jjnet
02-03-2006, 03:54 PM
Background of Previous Posts On This Subject:
All new equipment in first winter:
Trane XL19i 2TWZ9036A 3 ton two compressor heat pump.
Trane TWE037E13F variable speed air handler w/ strip heat backup (Trane 1410, one stage 9.6kw @ 240v).
Trane Zoning: 6 Zones
Trane Electrostatic Air Filter
Does anyone have an opinion on whether we have a mismatched air handler for our heat pump? Here’s the background.
Problem: 1st Stage 1 ½ ton compressor runs for 15 or 20 minutes, then appears (to the untrained eye) to shut off, and the suction line goes cold. HP stays off for a few minutes, then comes back on. This is not a defrost cycle. The stage’s contactor outputs remain hot with 240v even when the compressor stops working, and the outdoor fan continues to run.
(Defrost cycles are pretty clear because the outdoor fan stops, the zone controller opens all the zone dampers, and the strip heat kicks in, which causes the air handler fan to instantly speed up and make substantially more noise at all registers. Defrost cycles seem to happen at about ½ hour intervals and last from 1 ½ minutes to just under 3 minutes, depending on how cold it is outside.)
The second stage is even worse. It only runs a few minutes before going cold, and will not come back on for a long time. We’ve spoken to our contractor verbally and sent 3 detailed emails to 2 different addresses. (He’s occasionally told us that he didn’t get an email from us because we sent it to his wife’s address, even though we know he’s responded to other messages to that address.) He told us that it sounds like our discharge air temperature sensor is shutting the system down because it’s too close to the strip heating elements. We have not been able to communicate to him that the problem happens when strip heat is not active and that it has something to do with the compressors. He said he would check with Trane and get back to us. That was a full month ago and we’ve heard nothing.
We finally contacted another local Trane dealer a few weeks ago. Like every other HVAC company around here, they are incredibly busy. But after a few weeks they were finally able to work us into their schedule and sent two techs over yesterday to get pressure and temp readings to try to diagnose the problem. Unlike our original contractor, this dealer does not have extensive experience with Trane zoning. But like our original guy, they have not seen many 2 compressor systems and have only installed one other air/air heat pump (that’s one more than our original contractor, who is an expert in ground source heat pumps but not on air/air HP’s). They made it clear from the start that they would have a learning curve on our system, but could certainly pass the info on to Trane and get their recommendations.
They were here for about 3 hours watching what the system did in each stage of both heating and cooling and at many zone damper configurations. Here’s what they found:
The head pressures and temperatures went way too high (I think temp was up to 380 degrees) at about the time intervals we expected for each compressor. When it looked and sounded to us like the compressor was turning off, it was actually temporarily switching the compressors into a bypass mode to respond to the high pressures and temps. After it did this a few times it would finally have to shut down for an extended period, most likely due to internal thermal overload protection.
They thought the system might be somewhat overcharged, but felt that the air handler fan was running at too low a speed to get rid of enough refrigerant heat in the indoor coil. We experimented with the system for a long time, so they could see how the zone controller varied the indoor fan speed with different zones open and closed. We made all zones wide open by choosing set points of 90 across the board. We bumped up the fan from 400 cfm/ton to 450 and changed from Residential to Commercial air flow. We changed the strip heat air flow from 900 to 1100 In all cases, they felt that the fan should be running at a higher speed than it was. Or, if the indoor coil were larger, the system might work at the present air flows.
The possibility that the indoor coil might be too small brought up a conversation I had with Trane in Denver a few months ago, when one employee told us that we had the wrong air handler for our heat pump. He said that Trane does not recommend the TWE037 for this HP, but says to use the TWE040 instead. And all the Trane charging curve info on the heat pump Service Facts sheet is for the TWE040. These tables include adjustment factors for all the other Trane air handlers that should be used with this HP, but this list did not include our TWE037 air handler.
So at this point we are waiting for Trane’s interpretation of all this. If anyone has experience with similar components or symptoms, we’d really appreciate hearing their perspective on this.
In the meantime, to check the possibility that the discharge air sensor is involved, we recently added our own wireless temp sensor in the supply plenum. The hottest it’s ever gotten was 115, and that was with the strip heat on for 20 minutes or so. With all the heat pump testing yesterday it never got higher than that 115 point, even when the refrigerant was over 300. I don’t know what the standard discharge air threshold is, but they were pretty sure that it was well over 115.
In addition, to see if our ducting is at fault, we’ve made up a table listing each zone, its square footage, heat loss, heat gain and recommended CFM from HVAC-Calc. This table summarizes the duct sizes and lengths to each supply outlet and each return. We’ve set up this table as an HTM file with the following link:
http://www.frontier.net/~jj/HVACZoneDucts.htm
All new equipment in first winter:
Trane XL19i 2TWZ9036A 3 ton two compressor heat pump.
