I will be doing my first Pool Pak start up tommorrow.I have all the Pool Pak literature and start up sheets. Anyone have anything they have run into to look out for?

jacob perkins
02-28-2006, 10:16 PM
Originally posted by fixerup
to look out for?

cannon ball!!!

outside rep
02-28-2006, 10:54 PM
hmmmm were is my startup guy at

hes on this site he will be able to point you in the right direction


and have you talked with pool pak at all if you need numbers let me know I will be there thursday to pick up some stuff

[Edited by outside rep on 02-28-2006 at 10:57 PM]

fixerup
03-01-2006, 09:45 PM
What a mess.Surface temp.sensor not wired,no control wiring for auxillary strip heat, 24 volt signal to remote condensing unit not wired,remote interface didn't work found com cable connector coated with sheetrock mud cleaned up connector interface now works,flow switch not working,removed flow switch found flow switch is hitting bottom of pipe trimmed flow switch to allow it to work and confirm flow, trimmed refrigerant charge to 16F subcooling.I guess it's called job security.

duke of earl
03-01-2006, 10:01 PM
I am a startup rep for Desert Aire in my area. It sounds like a typical startup (or mopup)if you know what i mean.make sure you set pool water setpoint at about 82 degrees and cooling setpoint at least 2 degrees above that.set humidity between 50-60%.check airflow with a 0-2 inch magnehelic gage and adjust sheaves if necessary.make sure airflow is dead on or as close as possible.depending on type of reheat, the controller may need some program tweaking to match type of heat to the control scheme.pay close attention to the duct design as a smooth, straight airflow pattern is critical entering the evaporator.verify poolheater waterflow through the unit by checking delta-t.I would recommend reading the startup manual before proceeding.Good luck my friend.

The Duke

outside rep
03-02-2006, 03:48 PM
Originally posted by fixerup
What a mess.Surface temp.sensor not wired,no control wiring for auxillary strip heat, 24 volt signal to remote condensing unit not wired,remote interface didn't work found com cable connector coated with sheetrock mud cleaned up connector interface now works,flow switch not working,removed flow switch found flow switch is hitting bottom of pipe trimmed flow switch to allow it to work and confirm flow, trimmed refrigerant charge to 16F subcooling.I guess it's called job security.

now did your company only do startup and thats it or did they also install sounds like alot of the problems that you had sould like there from the install side

fixerup
03-02-2006, 07:14 PM
Actually another contractor did the install.We were contacted by pool pak to do the start up check for them.