Mickandmousemechanical
12-29-2011, 08:11 PM
Hey guys,
M#HEHF-100 S#0094052 115v 12A 80,000 BTU High Eff.
I'm stumped.
Came across this 15 year old furnace low boy in a crawl space. Brand new thermostat set for Fan auto, Ambient 22, Set point 27 C. Found the burner cycling. The following are steps I've taken to correct this issue:
1. Cleaned flame sensor and checked HSI (both are fine).
2. Checked amp draw on the V-mtr (rated 3.0A) found 1.2A
3. Went through the safeties and jumped each individually to narrow down the search. All safties are working correctly in the burner circuit. (R.O switch, Air switch, Centrifugal) no High limit switch was found on wiring diagram or on unit.
4. Removed blower panel and tightened belt. (This stopped immediate short cycling and burners run for approx 2-3mins before shutting off and going through the process again).
Found a sequencer rated for H20 C40-120.
My question lies here, is this furnace running correctly (is it supposed to cycle like this)? And if not what am I missing?
:.02: Thanks
M#HEHF-100 S#0094052 115v 12A 80,000 BTU High Eff.
I'm stumped.
Came across this 15 year old furnace low boy in a crawl space. Brand new thermostat set for Fan auto, Ambient 22, Set point 27 C. Found the burner cycling. The following are steps I've taken to correct this issue:
1. Cleaned flame sensor and checked HSI (both are fine).
2. Checked amp draw on the V-mtr (rated 3.0A) found 1.2A
3. Went through the safeties and jumped each individually to narrow down the search. All safties are working correctly in the burner circuit. (R.O switch, Air switch, Centrifugal) no High limit switch was found on wiring diagram or on unit.
4. Removed blower panel and tightened belt. (This stopped immediate short cycling and burners run for approx 2-3mins before shutting off and going through the process again).
Found a sequencer rated for H20 C40-120.
My question lies here, is this furnace running correctly (is it supposed to cycle like this)? And if not what am I missing?
:.02: Thanks