlining this procedure?

    Thanks for all of the information.
    Yes that's correct. Just add the approiate snvt and connect them, recompile and upload the program. What platform are you integrating to?
  • 09-30-2012, 09:03 AM
    amigo
    If I were you I would first see if you can get on that MP581 with your rover and see if the tgp is not password locked. Also if this a factory/oem programmed MP, ask yourself if you will be voiding the warranty if you touch it.
    my 2cents.
  • 09-30-2012, 07:33 AM
    apprentice3
    Quote Originally Posted by dboone View Post
    The points have to be mapped in TGP, which is done using the Rover service tool. Every desired point has to be linked to a network variable (snvt type). This is not done typically in basic programming as Trane front ends can see the points without additional mapping. Third party integrations require this additional step.
    So lets say I want to bring a supply fan status input out of the MP581 for viewing. I would have to find the TGP programming that has that binary input in it. Then drag a line in TGP off of it to the correct SNVT type/NVO?

    Is there some sort of manual outlining this procedure?

    Thanks for all of the information.
  • 09-29-2012, 09:48 PM
    dboone
    The points have to be mapped in TGP, which is done using the Rover service tool. Every desired point has to be linked to a network variable (snvt type). This is not done typically in basic programming as Trane front ends can see the points without additional mapping. Third party integrations require this additional step.
  • 09-29-2012, 07:54 AM
    dapper
    Mapping the points in not a real big deal. The problem is when you discover them the assigned pt names will not be brought in. I'm not sure what they will look like but for instance they will come in like AnalogInput1, AnalogInput2 or BinaryInput1, BinaryOutput1 etc. The same holds true for the variables and constants. You will need program so you can identify all of the points as they are used in the program.
  • 09-29-2012, 07:16 AM
    apprentice3
    Quote Originally Posted by dapper View Post
    'Trane Tracer comm 5' IS 'True Lon'. You can connect the MP580s directly to the LON network. The issue that you will have is mapping the points. In order to do this you will need a copy of the programs.
    I have Trane Rover Comm 5. The MP581s on these units have already been programmed by a manufacturer called Innovent. I am not sure if they have somehow locked up the program or not, but could I just connect with Rover, pull the program/back it up, and map the points? If so how hard is it to map all of the points? Does Trane have a manual on exactly how to do this? All I have done with NVs is Comm 5 bindings. Like for instance a OAT NVO on a MP503, I have binded to the NVI on a MP581. Does the mapping take place somewhere around the binding portion in Rover?

    Thanks for all of the help so far.
  • 09-28-2012, 11:03 PM
    amigo
    and Rover tool of course to make changes or add more nv points.