Trane TWE037E13F variable speed air handler w/ strip heat backup (Trane 1410, one stage 9.6kw @ 240v).
Trane Zoning: 6 Zones
Trane Electrostatic Air Filter
Does anyone have an opinion on whether we have a mismatched air handler for our heat pump? Here’s the background.
Problem: 1st Stage 1 ½ ton compressor runs for 15 or 20 minutes, then appears (to the untrained eye) to shut off, and the suction line goes cold. HP stays off for a few minutes, then comes back on. This is not a defrost cycle. The stage’s contactor outputs remain hot with 240v even when the compressor stops working, and the outdoor fan continues to run.
(Defrost cycles are pretty clear because the outdoor fan stops, the zone controller opens all the zone dampers, and the strip heat kicks in, which causes the air handler fan to instantly speed up and make substantially more noise at all registers. Defrost cycles seem to happen at about ½ hour intervals and last from 1 ½ minutes to just under 3 minutes, depending on how cold it is outside.)
The second stage is even worse. It only runs a few minutes before going cold, and will not come back on for a long time. We’ve spoken to our contractor verbally and sent 3 detailed emails to 2 different addresses. (He’s occasionally told us that he didn’t get an email from us because we sent it to his wife’s address, even though we know he’s responded to other messages to that address.) He told us that it sounds like our discharge air temperature sensor is shutting the system down because it’s too close to the strip heating elements. We have not been able to communicate to him that the problem happens when strip heat is not active and that it has something to do with the compressors. He said he would check with Trane and get back to us. That was a full month ago and we’ve heard nothing.
We finally contacted another local Trane dealer a few weeks ago. Like every other HVAC company around here, they are incredibly busy. But after a few weeks they were finally able to work us into their schedule and sent two techs over yesterday to get pressure and temp readings to try to diagnose the problem. Unlike our original contractor, this dealer does not have extensive experience with Trane zoning. But like our original guy, they have not seen many 2 compressor systems and have only installed one other air/air heat pump (that’s one more than our original contractor, who is an expert in ground source heat pumps but not on air/air HP’s). They made it clear from the start that they would have a learning curve on our system, but could certainly pass the info on to Trane and get their recommendations.
They were here for about 3 hours watching what the system did in each stage of both heating and cooling and at many zone damper configurations. Here’s what they found:
The head pressures and temperatures went way too high (I think temp was up to 380 degrees) at about the time intervals we expected for each compressor. When it looked and sounded to us like the compressor was turning off, it was actually temporarily switching the compressors into a bypass mode to respond to the high pressures and temps. After it did this a few times it would finally have to shut down for an extended period, most likely due to internal thermal overload protection.
They thought the system might be somewhat overcharged, but felt that the air handler fan was running at too low a speed to get rid of enough refrigerant heat in the indoor coil. We experimented with the system for a long time, so they could see how the zone controller varied the indoor fan speed with different zones open and closed. We made all zones wide open by choosing set points of 90 across the board. We bumped up the fan from 400 cfm/ton to 450 and changed from Residential to Commercial air flow. We changed the strip heat air flow from 900 to 1100 In all cases, they felt that the fan should be running at a higher speed than it was. Or, if the indoor coil were larger, the system might work at the present air flows.
The possibility that the indoor coil might be too small brought up a conversation I had with Trane in Denver a few months ago, when one employee told us that we had the wrong air handler for our heat pump. He said that Trane does not recommend the TWE037 for this HP, but says to use the TWE040 instead. And all the Trane charging curve info on the heat pump Service Facts sheet is for the TWE040. These tables include adjustment factors for all the other Trane air handlers that should be used with this HP, but this list did not include our TWE037 air handler.
So at this point we are waiting for Trane’s interpretation of all this. If anyone has experience with similar components or symptoms, we’d really appreciate hearing their perspective on this.
In the meantime, to check the possibility that the discharge air sensor is involved, we recently added our own wireless temp sensor in the supply plenum. The hottest it’s ever gotten was 115, and that was with the strip heat on for 20 minutes or so. With all the heat pump testing yesterday it never got higher than that 115 point, even when the refrigerant was over 300. I don’t know what the standard discharge air threshold is, but they were pretty sure that it was well over 115.
In addition, to see if our ducting is at fault, we’ve made up a table listing each zone, its square footage, heat loss, heat gain and recommended CFM from HVAC-Calc. This table summarizes the duct sizes and lengths to each supply outlet and each return. We’ve set up this table as an HTM file with the following link:
http://www.frontier.net/~jj/HVACZoneDucts.htm